When testing a circuit protected by RCBO, do you test at the DB or furtherst point | Page 3 | on ElectriciansForums

Discuss When testing a circuit protected by RCBO, do you test at the DB or furtherst point in the Commercial Electrical Advice area at ElectriciansForums.net

If you carry out the RCD test (e.g. BS EN 61008), for example x 1, the testing device introduces the 30mA current, for which the RCD must detect & disconnect within 300ms.
I can't see how an RCD would pass such a test, but fail because the mA would be too high, as the test current used by the test device is set at 30mA.

A ramp test will measure at what mA the RCD is tripping at. If the RCD was tripping at say 40mA, it would fail the x 1 test, surely?

I have had this issue on 3 occasions in the the last couple of years
One was a CU installed 6 months previously tested ok at install yet one of the RCD's was found to be faulty 6 months later, the other 2 were brand new CU's where one of the RCD's was not within spec at install

The first CU was found because a quick check at a socket where it had previously been ok failed to trip, tested at the CU it tripped within acceptable times both 1x and 5x although a little higher than I would normally expect decided to do a ramp test at the CU and found it tripped at 37mA I ramp tested it back at the socket but can't remember the exact figure I got but was high enough to cause concern as to whether it is acceptable just to test at the RCD
The other 2 had similar outcomes
On all occasions having contacted the manufacturers the RCD's have been replaced with no problems


It doesn’t matter if it fails the x 1 test.
It’s the x 5 test that it has to pass.

On my MFT on auto test if it fails the 1x then it fails the whole test
Given that ventricular fibrillation can occur at currents as low as 30mA I think the 1x test really matters
 
From the current Regulations:
NOTE: Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1 disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating current.

You want to disagree with what it says, fine.
Take it up with the IET.
 
I have had this issue on 3 occasions in the the last couple of years

The first CU was found because a quick check at a socket where it had previously been ok failed to trip, tested at the CU it tripped within acceptable times both 1x and 5x although a little higher than I would normally expect decided to do a ramp test at the CU and found it tripped at 37mA I ramp tested it back at the socket but can't remember the exact figure I got but was high enough to cause concern as to whether it is acceptable just to test at the RCD

I'll say this again, & then drop it.

At x 1 my MFT introduces a test current of 30mA (+0% to +10%.) to test an RCD. If it was testing this faulty RCD, its not going to provide it with the 37mA it needs to trip and the test would time out at 300ms, and my MFT would display an error code. I would then go on to conduct a ramp test on the RCD.

Therefore there is no need to conduct a ramp test, in normal circumstances.
 
From the current Regulations:
NOTE: Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1 disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating current.

You want to disagree with what it says, fine.
Take it up with the IET.

Ridiculous change to the regs IMHO! A working 100mA RCD will pass as a 30mA one.
 
Guidance Note 3 Section 2.6.19 says testing should be at the load side of the RCD, with loads disconnected. I always strive to test at the furthest point on a circuit, as Zs is critical to correct operation, and even correct type of RCD (see Section 411). What is the point of Table 41.3 if circuit resistance can be ignored? I admit if I'm working alone on a big circuit I'll test at the board, but this is very rare as I can usually find a helper for the resets.
 
Guidance Note 3 Section 2.6.19 says testing should be at the load side of the RCD, with loads disconnected. I always strive to test at the furthest point on a circuit, as Zs is critical to correct operation, and even correct type of RCD (see Section 411). What is the point of Table 41.3 if circuit resistance can be ignored? I admit if I'm working alone on a big circuit I'll test at the board, but this is very rare as I can usually find a helper for the resets.

For the umpteeth time, you are testing the device, not the circuit.
Do test every circuit connected to an RCD?
And, finally, surely you have an instrument that can perform auto testing?
 
For the umpteenth time plus 1 :D, the all knowing all seeing IET have this little piece about RCD's; testing is at indent 5.

Inspection and testing of electrical installations: residual current devices - https://electrical.------.org/wiring-matters/issues/50/inspection-and-testing-of-electrical-installations-residual-current-devices/

How do we interpret that? Think it says something similar in GN3.
 
For the umpteenth time plus 1 :D, the all knowing all seeing IET have this little piece about RCD's; testing is at indent 5.

Inspection and testing of electrical installations: residual current devices - https://electrical.------.org/wiring-matters/issues/50/inspection-and-testing-of-electrical-installations-residual-current-devices/

How do we interpret that? Think it says something similar in GN3.
The way I interpreted that is that you test on the load side and that can be anywhere in the circuit covered by the rcd, be it at the CU or at the closest socket outlet or the furthest light.
Your just testing the device only and not the circuit is what the article is saying.
I always test at the CU and until the regulations say different then I always will:)
 
The way I interpreted that is that you test on the load side and that can be anywhere in the circuit covered by the rcd, be it at the CU or at the closest socket outlet or the furthest light.
Your just testing the device only and not the circuit is what the article is saying.
I always test at the CU and until the regulations say different then I always will:)

Its the words 'between the line conductor of the protected circuit and the associated cpc' that confuses me. Personally, I would test the easiest quickest way, either at the CU or from somewhere on the circuit, which for me is usually the latter.
 
don't blame me. i didn't put them there. and it wasn't my fault the Titanic sank.
 

Reply to When testing a circuit protected by RCBO, do you test at the DB or furtherst point in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Get better soon
    • Friendly
    • Like
Replies
10
Views
481
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
751
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
518
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
907

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top