19.1ka psc reading on a 2 bed small house!

So a message for some sparks, more experienced than moi!...

I've never seen this scenario, so how would you get around it?
All I can think of is a 100amp BS1361 (33kA) protecting the installation after the suppliers main fuse, then into your CU as normal.
 
So a message for some sparks, more experienced than moi!...

I've never seen this scenario, so how would you get around it?
All I can think of is a 100amp BS1361 (33kA) protecting the installation after the suppliers main fuse, then into your CU as normal.

BS88 fuse, has 80Ka breaking capacity
 
Would my method ensure compliance?

I think the most I have ever seen was 10/11kA. Block of flats, tranny on site.

Edit:

Do the smaller rating BS88s still have 80kA breaking cap?
 
Last edited by a moderator:
Fuse back-up protection to 16 kA is a mandatory test for the incoming device, protective devices, connections, and any other item in a Consumer Unit complying with BS EN 60439-3 Annex ZA & BS 5486-13.

This is a conditional rating, as the conditions specifically relate to the use of an upstream BS 88-3 (formerly BS 1361) 100 A fuse.

 
Last edited:
I've never seen this scenario, so how would you get around it?
.

Too high a pfc could be a down side of unnecessarily upgrading meter tails. Lot of people seem to think if they are not 25mm² then they must be upgraded, but there is a down side.

Not getting round it as such, but possibly preventing it from happening.
 