A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
“ Certification& Reporting “ :presents3:

Listfour characteristics of the Electrical Supply that should be recorded on theDocument - this could come Up on-&-s .

313 – Supplies .

313.1. General The followingcharacteristics of the supply or supplies . from whatever source . & thenormal range of those characteristics where appropriate . shall be determinedby Calculation . Measurement . Enquiry or Inspection .

i) The nominal voltage(s) & its characteristics includingharmonic distortion .
ii) The nature of the current & frequency .
iii) The prospective short-circuit current at the Origin of the installation. ◄
iv) The Earth Fault Loop Impedance of that part of the systemexternal to the installation ( Ze )
v) The suitability for the requirements of the installation .including the Maximum Demand .
vi) The type & rating of the overcurrent protective device(s)acting at the Origin of the installation . ◄

These characteristics shall be ascertained for an External Supply& shall be determined for a private source . These requirements are equallyapplicable to main supplies & to safety services & standby supplies . ◄

NOTE : The above information should be provided by distributors’on request ( see Appendix 2 sec 2 )

Appendix 2 – Informative ) Some things have been Changed . inWording .

Definitions- p/39 . ( Ze )
That part of the Earth Fault Loop Impedance which is External tothe Installation ( Ω ) 313.1.


 
Fundamental requirement to understandthe basic principles . Measured / Calculated results and what affect they haveon a circuit . :rofl:

Conductor Résistance .

Whywe divided the Length ( x . mΩ/m figuresby ( 1000 )

Wedivided the length ( x . mΩ/m figures by ( 1000 ) to obtain a résistance value in Ohms .

O.S.G.– 9A )- milli-ohms per meter values . Weneed to covert them to Ohms for our Calculations’ ( dividing by 1000 does this )



 
Chapter 61 :

Initial Verification – Inspection 611 & Testing 612

Initial Verification [ Inspection & Testing ] Therefore helpsto ensure that Electrical Installations are Safe before being put into Service.

611 )- Inspection .

611.1. – Inspectionshall precede Testing & shall normally edone with that part of the installation under Inspection disconnected from theSupply . ◄◄


 
Therequirements of BS-7671:

BS-7671requires that every installation shall be Inspected& Tested to verify that the Regulation(s) havebeen met before [ Being put into Service ]

On completion of an installation or an addition or alteration toan installation . appropriate Inspection & Testing shall be carried out toverify so far as is reasonably practicable that the requirements of thisstandard have been Met .

133.2.1. Voltage :
Electrical equipment shall be suitable with respect to the maximumsteady-state voltage ( r/ms value for a.c. ) likely to be applied . as well as overvoltage’slikely to occur .

Note : for certain equipment . it may also be necessary to takeaccount of the lowest voltage likely to occur .

610.1. Every installation shall . during erection & oncompletion before being put into service . be inspected 7 tested to verify . sofar as is reasonably practicable . that the requirements of the regulation(s)have been Met .

Precautions’ shall be taken to avoid danger to persons &livestock . & to avoid damage to property & installed equipment . duringInspection & Testing .

612 )- Testing . InitialVerification .
612.1. General .
The tests of regulation 612.2. to 13 . Where relevant . shall becarried out the results compared with relevant criteria .

The Test of Regulation(s) 612.2.1. to 612.6. where relevant shall be carried out in thatorder before the installation is Energised .

If any Test indicate a failure to comply . That Test & any precedingTest . the results of which may have been influenced by the fault indicated .shall be repeated after the fault has been rectified

Three Important Tests .

612.2. – Continuity of Conductors .
612.2.1. - Continuity of Protective Conductors including main& supplementary equipotential bonding .

A continuity test shall bemade . it is recommended that the test be carried out with a supply having a (No-load ) voltage between 4V & 24V .ETC.

612.2.2. Continuity of the Ring Final Circuit Conductors .

Your Earthing is your First Line of Defence . ◄◄ :19:
 
( T ) 134.2. InitialVerification . -&-s :19:

134.2.1. During erection& on completion of an installation or an addition or alteration to aninstallation .
& before it is put into service . appropriate inspection &Testing shall be carried out bycompetent persons to verify that the requirements of this Standard have be Met.


 
Exclusions from Scope . 702.11.

Except for Areas designed especially for Swimming Pools . The requirementsof Section 702 . Do Not Apply to .

Natural waters . Lakes or Coastal Beaches .

 
(T) 711.6. Inspection& Testing .

All TemporaryElectrical Installation(s) ofExhibitions .
Shows& Stands are required to be Inspection& Tested in line with Chapter 61 after EACHASSEMBLY on SITE.

First Amendedment . No change . 711.6.
 
What is the Maximum value of Insulation résistanceof a 230V lighting circuit .

( 1MΩ ) - 612.3.2. – Table 61. 500V / d.c. . -&-s . 2392-10 :19:

612.3.2.
The insulation résistance measured with the test voltage(s) indicatedin Table 61 . shall be conceded satisfactory if the main switchboard and eachdistribution circuit tested separately . with all its final circuit(s)connected but with current-using equipment disconnected . has an insulation résistancenot less than appropriate value given in Table 61.

Note 2 . Insulation résistance values are usually much higher thanthose of Table 61.


Whichof the following is Verified by the Polarity Test . -&-s . 2392-10

A) That there is a separation of live partsfrom other circuit(s) & from earth .
B) The Phase sequence of multi-phasecircuits is maintained throughout the installation .
C) Every fuse &single-pole control & protective device is connected to the line conductoronly . 612.6. & 612.1. :19:
D) All assemblies are properly mounted .adjusted . & installed correctly as required by the reverent regulation(s) .

 
Which IET Guidance Note . describes methods of Testing ElectricalInstallation(s) ◄► -&-s

IET Guidance Note 1
IET Guidance Note 2
IET Guidance Note 3 ◄◄ :19:
IET Guidance Note 4

 
Taken for old Notes .

Calculationwhen the protective device is an RCD orRCBO . :rofl:

ResidualCurrent Devices ( RCDs )

Wherethe installation is part of a TN-system . the basic requirement is given in Regulation 411.4.5. i.e..

Zs x Ia ≤ Uo volts.

Foran RCD ( Ia ) is the rated residual operatingcurrent providing disconnection in the required time .

ForTT systems the additional requirement that ( Ra x I∆n ≤ 50V )is given in regulation 411.5.3. In this requirement ( Ra ) is the sum of the earth electrode résistanceof the protective conductor connecting it to the Exposed Conductive Parts .

Inthe above expression . of course . ( I∆n ) is in amperes . limitingconsideration to residual current circuit breakers ( RCBOs ) to BS-EN 61008 . the values of ( Zs ) & ( I∆n ) encountered in practice are such that there is no difficulty in meeting therequirement given above .

Theearth fault current is limited by the value of ( Zs ) & will be of the same order as occurs when fault protection . is provided byOvercurrent protective devices . It should be checked that the RCD complieswith Regulation 531.2.8. which requiresthat it is capable of withstanding without damage the Thermal & Mechanical Stresses caused by the earth faultcurrent .

Ifan ( RCCB ) to BS-EN 61008 does notincorporate an intentional time delay it is required by the British Standard tooperate within ( 0.04 sec ) at aresidual current of ( 5 I∆n A ) &the designer merely has to check that the circuit is Thermally protected forthat time .

531.2.8.

Wherean RCD is used for fault protection with . but separately from . an Overcurrentprotective device . it shall be verified that the residual current operateddevice is capable of withstanding . without damage . the Thermal &Mechanical Stresses to which it is likely to be subjected in the case of afault occurring on the load side of the point at which it is installed .
 
BS-7671:2008. does not Demand that diversity be taken into account but . for the economicdesign of an installation . diversity cannot be ignored .
Thediversity factors used must be optimistic . an adequate margin of safety mustalways be allowed .

Asindicated in Regulation 433.1. whichgives the general requirement concerning Overload protection .
Circuitsshall be so designed that small Overloads of long duration are unlikely toOccur .

 
Inspection: 2392-10

Carryout the Initial Verification ( Inspection . Testing & Certification ) of aninstallation to BS-7671:2008

As -&-s rightly asks the Q/As . State the Human Senses that may need to be employed the Initial Verification of an Installation .

Definitions p/29Inspection : Examination of an Electrical Installationusing all the Senses as Appropriate . BS-7671:2008 . Amendment No 1 :2011

2392-10. Fundamental Initial Verification of ElectricalInstallation(s) - Three areas to this Unit . :19:
Preparationfor Initial Inspection & Testing .

Inspection.
Testing.
 
General Requirement : :19:

Regulation 6101. ( p/156) - ( p/189)

Every installation shall . during erection and/or on completion beforebeing put into service be Inspected & Tested to verify . so far asreasonably practicable . that the requirements of the Regulation have been Met.

As an Inspector 2391-10 :2392-10 : )- The reason(s) for an Inspection & Test of an ElectricalInstallation is to verify that the installation complies with the Regulationswith regards to its ( Design & Construction )

Asan Inspector )- Carrying out the Inspection to for fill these requirements the Regulations . Call forthe following information to be “ MADE AVAILABLE

Results of the assessment of General characteristics required bySection(s) ( 311. 312 . & 313 . )

Youare looking at .

313.1. General The followingcharacteristics of the supply or supplies . from whatever source . & thenormal range of those characteristics where appropriate . shall be determinedby Calculation . Measurement . Enquiry or Inspection .

i) The nominal voltage(s) & its characteristics includingharmonic distortion . ◄
ii) The nature of the current & frequency . ◄
iii) The prospective short-circuit current at the Origin of theinstallation . ◄
iv) The Earth Fault Loop Impedance of that part of the systemexternal to the installation ( Ze ) ◄
v) The suitability for the requirements of the installation .including the Maximum Demand . ◄
vi) The type & rating of the overcurrent protective device(s)acting at the Origin of the installation . ◄

These characteristics shall be ascertained for an External Supply& shall be determined for a private source . These requirements are equallyapplicable to main supplies & to safety services & standby supplies . ◄

Regulations call for the informationto be made available . ( 514.9. )
( Provide all the necessaryinformation as to circuit type . number of points & their positions . cablesizes . protective device types & their ratings . )

InitialInspection :
611.1. ( p/156 ) – ( p/189 )

Inspectionshall precede testing & shall normally be done with that part of the ( Installation Disconnected from the Supply ) ◄◄◄◄◄◄

Just a Reminder !

Regulation(s) states134.1.1. ( p/19 ) – ( p/21 )
Good workmanship by a Competent Person or Persons under theirsupervision & proper materials shall be used . in the erection of the electricalinstallation . Electrical equipment shall be installed in accordance with theinstructions provided by the ( MANUFACTURES of the EQUIPMENT )

Regulation 612.2. ( p/159 ) – ( p/191 )
Calls for the inspector to confirm that equipment has been selectedin accordance with Section 511 . of theWiring Regulations . & the equipments compliance with the relevant Britishor Equivalent Standard .
 
2392-10:

Of what use to us is the Measuring of Earth Fault Loop or ( Zs ) of the circuit .

Ifwe know the value of it we can use “ Ohm(s) Law “ to calculate the Fault Current that will flow. ( if a FaultOccurs )

Formulawe can apply is ( Voltage = Current ) Résistance .

Wecan see that Fault Current & EarthFault Loop Impedance are directly linked . The lower the Earth Fault Loop theHigher the Fault Current & Vice Versa .
Therefore - The lower the Earth Fault Loop / The Higherthe Fault Current . The quicker the Protective Device will operate to cut theCurrent .

Ifwe limit the Maximum Value of the Earth Fault Loop we can be confident that theFault Current will be of a Higher Magnitude to operate the protective device .
Regulation– 411.3.2. :- Automatic Disconnection inCase of a Fault .

 
Inspector - has responsibilityplaced upon him as to the Safety of the Installation .
Visual Inspection )- is Essential to assess the safety of anInstallation before testing takes place .

Verification . All measures by means of which compliance of the electricalinstallation with the relevant requirements of BS-7671 are checked .comprising Inspection . Testing & Certification .
 
Justa Reminder . 2392-10

612.2.2. Continuityof the Ring Final Conductors’ . :19:

A “ Test “ shall be made to “ Verify “ the Continuity of Each Conductor includingthe Protective Conductor . of every Ring Final Circuit .

 
Justa Reminder . 2392-10

RingFinal Circuit )- Correctly connected . Ring Final Circuit showing ( Equal Current on Each Leg of the “ Ring “ ) :19:

 
Justa Reminder . 2392-10

( IR ) Insulation Résistance Testingrequires different test voltages for “Certain Circuits “ indentify what circuit(s) require the following voltages . 250V. 500V . 1000V

Isall in the Wording . -&-s



 
Competent. Persons responsible for Inspection & Testing . :19:

Competent person . A person who possesses sufficient technicalknowledge . relevant practical skills & experience for the nature of the electricalwork undertaken & is able at all times to prevent danger & where appropriate. injury to him / herself

Inspection& Testing . of the installation will be your responsible for decidingwhether or not an Installation complies with the Regulations in their Entirety. BS-7671:2008

2392-10:
Regulation. 134.1.1. Therefore the person carryingout the Installation . ( p/19 ) – ( p/21 ) Goodworkmanship by Competent persons or Person . Etc

Regulation . 610.5. Inspection & Testing of any Electrical Installation Work mustcomply . ( 156)
Regulation . 610.5. The Verification shall be made by a CompetentPerson . First Amendedment . ▼▼▼

Competent person . A person who possesses sufficient technicalknowledge . relevant practical skills & experience for the nature of the electricalwork undertaken & is able at all times to prevent danger & where appropriate. injury to him / herself

 
ConditionReport Inspection Schedule for Domestic & Similar Premises with up to 100ASupply .

Final Circuit(s)

Identification of conductors ( 514.3.1. )
Cables correctly supported throughout their run ( 522.8.5. )
Condition of insulation of live pars ( 416.1. )
Non-sheathed cables protected by enclosure in conduit . ducting ortrunking ( 521.10.1. )
□ To include the integrity of conduit & trunking systems ( metallic & Plastic )

Adequacy of cables for current-carrying-capacity with regard forthe type & nature of installation ( Section 523 )
Coordination between conductors & overload protectivedevices ( 433.1. : 533.2.1. )
Adequacy of protective devices . type & rated current forfault protection ( 411.3. )
Presence & adequacy of circuit protective conductors ( 411.3.1.1. : 543.1. )
Wiring system(s) appropriate for the type & nature of theinstallation & external influences (Section 522. )
Concealed cables installed in prescribed zones ( see Section D . Extent & Limitations’ ) (522.6.101. )
Concealed cables incorporating earthed armour or sheath . or runwithin earthed wiring system . or otherwise protected against mechanical damagefrom nails . screws & the like . see Section D . Extent & limitations .( 522.6..101 : 522.6.103. )
Provision of additional protection by RCD not exceeding 30mA .
□ for all sockets-outlets of rating 20A orless provided for use by ordinary persons unless an exception is permitted ( 411.3.3. )
□ For supply to mobile equipment not exceeding 32A rating for use outdoors (411.3.3. )
□ For cables concealed in walls or partitions ( 522.6.102 : 522.6.103. :
Provision of fire barriers . sealing arrangements & protectionagainst thermal effects ( Section 527 )
Band ii cables segregated / separated from band 1 cables ( 528.1. )
Cables segregated / separated from communications cabling ( 528.2. )
Termination of cables at enclosures - indicate extent of samplingin Section D of the report ( Section 526. )
□ Connections soundly made & under no undue strain 526.6.
□ No basic insulation of a conductor visible outside enclose ( 526.98 )
□ Connections of live conductors adequately enclosed 526.5
□ Adequately connected at point of entry to enclosure ( glands .bushes etc. ) 522.8.5.
Condition of accessories including socket-outlets . switches &joint boxes ( 621.2 – ( iii )
Suitability of accessories for external influences ( 512.2. )






 
Examples of items requiring Inspection for an ElectricalInstallation Condition Report .

A Visual Inspection shouldfirstly be made of the External Condition of al Electrical Equipment which isNot – Concealed . :19:

Further detailed Inspection . including partial dismantling ofequipment as required . should be carried out as agreed with the personordering the work . ( 612.2. )



 
State:- Indentify the type of circuit thatwould require the following applied voltages when conducting an Insulation Résistancetest . :19:

i) 250V .
ii) 500V .
iii) 1000V .

i) SELV / PELV .
ii) Systems up to & including 500V .
iii) Systems over 500V but under 1000V .

Short& Simple . -&-s

Locations ) containing a Bathor Shower .

Additional protection for all low voltage ( LV ) circuits by RCD not exceeding 30mA ( 701.411.3.3. )
Where used as a protective measure . requirements for SELV orPELV met . ( 701.4.4.4.5. )
Shaver sockets comply with BS-EN 61558-2-5 . formally BS 3535( 701.512.3. )
Presence of supplementary bonding conductors . unless not requiredby BS-7671:2008 . ( 701.415.2. )
Low voltage ( e.g. 230 volt ) socket-outlets sited at least 3m from zone 1 ( 701.512.3. )
Suitability of equipment for external influences for installedlocation in terms of ( IP ) rating (701.512.2. )
Suitability of equipment for installation in a particular zone . (701.512.3. )
Suitability of current-using equipment for particular positionwithin the location ( 701.55. )

 
AFundamental principle of ELECTRICAL SAFETY is that NO SINGLE FAULT CONDITION should cause ahazardous situation . Plain English .

Asthe FirstAmendment says .

Definitions . Fault Protection . p/28 .
Protection against electric shock under ( Single Fault Conditions)

Note )- for low voltageinstallations . systems & equipment . fault protection generallycorresponds to protection against indirect contact . mainly with regards tofailure of basic insulation . Indirect contact is “ contact of persons orlivestock with exposed-conductive-parts which have become live ( UNDERFAULT CONDITIONS “


 
Electrically Independent Earth Electrodes . p/27

Earth electrodes located at such a distance from one another thatthe maximum current likely to flow through one of them does not significantlyaffect the potential of the OTHER(S) .
 
E.I.C.R.

Current – Using Equipment (Permanently Connected )

• Condition of equipment in terms of ( IP ) rating etc . ( 416.2.)
• Equipment does not constitute a fire hazard ( Section 421 )
• Enclosures not damaged / deteriorated so as to impair safety (621.2. (iii))
• Suitability for the environment & external influences (512.2. )
• Security of fixing (134.1.1. )
• Cable entry holes in ceiling above luminaires . sized or sealedso as to restrict the spread of fire .List number & location of luminairesinspected ( Separate page )
• Recessed luminaires ( Down lights )

1) Correct type of lamps fitted .
2) Installed to minimise build-up of heat by use of “ fire rated “fittings . insulation displacement box or similar ( 421.1.1.1. )
3) No signs of overheatingto surrounding building fabric (559.5.1. )
4) No signs of overheatingto conductors / terminations ( 526.1. )
 
TheImpedance of the Earth connection must be low enough to ensure that sufficient currentcan flow through the protective device so that it disconnects the supply quickly( 0.4 sec ) & Voltage on the Earthconnection does not RISE more than( 50V )

RCDsoperate at much lower Fault Currents . ◄◄◄ :19:



 
701.411.3.3. Additionalprotection by RCDs

Additional protection shall be provided for all circuits of thelocation . by the use of one or more RCDs having the characteristics specified inregulation 415.1.1.
Note : see also Regulation 314.1. ( iv ) & 531.2.4. concerningth avoidance of unwanted tripping . p/166

701.411.3.3. Additionalprotection by RCDs

Additional protection shall be provided for all [ low voltagecircuits of the location ] . by the useof one or more RCDs having the characteristics specified in regulation 415.1.1.
Note : see also Regulation 314.1. ( iv ) & 531.2.4. concerningthe avoidance of unwanted tripping . p/199




 
Section705 : Additional protection : Supplementaryequipotential bonding .

Theonly wording that is changed . 705.415.2.1. ( p/183 ) – ( p/216 )

Note : Where a metal grid isnot laid in the floor a TN-C-S supply is not recommended .

Note : Where a metal gridis not laid in the floor . the use of a PME Earthing facility as the means of Earthing for the electrical installationis not recommended .



 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Section 705 : 705.1. Scope :

Theonly wording that is changed .

Rooms . locations & areas for household applications &similar are not covered by this section . p/183 .
Note : Section 705 does not cover electric fence installations .Refer to BS-EN 60335-2-76 & BS-EN 6100-1.

Rooms . locations & areas for household applications &similar are not covered by this section . p/216 .
Note : Section 705 does not cover electric fence installations .Refer to BS-EN 60335-2-76



 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Section 706 : 706.1. p/188 .

Theonly wording that is changed . added on .

This section does not apply to electrical systems as defined inBS-7909 used in structures . sets . mobileunits etc as used for public or private events , touring shows . theatrical .radio . TV or film productions & similar activities of the entertainmentindustry . :19:


 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Theonly wording that is changed .

Section 708 : 708.411.4.. p/223 . TN system ◄ . :19:
The Electricity Safety . Quality & Continuity Regulations 2002 ( ESQCR ) prohibit the connection of aPME earthing facility to any metalwork in a leisure accommodation vehicle (including a caravan )

This does not preclude the use of a PME earthing facility as themeans of earthing for other purposes . such as to the installations ofpermanent buildings .

Note : The requirements of other section of Part 7 . may alsoapply .



 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Theonly wording that is changed .

708.553.1. Plugs & Sockets-outlets . :19:
708.53.1.8. N/C .
708.53.1.9. N/C .
708.53.1.10. N/C .
708.53.1.11. N/C .

708.53.1.12. Each socket-outlet shall be protected by anindividual overcurrent protective device . in accordance with the requirementsof Chapter 43 .

A fixed connection for the supply to each leisure accommodationvehicle ( including caravans ) or tentshall be protected individually by an overcurrent protective device . inaccordance with the requirements of Chapter 43 .

708.53.1.13. N/C .
708.53.1.14. Socket-outletprotective conductors shall not be connected to a PME earthing facility .

The protective conductor of each socket-outlet shall be connectedto an Earth Electrode & therequirements of Regulation 411.5. for aTT system shall be complied with

 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Theonly wording that is changed . Section 709 .

709.1. N/C
709.3. N/C
709.313. N/C
709.41. N/C
709.41.3.5. N/C
709.41.3.6. N/C
709.411.4. TN-system . The Electricity safety . Quality & ContinuityRegulations 2002 ( ESQCR ) prohibit theconnection of a PME earthing facility to any metalwork in a boat .

This does not preclude the use of a PME earthing facility as themeans of earthing for other purposes . such as to the installations of permanentbuildings .

Note : The requirements ofother sections of Part 7 may also apply .

 
709.5. N/C
709.512.2. N/C
709.512.2.1. N/C
709.512.2.1.2. N/C
709.512.2.1.2.3. N/C
709.512.2.1.2.4. N/C
709.521. N/C
709.521.1. N/C
709.521.1.4. . N/C
709.521.1.5. The following wiring systems . etc . ii) Non-sheathed cables in cable management systems . rest are the same .
709.521.1.6. . N/C
709.521.1.7. . N/C
709.521.1.8. . N/C
709.531. . N/C
709.531.2. .
709.533. . N/C
709.537.
709.537.2. N/C
709.537.2.1. N/C
709.537.2.1.1. N/C
709.553. N/C
709.553.1. N/C
709.553.1.8. N/C
709.553.1.9. N/C
709.553.1.10.. N/C
709.553.1.11.. N/C
709.553.1.12.. N/C
709.553.1.13. N/C

709.553.1.14. Socket-outletprotective conductors shall not be connected to a PME earthng facility .

Fig – 709.1. p/228 .

Main Switch . L1 / N / PE .
Main Switch . L / N / PE . – drawing the same .

Fig – 709.2. p/229 . – drawing the same .

The rest all the same . / The rest all the same . Instructions for Electricity Supply .

 
Section710 : MedicalLocations .

710.411.3.3. Additional Protection .
Wherea medical ( IT ) system is used . additional protection bymeans of an RCD shall NOT be USED.
 
Section740 :

740.1. N/C
740.1.1. N/C . Scope :- Note / Note . The permanent electrical installation is excludedfrom the scope .
740.3. N/C .
740.31. N/C .
740.313. N/C .
740.313.1.1. N/C .
740.313.3. ( Phase to Line ) N/C .
740.4. N/C .
740.4.1. N/C .
740.410.3. N/C .

( NEW ) 740.410.3.5. - The protective measures of obstacles ( Regulation 417.2 ) is not permitted .
Placingout of arms reach is acceptable for electric dodgems ( Regulation 740.55.9. )

740.410.3.6. N/C .

( The Electricity at Work Regulation “ 1989 “ ) Design . Erection – Verification ElectricalInstallation in Fairgrounds . ( YES )

740.411. N/C .
740.411.4. TN-
( NEW ) 740.411.4.1. A PME earthing facility shall not be used asthe means of earthing for an installation falling within the scope of thissection .
Note : The ESQCR . prohibitthe use of a PME earthing facility asthe means of earthing for the installation of a caravan or similar construction.
( NEW ) 740.411.4.3. Where the type of system earthing is . TN- . a PEN conductor shall not be used downstream ofthe similar construction .
740.411.6. N/C .
740.415. N/C .
740.415.1. N/C .
740.415.2. N/C .
740.415.2.1. N/C .
740.415.2. N/C .
740.415.2.1. N/C .
740.42. N/C .
740.422.3. N/C .
740.422.3.7. N/C . -
 
740.5. N/C .
740.51. N/C .
740.512. N/C
740.512.2. N/C
740.52. N/C
740.521. N/C
740.521.1. – Conduit systemsshall comply with the relevant part of the BS-EN . That’s . it Wording . Rest ok .

NOTE . 2 ) Where mechanical protection of cables is provided . p/221
The following methods are considered to meet the aboverequirements . p/270

(i) ◄ Conduit systems shall . etc .
(ii) ◄ Cable trunking systems & cable . etc .

NOTE . 3 ) Cable of type H07RNF . Changed to NOTE 2 . Restok .

740.526. N/C
740.53. N/C
740.537.1. N/C
740.537.2.1.1. N/C
740.537.2.2. N/C
740.55. N/C
740.55.1. N/C
740.55.1.1. N/C
740.55.1.2. N/C
740.55.1.3. N/C
740.55.1.4. N/C
740.55.1.5. N/C
740.55.3. N/C
740.55.3.1. N/C
740.55.3.2. N/C
740.55.5. N/C
740.55.7. N/C
740.55.8. N/C
740.55.9. N/C
740.551. N/C
740.551.8. N/C
740.6. N/C
 
Appendix2 ( Informative ) p/240

StatutoryRegulations & Associated Memoranda .

( vi ) Theatres & otherplaces licensed for public ETC.
conditions of licence under : (a) in England& Wales. The local Government ( Miscellaneous provisions ) Act 1982.
(a) The Secretary of state for the Home Department .

Statutory Regulations & Associated Memoranda . p/292

( vi ) Theatres & otherplaces licensed for public ETC.
conditions of licence under : (a) in England& Wales. The local Government licensingAct 2003.
(a) Department for Culture . Media & Sport .


 
UsefulJunk : ( ESQC ) Whereto find it .

17[SUP]th[/SUP] Edition p/241 & FirstAmendment . p293

UnderRegulation 28 . of the Electricity Safety . Quality & Continuity Regulation 2002 . requires distributors to provide the following information to relevantpersons free of charge .

- The maximum prospective short-circuit currentat the supply terminals .
- The maximum earth loop impedance of the earthfault path outside the installation ( Ze )
- The type & rating of the distributorsprotective device or devices nearest to the supply terminals
- The type of earthing system applicable to theconnection .
- The number of phases of the supply
- The frequency of the supply & the extentof the permitted variations .
- The voltage of the supply & the extent ofthe permitted variations .




 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
***Cont../ Useful Information for Electricians & Apprentices***
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
933
Unsolved
--

Advert

Thread statistics

Created
amberleaf,
Last reply from
Dan,
Replies
933
Views
96,653

Advert

Back
Top