Code C2 for missing blank plate.Which are totally open to interpretation.
Code C1 for exposed ‘live’ conductive parts.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Code C2 for missing blank plate.Which are totally open to interpretation.
Not sure how bins, radiators etc. would meet the BS7671 definition of exposed conductive parts... They don't form part of the electrical installation.It’s not an interpretation, it’s an application of the Regulations as written.
A metal CU does.Not sure how bins, radiators etc. would meet the BS7671 definition of exposed conductive parts... They don't form part of the electrical installation.
Yes a potential danger which is not the standing of a Code 1.
I think the Code definitions are poorly defined. Code 1 Danger present, what does that actually actually represent. Code 2 Potentially dangerous is clear that there is potential for an incident. An mcb blank missing offers a potential to danger.What would you consider a C1?
I think the Code definitions are poorly defined. Code 1 Danger present, what does that actually actually represent. Code 2 Potentially dangerous is clear that there is potential for an incident. An mcb blank missing offers a potential to danger.
So what is Danger present?
I think with that argument Westward there would never be a C1 as you could argue that a CU with it's cover left off is only 'potentially' dangerous.Yes a potential danger which is not the standing of a Code 1.
This is my point on the Code definitions. Separate Danger Present and Potentially Dangerous, they walk the same path to a hazard. What is Danger Present, something Potentially Dangerous.I think with that argument Westward there would never be a C1 as you could argue that a CU with it's cover left off is only 'potentially' dangerous.
Reply to Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net