Why is split RCD not appropriate for TT?

swaRRR

Deleted account
OSG Pg.40 says:

'[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault protection of the single-insulated conductors that connect the load side of the double-pole main switch to the supply-side of the RCCB's.'

Why is there insufficient fault protection here?

I've seen loads of TT systems with RCD protection in them. What would you use instead? I know you can use RCBO's but they're not standard.
 
OSG Pg.40 says:

'[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault protection of the single-insulated conductors that connect the load side of the double-pole main switch to the supply-side of the RCCB's.'

Why is there insufficient fault protection here?

I've seen loads of TT systems with RCD protection in them. What would you use instead? I know you can use RCBO's but they're not standard
I think it's because of the split cu. The cable connecting from the bottom of the main switch to the top of the RCCB's aren't RCD protected.
If you have an RCD main switch or Isolator the it's ok.
That's my interpretation of it anyway, I may well be wrong.
 
OSG Pg.40 says:

'[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault protection of the single-insulated conductors that connect the load side of the double-pole main switch to the supply-side of the RCCB's.'

Why is there insufficient fault protection here?

I've seen loads of TT systems with RCD protection in them. What would you use instead? I know you can use RCBO's but they're not standard.
Typically, with a split-board consumer unit having one or more 30 mA RCDs for the final circuits, the front-end RCD would be 100 mA, type S (time-delayed) to permit selectivity between RCDs.


However, the cables from the origin of the supply to the input terminals of the RCD were a concern. This was because RCDs don’t protect the cables which supply their input terminals. This means that a line to earth fault on the supply side of the front-end RCD could go undetected.

Where a metal consumer unit is installed, there’s always the risk, however small, that the metal enclosure – and other exposed-conductive-parts – will make contact with a live conductor, causing the metalwork to rise to a potential approaching that of the line voltage of the supply.


The relatively high external earth loop impedance in TT systems might mean that the service cut-out fuse would not operate within the maximum permitted time of five seconds, permitting a dangerously high potential to remain on all the earthed metalwork of the installation.

Consequently, you needed to be sure that any exposed metalwork couldn’t be made live by a fault ‘before’ the RCD, caused either by an insulation fault or by one of the conductors becoming loose.
 
Last edited:
Typically, with a split-board consumer unit having one or more 30 mA RCDs for the final circuits, the front-end RCD would be 100 mA, type S (time-delayed) to permit selectivity between RCDs.


However, the cables from the origin of the supply to the input terminals of the RCD were a concern. This was because RCDs don’t protect the cables which supply their input terminals. This means that a line to earth fault on the supply side of the front-end RCD could go undetected.

Where a metal consumer unit is installed, there’s always the risk, however small, that the metal enclosure – and other exposed-conductive-parts – will make contact with a live conductor, causing the metalwork to rise to a potential approaching that of the line voltage of the supply.


The relatively high external earth loop impedance in TT systems might mean that the service cut-out fuse would not operate within the maximum permitted time of five seconds, permitting a dangerously high potential to remain on all the earthed metalwork of the installation.

Consequently, you needed to be sure that any exposed metalwork couldn’t be made live by a fault ‘before’ the RCD, caused either by an insulation fault or by one of the conductors becoming loose.
Ok but how is this different with RCBO's?

And what's the difference between a normal 100a main switch in a CU and an S Type RCD?

It's amazing how many of these i've worked on without knowing anything about them.
 
Last edited:
They are standard for me, and plenty of other sparks. I will not install a split load board anymore, as the RCBO boards are so much cheaper to buy now, and are infinitely superior.

The only sparks to be fitting them now are the John Wayne ones.

The likes of screw fix and tool station still punting them out cheap as chips type AC rcds no spd they should be ashamed.

I like the Fusebox range.
 
The only sparks to be fitting them now are the John Wayne ones.

The likes of screw fix and tool station still punting them out cheap as chips type AC rcds no spd they should be ashamed.

I like the Fusebox range.
I worked on a 1700-home council refit earlier this year where every single board was split RCD.

I also worked on several premium new builds (you know the ones where they use nice insulation instead of the stuff that itches and it comes with triple-glazing?) that used them too.

Scandalous really.
 
They are standard for me, and plenty of other sparks. I will not install a split load board anymore, as the RCBO boards are so much cheaper to buy now, and are infinitely superior.
Agree havnt fitted a split load for at least 4 years I reckon
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
swaRRR,
Last reply from
Tart83,
Replies
79
Views
9,085

Advert

Back
Top