Evening all...

I have just got back from a CU change. All was going very well and I was finishing early which was lovely for a friday evening, and then.......

The RCD on the opposite side to the lights trips when the lights are switched on... arghh. I eventually found the problem, I had screwed through the shower cable when attaching the CU to the piece of wood I was using to hang it on.

Whilst the screw was still through the shower cable (touching N-E) why did this stop the test button from working on the RCD? There was 240V going through the RCD and by using something on the other side of the dual RCD board it would trip, but it would not trip with the test button?

Cheers.
 
Found this diagram I had drawn earlier whilst I was starting to search for a diagram to work from to draw just this diagram. (or whatever) test current can go through the fault and by pass the sensing coil.
RCD test no trip.jpg
 
I know some of the information and can sometimes manage to waffle enough to put it across, but looking at the blank incomprehension I might receive I would kill too many students if they were within reach, it is safer online!
Yours has always been appreciated input and having helped innumerable posters, increasing a depth of knowledge that this industry requests.

Sounds a bit creepy but honestly intended.
Now the chanting of, ‘for He’s a jolly good fellow’, would take it to the realm of creepy!
(Song is stuck in my head now!)
 
Yours has always been appreciated input and having helped innumerable posters, increasing a depth of knowledge that this industry requests.

Sounds a bit creepy but honestly intended.
Now the chanting of, ‘for He’s a jolly good fellow’, would take it to the realm of creepy!
(Song is stuck in my head now!)
Thank you, glad it has been of help.:)
(Chanting not needed!)
 
it's saturday, raining, nothing to do, so, for your entertainment ( turn the volume up) and enjoy.

 
And I'd like to flip this on it's head and ask why a Memera RCD pod would trip with the test button, not when tested with my MFT from the terminals with nothing connected but then work 100% (bit slow at rated fault current ~ 50ms, but still acceptable) when tested from a newly installed double socket?

I usually test RCDs at the board with nothing connected, but this had me all confused this morning :)
 
The line conductor must pass through the pod where there is a sensing coil. Connecting direct to the terminals with any tester will not activate it unless your test lead passes through the pod tunnel. If you want test at the board make an extension socket with fly leads to connect at the device.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Why was the RCD test button not working?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
telectrix,
Replies
19
Views
12,845

Advert

TrueNAS JBOD Storage Server

Back
Top