Hi All,

I am at my wits end here so here goes...

On Monday I was called to a domestic premises with reported shocks occuring while the client was taking a shower. This was apparently first noticed over 2 weeks ago!

We proceeded to do all the relevant checks on Earth Bonding and various testing including IR on all circuits. Most circuits proved to be fine apart from a high Zs (3.06) on the upstairs ring. All bonding was proved to be sound. Install is a PME with a split board with only 1 RCD. Main incomer has a Zs of 0.26. I moved all circuits over to RCD protection to see if any tripping would occur....to no avail.

Upon further investigation we ran a lead out from the board to provide a means of testing in the shower...what is clear is that a voltage of 6v can be meaured between Earth and the actual water in the shower tray but ONLY WHEN IT IS DRAINING THROUGH THE WASTE! This voltage increases to around 18v at least as load is increased around the house.

Upon FURTHER investigation I have now discovered this to be the case on all 3 showers and all basins upstairs. With the basins I actually filled them up, released the plug then could measure the voltage as the water drained...NOT BEFORE. With the showers I ran the water and turned off then measured the voltage again as the water drained. All showers are hot and cold fed with no local pumps.

I have had every circuit apart and individually connected 1 circuit at a time in the board and found that 4 out of the 6 circuits seemed to bring about the voltage. I have also bizarrely placed a lead between the mixer taps and into the water in the plug hole while running the water. This always removes the voltage.

I am left with the only answer that somehow a voltage is finding its way through the waste water and once someone gives it a path then the shock occurs!!

I have had SSE out today checking everything their end....no problems. Contacted the NICEIC...no advice could be given! I've consulted 2 of my so called guru electricians who are stumped. I am hoping that tomorrows investigation of the external wiring will reveal something but I'm not holding my breath!

Somebody please tell me they have come accross this before!!
 
Shame purple never let us know. He can't still be fault finding

Last I heard he was wearing a snorkel, in the garden pond, trying to megger the gold fish.....
 
Is Purple really not going to let us know how it ended? I'd really like to know? Theres been almost 5000 views!! Come on Purple!!
 
Last edited:
" The purpose of connecting the customer's system to ground is to limit the voltage that may develop if high voltage conductors fall down onto lower-voltage conductors which are usually mounted lower to the ground, or if a failure occurs within a distribution transformer. If all conductive objects are bonded to the same earth grounding system, the risk of electric shock is minimized. However, multiple connections between the utility ground and customer ground can lead to stray voltage problems; customer piping, swimming pools or other equipment may develop objectionable voltages. These problems may be difficult to resolve since they often originate from places other than the customer's premises. "

Just found this on the net,
It may help your quest, although it does say it may be difficult to resolve lol.
I'm keen to hear your findings .
May you get to the source my friend.
 
I've had same with 'tingly taps' post a while ago, finishing with SEB digging hole and repairing joint, the end.......no, after this was called in again as fault returned. Bloody macerator was faulty. Have you got one in the system?
 

Reply to Voltage in shower waste! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
2
Replies
15
Views
3K
Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top