Calculating volt drop, cable selection and mcb selection on an 3kw motor
ok here i go :
For deign current : 36.1 A
In : 40A
Ok..... here goes...
Ca : 35 oc...... : factor of 0.94....table 4b1 ?
Cg : 0.82........table 4C1 ???
so ...It = 50.8 A ...????
Im lost as to where i go from here....
I can do the volt drop calc....but i cant suss how to find the correct table for the cable selection ?
how do you get 36.1A for a 3kw motor?
Ib -
Ib = Power / SQUARE ROOT of three x Uo = 36.1 A
In = Greater than Ib = 40A breaker
It : = In / Cg = 40 / 0.82 (table 4c1) ......It = 48.78 A
(these values have changed)
Cable : 4mm cable (Table 4G1A , column 9) ?????????????????
daiplayer,
Dan,