O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Whys?. We use 32A Ring Mains for Extra safety & part of the old standards for harmonisingwith the rest of Europe .

433.1.5follow Up .

2.5mm[SUP]2[/SUP] x ( 2 ) is 54A so with a balanced current in each Leg .the wires can handle 54A . :oops:

2392-10. You make up your on Mind on this Matter . ◄

Example- 4D5
ARing Final Circuit . has two 2.5mm[SUP]2[/SUP].cables . a 2.5mm[SUP]2[/SUP].cable is rated to carry ( 27A ) if & onlyif its clipped on the surface .
Itcarries less when its installed in walls . behind plasterboards . Etc

Each 2.5mm[SUP]2 [/SUP]will nevercarry the same amount of current different lengths on the legs gives different currentsin each leg . Using a conservative ( 2/3 ) of the total current in one leg . Thiscould mean ( 26.67A ) flowing through one ( 2.5mm[SUP]2 [/SUP]) whichis on the absolute limit of the cable even if the whole circuit was clipped onthe surface
 
433.1.5.

i)Accessories to BS-1363 . may be supplied through a Ring Final Circuit – with orwithout Unfused spur .
ii)Protected by a ( 30 or 32A ) protective device [ complying with BS-EN 60898/ MCB . BS-EN 60947-2 / MCCB. or BS-EN 61009-1/ RCBO ] the rest I left out

ii)You need the manufactures data for these . They will have different characteristicsto BS-EN 60898.Different Circuit/ Breakers
will not come under you Verification . 2392-10 . New / Installation :26:

BS-EN 60947-1
BS-EN 60947-2 - ( Single –phase/ Three-phase ) 100A . 63A . 20A
BS-EN 60947-2 - ( Donot have Characteristics like MCBs you need toconsult the Manufactures ) – Make & Model .
BS-EN 60947-3 - Switch Disconnector / Isolator .

Look in the . O.S.G. P/57 – Bottom/ The Short-circuit capacity of devices to BS-EN60947-2 ( is as Specified by the Manufactures) BS-EN 60947-2 / Regulation(s) 433.1.5

UsefulJunk : MCBs / New

BS-EN 60898. Time / Current Characteristics .
B(- range of trip ( 3 to 5 In ) Load type – Resistive .
Range(- Domestic . Heaters . Shower(s) . Cooker(s) . GeneralSocket Outlets . Etc

C(- range of trip ( 5 to 10 In ) Load type –Inductive . Etc
Range(- Motor(s). General lighting circuit(s) . Power Supplies .Etc

D(- range of trip ( 10 to 20 In ) Load type –High / Inductive .
Range(- Transformer(s). Motor(s) . Dischargelighting circuit(s) . Computer(s) Etc

UsefulJunk : MCBs / Old/ 3871 – Range . O.S.G. . P/57 3871 ◄◄

1 (- range of trip ( 2.7 to 4 In ) Load type– Resistive .
Range(- Domestic . Heaters . Shower(s) . Cooker(s) . GeneralSocket Outlets . Etc BS-1363

2 (- range of trip ( 4 to 7 In ) Load type– Resistive /Inductive .
Range(- Small Inductive . Switching Load(s) Lighting& Domestic circuit(s) . Etc

3 (- range of trip ( 7 to 10 In ) Load type– Inductive .
Range(- Motor(s) . General Lightingcircuit(s) . Supplies . Etc . I leaf out ( 4 )

Asa Designer .
2392-10 (- Installation(s) should be arranged so as toavoid Danger in the event of a Fault ( i ). & ( ii ) the facilitate safe operation . Inspection /Testing & Maintenance .
Yourcomply with Regulation - 314.1. (iii )

Notto confuse the “ Apprentices “ . :aureola:

BS-3871 .. ( Obsolete ) has been Replaced by ( BS-EN 60898 )
Theare still out There . 16[SUP]th[/SUP] Edition . O.S.G. P/57

ShortCircuit Capacity ( Icn ) – Amperes ( A ) MCBs / BS-EN 60898 .

TheWhy’s are coming out Now . ??
Regulation433.1.1. . Says that ( ALL ) conductor(s) mustbe protected a ( Fuse/Breaker ) to PROTECT the CABLE . should anOvercurrent flow .( Iz )

Circuitshould be wired with Copper Conductor(s) having Line & Neutral conductor(s)with a minimum ( C.S.A. ) 2.5mm[SUP]2[/SUP]. Such circuit(s) are deemed to meet the requirements of Regulation . 433.1.1.

Now(- ( IF) the CurrentCarrying Capacityof the cable is NOT less than ( 20A ) . &
Underthe intended conditions of Use . The load current in any part of the Circuit isUnlikely to exceed for long periods the current [ Current Carrying Capacity ofthe Cable ]
 
Point to Note . Here . Amber . :welcome2:

Without any Thank You . I don’t know if am in the Right Direction .

Please hit the ( Like Button ) it does help me OUT. PS. What’s a click on the Button . ( A Lot To Me ) :aureola:
 
Apprentices (- Regulation . Chapter 31 – p/38

Purpose. Supplies & Structure .

312.3.1. Type of Earthing Arrangement .
Thetype of Earthing System to be used for installation shall be determined , due accountbe taken of the Characteristics of the source of Energy . &
Inparticular of any facilities for Earthing .

There Asking us . ??
:aureola: i) Will the Supply & Earthing arrangements will be Satisfactory.
ii) There may be a need to ( Alter ) the arrangementof the ( Installation )

Apprentices. Initial Verification “ is “ New Installation . ( your going down the Road of 2392-10 )
 
2392-10(- Design & Verification . ( Full TitleSwitch Disconnector ) :66:
Capableof Switching both Resistive & Inductive Loads.

Regulation. Table 53.2. ( Switching Devices) Isolation “ Wylex 100A “ on ConsumerUnit .

SwitchingDevices BS-EN 60947-3 . Yes[SUP]( [/SUP][SUP]1[/SUP][SUP])[/SUP]

Yes/ Function provided .
[SUP]( [/SUP][SUP]1[/SUP][SUP])[/SUP] Function provided if the device is suitable &marked with the symbol for isolation ( see BS-EN 60617 ) identity number S00288. )

( Switching Devices ) Isolation “ MK – Main Switch 100A “ on Consumer Unit .

EN-60947-3 ◄◄

Yes/ Function provided . Wylex
[SUP]( [/SUP][SUP]1[/SUP][SUP])[/SUP] Function provided if the device is suitable &marked with the symbol for isolation ( see BS-EN 60617 ) identity number S00288. )

Youare complying with Regulations . 17[SUP]th[/SUP]Edition 2008 .

 
Useful Junk .

Cable Reference :

CC – Bare copper sheathed .
MI - Cable .
V – PVC covered .
M – Low smoke & fume . ( LSF ) materialcovered .

L – Light duty ( 500V )
H – Heavy duty ( 750V )

Hence– a two-core 2.5mm[SUP]2 [/SUP] light duty ( MI ) cable with PVC oversheath would be ?? ( CCV –2L . 2.5 ) Next time look at your Pyro Cuter Tool ??

MineralInsulated copper sheathed ( MICS ) Cable . “ Fire Alarms“ :66:
 
UsefulJunk .

RingFinal Circuit : OneSolution . :aureola:

i)To indentify breaks in the Ring FinalCircuit & Interconnections across the Ring .
ii)Test with a Low Reading Ohmmeter between each ( L . N . & E . Leg ) &the corresponding terminal at the nearest socket .
- A Low value indicates the short leg .
- A High vale the Long Leg .

Reading at Mid-Point = 30m of 2.5mm[SUP]2[/SUP]+ 30m of 1.5mm[SUP]2 [/SUP]--- 2

=30 x 0.00741 + 30 x 0.0121 ÷ 2 = 0.293Ω
[ 30x 0.00741 + 30 x 0.0121 = 0.5853 )- ÷ 2= 0.293Ω ]

ThisValue is ( R1 + R2) Ring Final Circuit .

30m/ half of - 15m


 
UsefulJunk .

MainIsolation . 100A

TheMain Intake position . Domestic Installation . Usually as part of the ConsumerUnit . 2392-10 (- The means to Isolate the Supply to whole Installation .
Thereis a requirement to Ensure that such Isolation beAccessible :aureola:

Tomany times I,e seen them under Stairs incupboards’ . Etc



 
►Part P – ( BR ) 2006 p/134 – Note/ 3 :19:

Garages
Are considered to be Unsuitable for standard main frequencyfluorescent fittings due to ( ► Stroboscope Effects ◄ ) with rotating equipment .

[ Fluorescentlamp with ( High frequency electronic ballastsubstantially reduce this RISK . ]
 
Inductive Loads .
Motors: Discharge lighting – Metal halide : Fluorescent or Neon:beatnik:

PartP /Building Regulation – p/15 – look in Chapter 10. 117 :19:

►The ABC,s of the BuildingRegulation . ( BR)

Part ( A ) “ Structure“ Where the positioning of ( Holes in a Joist ) Depths of chases in a masonry wallare affected .
Part( B ) “ Fire Safety “ Considers ( Smoke Alarm Systems ) & what must be done tomaintain any ( Fire Barriers ) That have been ( Breached during Work ) in a Dwelling .
Part( C ) “ Résistance to Passage of Moisture “ Looks at the ( Ingress of Moisture ) through a wall & therequirement to limit moisture build up .
Part( E ) “Résistance to Passage of Sound “ Oftenoverlooked when fitting equipment in ( Ceilings &Walls ) The sound barrier is to be maintained .
Part( F ) “ Ventilation “ Requirements for fitting of Ventilation in certain roomswithin a dwelling & the required amount of ( AirFlow ) -&-s. Big / Time
Part( L ) - ( L1A & L1B ) “ Conservation of Fuel & Power . This covers both ►New& Existing dwellings ◄ for fitting orrecommending a certain amount of ( Low-energy light fixtures )

L1A / ► New Dwellings . L1B / ► Existing Dwellings .

Part( P ) – Electrical Safety ( P1 )
“Access to & use of Buildings “ Heights of Switches . Socket outlets &other equipment .

p/133. Part ( L ) – Fixed Internal Lighting . -&-s .
One energy efficientlight fitting per four ( Fixed light fittings ) read Note[SUP]2[/SUP][SUP] [/SUP] below . Whichever is the Greater .
►one per 25m[SUP]2[/SUP] of floor area ( excluding garages ) Note[SUP]2 [/SUP]&Note[SUP]3 [/SUP]. Whichever isthe Greater .

Note[SUP]1 [/SUP].Note[SUP]2 [/SUP]. Note[SUP]3[/SUP]. p/134
 
Rectification . in Wording . :43:

p/15- Building & Structures . with regards to SocketHeight as ( Part M ) sorry not Part P . Small Overpart on mySide .

TwoPart’s - Part / P . ( P1) “ Meaning “ Electrical Safety ( Firstly )

Part/ M . Heights of Switches. p.137 / 450mm . 1200mm

Kitchen Installation (- p/61

Rememberthat . in the ( BR) Kitchen is defined in the Building Regulations . as a room or part of a room ( -&- ) Specialinstallations . Special locations& Kitchens . p/59

( Not in Regulations BS-7671:2008 / Kitchen as Speciallocations )
 
To Overcome Thermal Insulation Issues . 17[SUP]th[/SUP]Edition 2008 .
:beatnik:
Isi t permissible to design a Ring Final Circuit using 2.5mm[SUP]2[/SUP]cable protected by a ( 20A ) protective device .

( Yes ) if the effective CurrentCarrying Capacityof the cable is at Least ( 12.5 amp –20A x 20/32 ) So as to effectively have the same “ Deemed to comply status “
As regulation(s) give to ( 30A & 32A Ring Final Circuits )
 
Useful Junk .
:19:

Youare Advised that it is ( Unlawful ) under the Electricity at Work Regulations 1989.

Towork on any Electrical Installation in the UK . unless you are a “ Competent Person “ ◄

TheElectricity at Work Regulations 1989 . requires persons to be Competent to prevent Danger& Injury . ( You will see this in the Regulations )
NoPerson should be Engaged in any work activity Unless . He or She possesses suchTechnical Knowledge or Experience . or is Supervised as appropriate for theWork .

TheMemorandum Qualifies Technical Knowledge or Experience as being .

i)Adequate knowledge or experience .
ii)Adequate experience of Electrical Work .
iii)Adequate Understanding of the system being worked on & practical experienceof that ( Class of System)
iv)Understanding of the Hazards that may arise during the work & thePrecautions . That . should be taken .
v)Ability to recognise at all times . whether it is Safe for Work to continue . Etc .

Useful Junk .
:19:

Copper isUsed for Underground Cabling in the transmission & Distribution Systems or (Where Weight is not an Issue ) right down toDomestic Supply ( Due to it’s LowResistivity )
 
Firstly am NOT a Tutor . Amber .

I can offer some Guidance Only.

Amonly using this as One Example . Can you be Asked this on 2391-10 . Exams?? ( A /B ) :willy_nilly:

Explainthe Terms : 2391-10

a)Main Earthing Terminal .
b)Main Protective Bonding Conductor .
c)Exposed – Conductive – Part .

a)Main Earthing Terminal . 17[SUP]th[/SUP] Edition . p/26
TheTerminal or Bar providedfor the connection of ( Protective Conductors )including Protective Bonding Conductors . &conductors for ( Functional Earthing ) if any .to the Means of Earthing .

b) Main Protective Bonding Conductor . 17[SUP]th[/SUP]Edition . p/32
Electrical Connection maintaining various ( Exposed Conductive Parts ) at Substantially the same Potential .

2391-10(- This involves joining together ( Metalwork )that is or may be Earthed so that it is atthe ( Same Potential) to prevent “ Danger “ Electrical Shock“ . frombetween those pieces of Metal as the Earth systemhandles a Fault .

c)Exposed Conductive Part : 17[SUP]th[/SUP] Edition. p/24
AConductive Part of equipment which can be Touched & which is NOT LIVE which can become Live when basicInsulation Fails .

17[SUP]th[/SUP]Edition . Conductive Part : of equipment which can be Touched & which is NOT LIVE which can become Live when basicInsulation Fails .

Refersto Items like :
TheMetallic Covers of electrical equipment which will normally be at Earth Potential . but which may develop a Voltage if the Fault Current goes through Equipment .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top