martinsayer81

hi guys

hoping you could give me your thoughts,

i am pricing for a consumer unit change, its an old fuseboard with re-wireables.
it has 16mm meter tails, but it has a fairly new looking 100A main fuse.

its a small-ish house..... 2 ring mains, 2 lighting radials, a couple of sockets in the garage, and an immersion heater radial,

i was wondering whether or not i could just down-grade the main fuse to a 60A and keep the existing 16mm tails( no damage, or signs of overheating or burning)
or whether i have to leave the fuse at 100A and fit 25mm tails?

there's no electric shower or oven,

i would appreciate your advice

many thanks
 
Yes but you didn't factor in the air fare it cost to go to china and back to get the gear
what it is.....is their `offcuts`...their issued with...lets say a 25 meter drum of tails.....so they put more on a job..than it really was....the rest goes on the bootsale...lol....god, he`s got allsorts..C/Us chuffin RCBOs..drums of twin...lol...
 
OK Martin, With a TNS and a run of less than 2 mtrs you can use 16mm tails as a foot note they normaly fit 80 amp fuses in the DNO for domestic properties nowdays previously they fitted 60 amp
 
the main fuse may be 80-100amp i would upgrade the tails to 25mm the fuse is nothing to do with you but as you are upgrading the system why not upgrade the main tails as its fairly cheap to do so £10 max material , disconnecting them from old board anyway .
i always upgrade to 25mm tails and 16mm earth incoming
 
the main fuse may be 80-100amp i would upgrade the tails to 25mm the fuse is nothing to do with you but as you are upgrading the system why not upgrade the main tails as its fairly cheap to do so £10 max material , disconnecting them from old board anyway .
i always upgrade to 25mm tails and 16mm earth incoming


So do you always cut the seals on the meter then?
 
consumers isolation switch is 30cm max from main fuse murdoch.

if there isnt a isolation point the electricity supplier will gladly fit this for £85 allowing the electrician to carry our his work without cutting seals or pulling fuse.

i could easily re seal using my sealing plyers and SP seals as i am authorised contractor ;)
 
consumers isolation switch is 30cm max from main fuse murdoch.

if there isnt a isolation point the electricity supplier will gladly fit this for £85 allowing the electrician to carry our his work without cutting seals or pulling fuse.

i could easily re seal using my sealing plyers and SP seals as i am authorised contractor ;)

And all your customers are happy to pay this?
 
all my customers appreciate my good quality work,knowledge and professionalism so my advice is golden to them its not much of a hassle to have this done actually can benifit in future , they are there for a reason thats why every new build will have L in and out of switch and nuetral in & out
 
:s every new property has this as standard so copper prices are not the issue , the guys asked for advice put in 25mm and allow for growth of the electrical system

Interestingly most products being bought now can be "greener" so when will the time come when we have to rip out 25mm tails and go around fitting 60A fuses!


LOL
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
upgrade meter tails, or downgrade main incoming fuse??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
63
Unsolved
--

Advert

Thread statistics

Created
martinsayer81,
Last reply from
Engineer54,
Replies
63
Views
14,678

Advert

Back
Top