Consumer unit change with a fault! | Page 5 | on ElectriciansForums

Discuss Consumer unit change with a fault! in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,277
Reaction score
5,772
Location
Gloucestershire
Evening all..

I have just changed a CU. I did find a neutral - earth fault prior to the change so I thought I would probably have a tripping RCD.. which I did!

My dilema is how do I proceed with the paperwork?

I'm going back tomorrow morning to do all of the testing and I shall give the required certificates (with a note on regarding neutral/earth fault on downstairs lights), but I get the feeling the chap is going to hunt for the fault himself, the reason being it will require the floorboards being taking up and he doesn't want to incur anymore cost (fault is in a junction box(s), under the floorboards that someone has kindly wired all the downstairs lights from - took me a while to figure this out!)

The main point being that the work is notifiable, but I cant notify it if it still has faults! How do I proceed?

I realise I should have perhaps corrected the fault before the CU change, but the chap just wanted the new CU in and due to my inexperience I wasn't sure if the new CU would trip!

Cheers...
 
Trouble is though Onions if you read the OP again especially the last paragraph it is pretty worrying, I too 100% Agree with Glenn, he is trying to drum home to HHD just how dangerous his work can be, the fact he was hoping the fault wouldn't trip the board even though he knew it was there is absolutely shocking and he needs to know that even if he is a liked member here.

I did find the bit about turning it on and guess what it tripped bit slightly bizarre. So the OP should also learn not to share everything on open forum some things are best kept to yourself. HHD I wouldn't ever tell you my deepest darkest secrets.

- - - Updated - - -

A dual with spades on the M1 sounds a tad on the dangerous side
 
I did find the bit about turning it on and guess what it tripped bit slightly bizarre. So the OP should also learn not to share everything on open forum some things are best kept to yourself. HHD I wouldn't ever tell you my deepest darkest secrets.

- - - Updated - - -


A dual with spades on the M1 sounds a tad on the dangerous side
thats the bit that got me started to be honest...

i just looked at it and thought `are you going to cast a spell on the damn thing` or summat like that...
 
glenns so hardcore he actually lives on the M1 , just under a bridge past jct 10.

;-)
wherever you may roam:

[ElectriciansForums.net] Consumer unit change with a fault!

and before theres any snyde comments winging their way over from you biff just remember thats my home your callin..
 

Reply to Consumer unit change with a fault! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
354
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top