It doesn’t matter if it fails the x 1 test.
It’s the x 5 test that it has to pass.
Take your point. I'm trying to make mine about ramp testing.
If you carry out the RCD test (e.g. BS EN 61008), for example x 1, the testing device introduces the 30mA current, for which the RCD must detect & disconnect within 300ms.
I can't see how an RCD would pass such a test, but fail because the mA would be too high, as the test current used by the test device is set at 30mA.
A ramp test will measure at what mA the RCD is tripping at. If the RCD was tripping at say 40mA, it would fail the x 1 test, surely?
I have had this issue on 3 occasions in the the last couple of years
The first CU was found because a quick check at a socket where it had previously been ok failed to trip, tested at the CU it tripped within acceptable times both 1x and 5x although a little higher than I would normally expect decided to do a ramp test at the CU and found it tripped at 37mA I ramp tested it back at the socket but can't remember the exact figure I got but was high enough to cause concern as to whether it is acceptable just to test at the RCD
From the current Regulations:
NOTE: Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1 disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating current.
You want to disagree with what it says, fine.
Take it up with the IET.
Guidance Note 3 Section 2.6.19 says testing should be at the load side of the RCD, with loads disconnected. I always strive to test at the furthest point on a circuit, as Zs is critical to correct operation, and even correct type of RCD (see Section 411). What is the point of Table 41.3 if circuit resistance can be ignored? I admit if I'm working alone on a big circuit I'll test at the board, but this is very rare as I can usually find a helper for the resets.
I wish they did one that does an auto resetFor the umpteeth time, you are testing the device, not the circuit.
Do test every circuit connected to an RCD?
And, finally, surely you have an instrument that can perform auto testing?
The way I interpreted that is that you test on the load side and that can be anywhere in the circuit covered by the rcd, be it at the CU or at the closest socket outlet or the furthest light.For the umpteenth time plus 1, the all knowing all seeing IET have this little piece about RCD's; testing is at indent 5.
Inspection and testing of electrical installations: residual current devices - https://electrical.------.org/wiring-matters/issues/50/inspection-and-testing-of-electrical-installations-residual-current-devices/
How do we interpret that? Think it says something similar in GN3.
Your just testing the device only and not the circuit is what the article is saying.
I always test at the CU and until the regulations say different then I always will![]()
Tel.....you got more titles than uncle Albert got medals!sod the IET. i do it my way.
Reply to the thread, titled "When testing a circuit protected by RCBO, do you test at the DB or furtherst point" which is posted in Commercial Electrical Advice on Electricians Forums.