Still don't agree that 100mA/300mA/500mA etc. time-delayed RCD can't be used as a main switch.

Minimising inconvenience in the event of a fault doesn't require there to be no protection in the event of a fault.
 
P 24 of the OSG shows a 100ma T/D RCD used as a main switch on a TT system,on a split load DB with only some final circuits 30ma protected.....I cant see how this can comply with 314.2 because a fault on any of the circuits not on the 30ma side will trip the whole installation.


A T/D RCD clearly can be used as a main switch as per the OSG I quoted above.
However a fault on the main switch side would trip the entire installation including the 30ma protected circuits in the arangement shown in the OSG.
This is somewhat contradictory to 314.2:confused:
 
it may be better to test with fault current imo - before pressing the test button

what do you think?

On my NIC inspection I had a note on my assessment sheet for pressing the test button before testing with the meter. Apparantly it could damage it and it should only be tested last after the other tests have successfully been completed.
 
I have recently renewed a CU on a TT system.

100mA RCD as main switch in meter cabinet with wylex rewireables.

Therefore converted to PME, new, dual RCD CU, left 100mA in situ.

Couldnt really see the point in ripping that out and replacing with a main switch.
 
100mA TD upstream and all final circuits having 30mA protection then it shouldn't give trouble

SP rcbo's downstream might take out a DP rcbo as the N-E fault isn't cleared by them
 
Last edited by a moderator:
I have recently renewed a CU on a TT system.

100mA RCD as main switch in meter cabinet with wylex rewireables.

Therefore converted to PME, new, dual RCD CU, left 100mA in situ.

Couldnt really see the point in ripping that out and replacing with a main switch.


Who did this you or the supply authority?
 
we used to have a dodgy TT system here at one stage( pre-rcd days)

i think the TT with all circuits 30mA protected may be safer than T-N-C-S

you'd need to confirm suitability-suppliers neutral multiple grounding and secure connnection to trafo

wouldn't be desirable to be the sole tn-c-s in a TT area either
 
Last edited by a moderator:
The brand is 3-IN-ONE professional, high performance lubricant.

Drives out moisture
dramatically reduces frition and wear


Isn't spraying a flammable liquid onto a area where arcing is going to be present something of a fire risk?

Better to use some teflon cycle lubricant in a pump not an aerosol.
 

Reply to 100ma RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top