I realise many threads have been discussed around the (maximum) figure of 200Ω for external earth fault loop impedance (as given by BS7671) on a TT, however I'd be interested to see what proportion would and wouldn't accept this figure.

Hopefully we wont get into semantics of was it a dry day, wet day etc. Its just a straight forward simple poll seeing how many would accept the figure given by BS7671.

This will be an anonymous poll.

EDIT : I SHOULD HAVE SAID :

"WOULD YOU ACCEPT A Ze OF 199 Ω ON A tt INSTALLATION WHICH ALSO HAS RCD PROTECTION"
 
Last edited:
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Should the option on the poll be below 200 ohms?

Yes.. bugger!

Can You change it mods?

I should have put 'Would you accept a Ze = 199Ω on a TT Installation which also has 30mA RCD protection'.

Hopefully you'll all see this and vote accordingly :smile5:
 
Last edited:
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

I'd be hoping to get a lower reading than that however most books say max value for a tt is 200 ohms
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

200 no


199 yes.

unless you are with the NICEIC and then its

100 no


99 yes

:rant::rant::rant:
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Does everything need to be a poll?

We'll be having designs put to a poll soon!
Like any other thread, you have the option to ignore it if it doesn't interest you.

If it interests nobody it'll soon drop off the bottom of the page....
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

And I'd like to think that all TT systems will have an RCD, multiple RCD's in fact. Even if they meet TN readings I'd still be inclined to have an upfront Type S RCD...
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Just don't show it to Tony Cable.
He will only frown at you for not listening to those who are above and beyond BS 7671.
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

Yes.. bugger!

Can You change it mods?

I should have put 'Would you accept Ze = 199Ω on a TT Installation which also has 30mA RCD protection'.

Hopefully you'll all see this and vote accordingly :smile5:

Do you mean Ra
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

let's put this stupid 200Ω myth to bed once and for all. it is NOT a max. figure in BS7671, which clearly states that a value above 200Ω is liable to be unstable. there is no mention of a max. figure in any BS7671.

for the record, i'd not accept it and i can't vote in the poll as there is a forum glitch. paul m is looking into it.
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

let's put this stupid 200Ω myth to bed once and for all. it is NOT a max. figure in BS7671, which clearly states that a value above 200Ω is liable to be unstable. there is no mention of a max. figure in any BS7671.

for the record, i'd not accept it and i can't vote in the poll as there is a forum glitch. paul m is looking into it.
Tel why is your text getting so small. (PS I've bought the bloody bonneville!!!!!)
 
Re: Would you accept a Ze of 200Ω on a TT Installation which also has an RCD.

I would want to see reading of less than 10, so keep swinging that hammer!!
 

Reply to Would you accept a Ze of 199Ω on a TT Installation which also has an RCD. in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
958

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top