dingledong
Just tested a flat no cpc to lights and switches , so on the report class 2 etc etc but the people are selling and there are 4 metal light fittings which are now pendants but I know from what's been asked and hinted he will put the metal lights back up nothing I can do to cover myself
Re: what should i do
Whacking a sticker on the CU cover, stating that circuits ? & ? have no provision for earthing and that metal fittings shouldn't be used, wouldn't hurt either.
Why? There is a perfectly good EICR being given to the customer, they will be well aware of the dangers once they have read it.
Should we also put a sticker on DBs if there are sockets that aren't RCD protected?
Were you asked to change the fittings?
What gave you the authority to make alterations?
You were there to do an EICR, fill it in and get paid. You can only advise, if the client chooses to ignore the advice it’s not your problem.
It’s a wonder you’re not getting charged for refitting them.
If there is not a sticker stating what circuits can only have class 2 equipment connected to them, then this should be noted on the EICR.
if you have removed lights etc to make it a class 2 circuit then it is your responsibility to put the sticker on.
You can buy then or make then on a Dymo (or any other make) printer
A sticker is a good idea as not every one has access to the certificate so any one switching off the circuit should see the sticker its called covering you backside me id take a pic too
Why does it need a sticker? All class 1 appliances have been removed from the circuit. The circuit complied when it was wired. Any future work should be carried out by a competant person who should know the regs so will be aware when they look at the circuit what is suitable to connect to it.
Cos sometimes when I post nothing happens so waited and I thought bugger it's happened again so I will do another one, so did the second and blow me down the first appeared
My apologies
No I just wanted something second opinion so posted twice
exactly because we have to protect ourselves from the prats ,
My apologies
OK I’ll repeat myself.
what can i do
Thread Tags
dingledong,
shanky887614,