The whole point of testing an RCD is to prove that if a fault occurs in the circuit then the RCD will trip. Unless you do this at the extremity you cannot be certain that there is not a fault on the circuit which results in the RCD NOT tripping.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss When testing a circuit protected by RCBO, do you test at the DB or furtherst point in the Commercial Electrical Advice area at ElectriciansForums.net
That is what a Zs test is for , checking the valve of the earth fault loop impedance so that the protective device will disconnect the power in the required times permitted,not an rcd test.The whole point of testing an RCD is to prove that if a fault occurs in the circuit then the RCD will trip. Unless you do this at the extremity you cannot be certain that there is not a fault on the circuit which results in the RCD NOT tripping.
Either way, for me, whichever is easier..... I had an assessor telling me it had to be done at the device....but what difference between that and circuit points, after all, you are just testing RCD operation times, as required.
Ramp testing is a separate test, altogether.
What are you talking about?I think we are all aware a ramp test is a separate test that wasn't the question asked and from your reply I assume you don't ramp test any RCD's so therefore don't fully check it's function
The whole point of testing an RCD is to prove that if a fault occurs in the circuit then the RCD will trip. Unless you do this at the extremity you cannot be certain that there is not a fault on the circuit which results in the RCD NOT tripping.
The return dumb is for an absolutely stupid assumption.I think we are all aware a ramp test is a separate test that wasn't the question asked and from your reply I assume you don't ramp test any RCD's so therefore don't fully check it's function
The return dumb is for an absolutely stupid assumption.
…...as well as not being able to take a joke!
Whether you see this or not, it seems you are one sad man……..resorting to such a serious and stupid accusation.I can take a joke but you clearly don't have a problem putting peoples lives at risk by trashing a serious conversation
Yes you can achieve the trip times and still leave a customer with a faulty RCD
Don't bother replying I won't see it you have disappeared from view
I think we are all aware a ramp test is a separate test that wasn't the question asked and from your reply I assume you don't ramp test any RCD's so therefore don't fully check it's function
I have found on quite a few occasions recently that RCD's / RCBO's can meet the trip times especially when testing at the device while a ramp test has indicated a trip current in excess of the specified 30mA to trip the device
So it is possible that a faulty device can meet the trip times but not within the specified 30mA tripping current
May be an instance. An existing RCD failed, initially. It tripped at well over on ramp. It hadn’t been tested or operated for a good while. After a few test button operations, it operated fine. Replaced anyway because it was pretty old, but it goes to show.If you carry out the RCD test (e.g. BS EN 61008), for example x 1, the testing device introduces the 30mA current, for which the RCD must detect & disconnect within 300ms.
I can't see how an RCD would pass such a test, but fail because the mA would be too high, as the test current used by the test device is set at 30mA.
A ramp test will measure at what mA the RCD is tripping at. If the RCD was tripping at say 40mA, it would fail the x 1 test, surely?
But what I am saying is, the tester introduces 30mA (at x 1) nothing more nothing less. If the rcd is faulty and only trips at say 40mA, the test will time out and therefore the rcd will fail that part of the test?May be an instance. An existing RCD failed, initially. It tripped at well over on ramp. It hadn’t been tested or operated for a good while. After a few test button operations, it operated fine. Replaced anyway because it was pretty old, but it goes to show.
It doesn’t matter if it fails the x 1 test.But what I am saying is, the tester introduces 30mA (at x 1) nothing more nothing less. If the rcd is faulty and only trips at say 40mA, the test will time out and therefore the rcd will fail that part of the test?
PS the inspector would then move to the ramp test, to verify the issue. Same would go for 1/2 x test.
Reply to When testing a circuit protected by RCBO, do you test at the DB or furtherst point in the Commercial Electrical Advice area at ElectriciansForums.net