rcd get stuck if you dont test them regular. i,ve been bit by one myself.but the fact remains 1667 ze 0.2 disconnection.who are we to judge
 
Well I am just waiting for the first test case for a fatality due to an RCD not operating and saving a life, I fitted a Power breaker RCD/FCU the other day, guess what >400ms over range about as much use as a fridge to an Eskimo, if a domestic inspect is 10 Years on a new install with the lower lethal level of 50ma what's the chances of it operating in <30ma 9 years time ?..None.
I retested mine at home today all come in at under <19ms @ x5
 
Energy let through limitation
The supply is 50Hz, i.e., 1 cycle every 20ms, even if the RCD can disconnect at 40ms, you'll get 2 cycles of the full fault current
A typical fault can be in hundreds of amps

This from another source

The surge current refers to the peak current an RCD is designed to withstand using a test impulse of specified characteristics ( an 8/20 µs impulse, named after the time constants of the rise and fall of current).
The IEC 61008 and IEC 61009 standards impose the use of a 0.5 µs/ 100 kHz damped oscillator wave (ring wave) to test the ability of residual current protection devices to withstand operational discharges with a peak current equal to 200 A.


These are others quotes and I just take note of them, bright ideas are rare coming out of my head unfortunately :)
I read those as saying to me.an Rcd faulting on a Tn system is liable to damage


Des could you please explain why it would be more dangerous on a TN?

low Zs of the TN would have virtually just the persons resistance as the limiting factor,kallowing a massive current flow
High resistance TT rod would limit the current flow
Both could kill,but the Tn would do a better job of it:)
 
To be pedantic, if that's the right word, the actual value is 1666.66 recurring. Therefore, to be on the 'safe' side we should be using 1666? 1667 gives a voltage of 50.01 - far too high!

Seriously though, I can see the logic on both sides of the argument. However, the maximum Zs is to protect the cpc. So, if we accept that the RCD may fail, should we still not use the maximum Zs for the MCB (or OC part of an RCBO) on a TN system just in case?
 
1667 is for TT systems.
On a TNS system the mcb or rcbo is your method of complying with 411.3.2.2 & you use table 41.3
The rcd is for additional protection so 1667 does not come into it.

Table 41.5 is for TT systems.

It is alo for TN system Reg 411.4.9 comes under TN. Under this reg table 41.5 can be used in a TN
 
A lot of people don't even realise this reg is under the TN section. When the 7671-2008 came up as DPC I wrote to the IET with several questions and this was one. Why start the TN section back on page 47 under 411.4 and end it on a TT page 411.4.9. pg 50

Told in short shrift that 411.4.9 is obviously still under TN as TT starts the 411.5 section!!! hush my mouth
 
Well I am just waiting for the first test case for a fatality due to an RCD not operating and saving a life, I fitted a Power breaker RCD/FCU the other day, guess what >400ms over range about as much use as a fridge to an Eskimo, if a domestic inspect is 10 Years on a new install with the lower lethal level of 50ma what's the chances of it operating in <30ma 9 years time ?..None.
I retested mine at home today all come in at under <19ms @ x5


RCD failing to trip? that's as unlikely to happen as the "unsinkable " Titanic sinking, or the Hindenberg catching fire! Personally , i consider RCDs to be secondary protection , albeit 95% reliable
 
b=5x c=10x d=20x
zs = nominal voltage/Ia (current causing automatic disconnection) x0.8
examples of making disconnection times with various mcb types
eg b32
b x 5=160 230/160=1.43 x 0.8 = zs max of 1.15ohms
eg c20
c x 10=200 230/200=1.15 x0.8 = zs max of 0.92ohms
eg d16
d x 16=320 230/320=0.71 x 0.8 = zs max of 0.57ohms

c and d type breakers are used for circuits with high inrush currents

ive gotta get out more!
 
b=5x c=10x d=20x
zs = nominal voltage/Ia (current causing automatic disconnection) x0.8
examples of making disconnection times with various mcb types
eg b32
b x 5=160 230/160=1.43 x 0.8 = zs max of 1.15ohms
eg c20
c x 10=200 230/200=1.15 x0.8 = zs max of 0.92ohms
eg d16
d x 16=320 230/320=0.71 x 0.8 = zs max of 0.57ohms

c and d type breakers are used for circuits with high inrush currents

ive gotta get out more!

That's a great formula but would it still apply to bs88 fuses?
 

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
564
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
342

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top