pme | Page 7

pme

  1. Robertbaker63

    application for pme

    Hi one of my customers have contacted western power distribution about getting pme installed as there is no reading when an earth stake is installed they have done a site visit and have asked their electrican (me) to do send of a request form i have trawlled the website and cannot find the...
  2. stidge

    Free PME

    Arranged for an elderly couple to have a PME installed,Rang Western Power with credit card ready , Employee didn't mention paying (usually between ÂŁ120/150).anyway they have been and fitted all good, couple didn't have to sign or pay ! Nice bonus for them . Have never come across this before and...
  3. T

    Pme query

    Hi all , went to look at a job today..... Main house with PME all good bonding etc. The detached garage and workshop also has a separate PME supply. Inbetween main house and detached garage they have built a one bed granny annexe, this links the two buildings but with no access through to...
  4. Midwest

    PME supplies to emote buildings

    I've previously posted about doing a CU replacement for my assessment. I will also have to re-supply a small garage CU (20a radial + 6a lighting), which has been answer for me, thank you. The property has a TN-C-S supply, which will be fed with new 25mm tails, 16mm EC. The garage is link...
  5. T

    NO EARTH FOUND ... can I change my system to pme myself?

    Think the builder ripped the earth rod out... Whatever happened there's not an earth now. Instead of installing a new one am I allowed to take the neutral from the metre and connect a main earthing conductor in a henley block. The street does have pme available, I checked. Is it legal though???
  6. M

    pme ordered but need to change cu asap

    Hi all, long story short... viewed cu upgrade job and realized non dno pme connection - ze showed 2.2 property just fully decorated and cleaned...as usual! client has tenants moving in before pme can be done but has been ordered to dno nightmare trying to install a rod for TT due to layout...
  7. T

    PME Earth Impedance and RCT times - advice ;-)

    Hi all, great site and sorry for the long post - I'm after some advice as I don't have total confidence in the 4 sparkies I've currently used with regards to the test results on my cert. That said I am not a sparky and if I'm being a total muppet please tell me - I can take it :-)...
  8. D

    PME final circuits question

    I have a query, Im working on some signage that is connected to a PME supply. This is supplied to a leb header by straight concentric 16mm cable and then to and RCD with outgoing circuits to the sign. Now I have just seen that work by others have been carried out in the form of doubling up on...
  9. E

    PME supply

    Hi All, Could anyone tell me why you can't have a PME supply within a metal garage/shed?
  10. B

    PME Swimming Pool, Pond, and Jaccuzi

    Went to look at a job the other day, The customer wants some "electrics" installed for his swimming pool, pond, and jacuzzi. Had a quick look at the existing Jacuzzi supply: this is tapped off of main tails (henley blocks), into Seperate RCD enclosure with 40A MCB. Unable to locate bonding...
  11. B

    pme earthing

    can i take pme earthing outside of a commercial building to supply some containers or am i right in thinking its treated as the same as domestic and i only take live and neutral out and put an earth rod in local to my new supply?
  12. Mr Mark Sparks

    Export pme to portakabin

    Hi factory unit with 800 amp supply 95 mm main earth and 50 mm main bonds portakabin has been delivered as a permanent addition wired on 10 mm 3 core swa and 32 a commando plugs there is a water supply and metal parts. am I right in saying that it will need to be put on a stake as the main...
  13. S

    Export PME or not that is the question?

    So guys I know that this is a frequentley asked question but which way would you do it? The building that requires power installing has extraneous parts by the way. Would you. 1. Devorce the PME earth from the house and install a spike. 2. Use the PME earth from the house within your...
  14. H

    Pme and over head supply

    can you have a PME from a over head supply?
  15. P

    PME and isolators

    Who is responsible for fitting the above, I always thought a supplier could install both. But just been speaking to EON on behalf of a customer and they say they can fit a isolator but it is up to to the DNO to install the PME. :dunce:
  16. K

    PME & Broken neutral

    I know some countries use protection to guard against a broken neutral in PME systems. Anyone know how they work?
  17. S

    Exporting PME to outbuildings

    Hi all, Just wanted to run this past some people, its for a little job im doing (possibly by moonlight). The property has recently (yesterday) been converted to PME when the DNO changed the cut-out. It is a farm and ususally around here they will not give PME to farms. The old service was TNS...
  18. S

    pme export

    its advised to install an earth rod not compulsary unless there is a window in the roof where direct contact could occur, there is argument that bonding class2 equipment could cause a potential too. if the array is not accesible i wont be installing any earth electrode in these circumstances as...
  19. S

    PME install, no CPC

    Hi guys, I've been called to look at a flat in north London. The flat is in a converted piano factory. Looking at the CU, perhaps installed in the 70's or 80's, it has a CPC. All good. Under the CU is a termination box of some description. The tails come up, through metal conduit, into...
  20. D

    ZS in a PME earthed household

    Please be gentle with me it's been a long day. In my previous life I was an electrician, suppose I still am but not practicing installation work. So I am trying to get up to speed with some modern practices, mainly Earth Loop Impedence. In my daily work I constantly use a megger for safety...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top