P 24 of the OSG shows a 100ma T/D RCD used as a main switch on a TT system,on a split load DB with only some final circuits 30ma protected.....I cant see how this can comply with 314.2 because a fault on any of the circuits not on the 30ma side will trip the whole installation.
it may be better to test with fault current imo - before pressing the test button
what do you think?
I have recently renewed a CU on a TT system.
100mA RCD as main switch in meter cabinet with wylex rewireables.
Therefore converted to PME, new, dual RCD CU, left 100mA in situ.
Couldnt really see the point in ripping that out and replacing with a main switch.
Who did this you or the supply authority?