Just noticed that the requirement for RCD protection has been removed for TT installations.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss TT and RCD protection in the UK Electrical Forum area at ElectriciansForums.net
The 17th did that. RCD protection has not been mandatory for a TT system since the 16th Edition.Just noticed that the requirement for RCD protection has been removed for TT installations.
Precisely. It's a decade new.I'm pretty sure that reg you have given was in the 17th, so nothing new.
Once got an RA of 6 ohms on a steel farm building by drilling and tapping a girder for the lug.Would have been ok for a B6 on a lighting cct I think.Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.
I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?
Essex, you're always (or rather 99.9% of the time) going to need an RCD for TT as you'll never be able to meet the Zs values unless the Ra<1Ω which (unless you are Trev) is nigh impossible.
I'm pretty sure that reg you have given was in the 17th, so nothing new. Would be very interesting to know if anyone on here has ever been able to get an Ra low enough to forgo an RCD on a TT though?