Hello all..

I expect my full rewire will be assessed this year by Stroma.

It has been done very well and neatly and ticks all the regulation boxes..... apart from socket/switches heights. These I have kept as existing, approx 1350mm for switches and 300mm for sockets.

I have rang Stroma and they have said that a full rewire needs to meet Part M requirements for these heights. I realise BS7671 553.1.6 doesn't give these heights but Part M does and if Stroma say it has to be then there's no arguing really. Also, even though the vast majority of threads say that a rewire does not need to meet part M heights I believe it does as Section 0, 0.2 says part M applies to new builds and also 'Material alterations' of existing dwellings.

Basically my question is 'could they possible make me change all the heights'? I can't believe they would as that's crazy, but just looking for reassurance. I expect it will go down as a note and be checked for the following year to make sure I have adhered to the heights?
 
Last edited:
I don't understand what has gone wrong?
I put some impromptu pictures of the install up and no one has said anything bad or picky???
This is not normal behaviour and I feel quite left out.... almost abandoned:(! For heavens sake chaps I'm a Electrical Trainee (well, 6mw)... where's all the bashing!!!
However, I can understand it if you all feel that I'm perfect :D

(PS.. no response from Stroma yet to my email.
 
I don't understand what has gone wrong?
I put some impromptu pictures of the install up and no one has said anything bad or picky???
This is not normal behaviour and I feel quite left out.... almost abandoned:(! For heavens sake chaps I'm a Electrical Trainee (well, 6mw)... where's all the bashing!!!
However, I can understand it if you all feel that I'm perfect :D

(PS.. no response from Stroma yet to my email.

They're all too busy bumping their gums about how to earth a back box. :)
 
Your first point, if you read item I) in below, and explain for me?

View attachment 43872

Your second point, its item 0.4 thats a bit gobbledygook.
Midwest very sorry about the delay I was away and didn't have time before leaving to open up the laptop and gather all the references. Normally I access the forum on my mobile phone. I hope it will be worth the delay!

I've looked at the online version so I could get the context of the previous page, and I think it's changed from your version.
https://assets.publishing.service.g...BR_PDF_AD_M1_2015_with_2016_amendments_V3.pdf
Using the new document, it's quite specific in the guidance now:
[ElectriciansForums.net] What will the outcome be of my assessment?

Looking at the actual regulation 5 in the legislation it does match your quote, but the context is essential here (see underline): The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/5
"there is a material change of use where there is a change in the purposes for which or the circumstances in which a building is used, so that after that change... ...the building, which contains at least one room for residential purposes, contains a greater or lesser number of such rooms than it did previously"
So it specifically only includes changes in what you're using the existing building, rather than changes resulting from building work.
Also the regulation itself excludes extensions specifically
[ElectriciansForums.net] What will the outcome be of my assessment?



Regarding 0.4, again it's changed in the latest version to 0.11
[ElectriciansForums.net] What will the outcome be of my assessment?

Looking at regulation 3 The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/3
"
(2) An alteration is material for the purposes of these Regulations if the work, or any part of it, would at any stage result—

(a)in a building or controlled service or fitting not complying with a relevant requirement where previously it did; or

(b)in a building or controlled service or fitting which before the work commenced did not comply with a relevant requirement, being more unsatisfactory in relation to such a requirement.
"
So a socket at 300mm doesn't comply, but it would be a material alteration if you moved it down to 200mm. Adding further sockets at an existing non compliant height, to me (non professional) would be a material alteration. However part M above specifically says that the building overall shouldn't be less compliant, so that clarifies matters somewhat.

Let me know if that is unclear - it's certainly clarified my understanding somewhat!:)
 
Last edited:
Just want to throw in a curved ball ... What about above counter sockets in kitchens .... They would struggle to comply with part m
Most kitchen sockets are within the appropriate range for habitable rooms (inc kitchens) in visitable dwellings for people with reduced mobility.
I suppose you don't consider that sockets at 1200 with a 600 depth unit in front meet the performance suggestion:
[ElectriciansForums.net] What will the outcome be of my assessment?

Thinking of older people I know, I think bending tends to be the tricky part rather than reaching forward, so perhaps the requirement isn't as far off as we'd expect?

Interestingly, for houses for people in wheelchairs, the requirements are far more strict and the whole kitchen is built around suitable requirements. The relevant part would be
[ElectriciansForums.net] What will the outcome be of my assessment?

I would expect the layout would be designed and provided by a designer for all the trades in that situation though.

[ElectriciansForums.net] What will the outcome be of my assessment?


[ElectriciansForums.net] What will the outcome be of my assessment?
 
Let me know if that is unclear - it's certainly clarified my understanding somewhat!:)

I really don’t understand what you are doing on here John, but what I do know is that the building regs are far too open to interpretation so my advice stands to the op

If Stroma think it’s wrong, ask them to clarify in writing what Is wrong and why

But go ahead with the assessment as I would wager a large bet it won’t be raised.
 
Midwest very sorry about the delay I was away and didn't have time before leaving to open up the laptop and gather all the references. Normally I access the forum on my mobile phone. I hope it will be worth the delay!

I've looked at the online version so I could get the context of the previous page, and I think it's changed from your version.
https://assets.publishing.service.g...BR_PDF_AD_M1_2015_with_2016_amendments_V3.pdf
Using the new document, it's quite specific in the guidance now:
View attachment 43910
Looking at the actual regulation 5 in the legislation it does match your quote, but the context is essential here (see underline): The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/5
"there is a material change of use where there is a change in the purposes for which or the circumstances in which a building is used, so that after that change... ...the building, which contains at least one room for residential purposes, contains a greater or lesser number of such rooms than it did previously"
So it specifically only includes changes in what you're using the existing building, rather than changes resulting from building work.
Also the regulation itself excludes extensions specifically
View attachment 43916


Regarding 0.4, again it's changed in the latest version to 0.11
View attachment 43911
Looking at regulation 3 The Building Regulations 2010 - http://www.legislation.gov.uk/uksi/2010/2214/regulation/3
"
(2) An alteration is material for the purposes of these Regulations if the work, or any part of it, would at any stage result—

(a)in a building or controlled service or fitting not complying with a relevant requirement where previously it did; or

(b)in a building or controlled service or fitting which before the work commenced did not comply with a relevant requirement, being more unsatisfactory in relation to such a requirement.
"
So a socket at 300mm doesn't comply, but it would be a material alteration if you moved it down to 200mm. Adding further sockets at an existing non compliant height, to me (non professional) would be a material alteration. However part M above specifically says that the building overall shouldn't be less compliant, so that clarifies matters somewhat.

Let me know if that is unclear - it's certainly clarified my understanding somewhat!:)

Thanks for the reply & time.

I can't find that the definition of material change of use, has been altered (or removed) in the latest legislation (Reg 5; (i) the building, which contains at least one room for residential purposes, contains a greater or lesser number of such rooms than it did previously. Clearly relates to an extension or alteration of a building. However, Reg 6 Requirements relating to material change of use, does not list Reg 5 (i), to include M1.

So in the broad sense, an alteration or extension to an existing property, is a material alteration, but not all the Documents apply, including M1. Not commenting on Reg 3, so as not to confuse things!

However, the Guidance given in 0.4, is what appears to meander around IMO, although it does give one example of removing a downstairs toilet in an extension or alteration, of making things worse in terms of (M1) than before.

Enough said now? :)
 

Reply to What will the outcome be of my assessment? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
632
  • Question
ok cheers for the help lads
Replies
7
Views
713

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top