O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
The most effective way ofTesting for ( Earth Faults) in the wiring or equipment is byMeasuring the Insulation Résistance . as described in Section 6 . 612.3.1.
( Nobreakdown of the Conductor Insulation ) Nails . & Picture hooks . Screws . ???????????? :svengo:

2392-10 .
Floorboards’ Nail driven between the Neutral & Earthconductor(s) creates a ( Neutral to Earth Fault) :hurray:
“ RCD to Trip “
The Fault can be located byInsulation Testing .
Damaged cable must be replaced& either relocated to avoid further damage or protected .

2392-10 :- Requirements to protect cables from Impact& Penetration are given in Regulation 522.6.5. ( v ) p/100 . 522.6.5. the same . ( v ) p/124






 
Section 712 :

Solar Photovoltaic ( PV ) Power Supply System(s)

712.512 : p/243 Accessibility.

712.513.1. The selection & erection of equipment shall facilitatesafe maintenance & shall notadversely affect provisions made by themanufactures of ( PV ) equipment to enable maintenance or service work to becarried out safely .

Scope .
Section 712 of BS-7671:2008 - ( Applies to the Electrical Installationof ( PV ) power )

Supply systems including system(s) with a.c. modules .

Note )- Section 712 does NOT apply to ( PV )power supply system(s) which are intended for ( Standalone Operation )

New Topics covered . On-Site Guide is Portable Generators .
Two classes of ( TemporaryGenerators ) – (i) Portable Generators .(ii) Mobile Generators .
Generators used for short periods :- One-day & these used for longer timescales .

□ Portable generators with an electrical output rating of up to( 10kVA ) used for small scale work –short term use ( Less than one day )
□ Mobile Generators . used for longer periods & can be in Excess of (( 10kVA ))

• Portable generator used with a Floating Earth .
• Portable generator used without reference to the general mass ofthe Earth .
• Portable generator referenced to the general mass of the Earth .

Permanent use of Generators . Guidance Note 5 - Guidance Note 7 .Section 551 . BS-7671:2008 / 2011 .

Generator(s) are used to ( supply Concession Vehicles ) such as (Burger Vans ) look Section 717 . Mobile & Transportable Units . / GuidanceNote 7 .

Temporarily supply electrical equipment or electricalinstallations with a generator where the mains or usual supply is Unavailable .

Portable generator with Floating Earth :

Small portable generators’ . ranging in ( Output ) from 0.3kVA / 10kVA single phase often have a ( Floating Earth )
Connection of the Socket-outlet of the Unit to the ( Neutral ) of the generator winding.
The ends of the generator winding are brought out to one or more (Three-pin socket-outlet(s) which should conform to BE-EN 60309-2.
[ The Earth socket-tube ofthe socket-outlet(s) are usually connected ( Internally to the Frame of the GeneratorOnly ] ► This arrangement is a form of ( Electrical Separation )

When do NEW INSTALLATIONS have to COMPLY with Amendment No 1 . Requirements
Amendment No 1 July 2011& will come into effect on ( 1 January 2012 ) This means that Installation(s) designedafter ( 1 January 2012 ) will need to comply with the Amendment 1 requirements

An Installation that was designed to the 17[SUP]th[/SUP] Edition “ BEFORE “ 1 January 2012 but gets completed after thisdate should be Certified to the 17[SUP]th[/SUP] Edition

 

( T ) Testingpurposes :- suitablewarning sign(s) & / or notices shall be provided 2391 / 2392 .

134.1.7. Where necessary forsafety purposes . suitable warning sign(s) & / or notices shall be provided.

134.2. Initial Verification .
During erection & on completion of an installation or anaddition or alteration to an installation . & before it is put into service. appropriate ( Inspection & Testing ) shall be carried out by CompetentPersons to verify that the requirements of this Standard have been met .

Appropriate certification shall be issued in accordance withSection 631 & 632 .

134.2.2. The designer ofthe installation shall make a recommendation for the interval to the firstperiodic inspection & test as detailed in Part 6 .
Note : The requirements of Chapter 34 ( Maintainability ) should be taken into consideration .

135 . Periodic Inspection and Testing .
135.1. It is recommendedthat every electrical installation is subjected to Periodic Inspection andTesting . in accordance with Chapter 62.

Definitions – Part 2 . p/25 .
□ Current-carrying capacityof a conductor .
The maximum current which can be carried by a conductor under specified conditions without its steady-statetemperature exceeding a specified value .

□ Current-using equipment .
Equipment which converts electrical energy into another form ofenergy . such as light . heat or motive power .

 
Definitions . p/26 . change.

Exposed-conductive-part . :carols:
Conductive part of equipment which can be touched & which isnot normally live . but which can become live under fault conditions .

Exposed-conductive-part .
Conductive part of equipment which can be touched & which is notnormally live . but which can become live when basic insulation fails .



 
UsefulJunk .

17[SUP]th[/SUP] Edition Wiring Regulations . Requirements forElectrical Installations 2008 . :gettree:

The term ( Phase ) is replaced with the term ( Line )

Line is the Internationallyused term . Do Not confuse ( Line ◄ ) conductor with ( Live ◄ )conductor which can be a ( Neutral ) conductor .

Line Conductor )- p/29 . Definitions

A conductor of an A.C. system for the transmission of electricalenergy other than a ( Neutral ) conductor . A protectiveconductor or a ( PEN ) conductor . Theterm also means the equivalent conductor of a D.C. system unless otherwisespecified in the Regulations .

( PEN Conductor ) p/33 . Definitions
A conductor combining the functions of both protective conductor& Neutral conductor .





 
Portablegenerator referenced to the general mass of the Earth.

Wherethere are ( Extraneous-conductive-parts ) or ( Exposed-conductive-parts ) fromother electrical systems present .
Generatorreference Earthing by means of an (Earth Electrode ) to the general mass of Earth should beinstalled .

NOTE )- That this does NOTcreate a ( TT Arrangement ) Thesupply will be ( TN-S ) from the generator but the ( Neutral ) or (Star point ) will be referenced to thegeneral mass of Earth .

( Generator reference Earthing - Using Earth Electrode )
Wherean Earth Electrode is supplied it will need to be tested by the Standard Method using a (Proprietary Earth Electrode résistance tester )

NOTE )- That an Earth FaultLoop Impedance Tester cannot be used for this Test as the Earth Electrode is NOT used as a meansof Earthing it used to reference the portable generator to the general mass ofthe Earth . As the Earth Electrode isused for referencing & NOT as a means of Earthing . The résistance should .( Ideally be Less than 200Ω )

If buried . generator reference Earthing&/or Bonding conductors should be sized in accordance with Table 54.1. & suitably protected in accordancewith Regulation 543.3.1. Whererestrictions . such as concreted / paved areas or the portable generator isbeing used some distance above ground level . make it impossible to install anEarth Electrode . ( Simultaneously )accessible metal parts . i.e. accessibleExtraneously-conductive-parts or Exposed-conductive-parts from other electrical systems . may beBonded to the ( MAIN ) Earthing Terminal of the generator .

Whereseparate accessible Extraneous-conductive-parts or Exposed-conductive-parts from other electricalsystems are connected together . protective conductors can be sized inaccordance with Regulation 544.1.1.

 
Importantto Emphasise that Generators must be Used in “ Accordance with the Manufacturers Instructions “ :iagree:

WhereGenerators are ( Hired from plant-hire companies ) it is ( Responsibilityof the plant-hire company ) toprovide the Hirer with Information regarding the Safe use of their Equipment . Underno circumstances should Hirers attempt to change the Internal electricalconnections of Hired Equipment .

Where( Doubt Exists ) as to the Internal Earthing connectionsof the generator . a ( Continuity Testbetween Neutral & Earth socket-tubesat the socket-outlet can be undertaken ) Very Low reading – Less than ( 0.1Ω ) wouldindicate that it is not a generator with ( Floating Earth)




 
Responsibilitiesof the Duty Holder :carols:

Minor Electrical Installation Work(s) Certificate .
( Requirements for Electrical Installations BS-7671 [[ IET Wiring Regulations ]]

To be Used only for minor electrical work which does NOT includethe provision of a NEW circuit .

System Earthing Arrangement . TN-C-S - TN-S - TT
Part 2 )- Installation details . Comments on existing installation . Includingadequacy of ( Earthing & Bonding ) arrangements ( T -&-s ) Regulation 131.8. )
131.8. Moved by BS-7671:2008 Amendment No 1 to 132.16 . ◄ p/393

( T -&-s ) 132.16. p/20 .
Additions & Alterations to anInstallation .

No addition or alteration . temporary orpermanent . shall be made to an existing installation . Unless it has beenascertained that the rating & the CONDITION of any EXISTING EQUIPMENT . including that of the distributor . will beadequate for the altered circumstances . furthermore . the EARTHING & BONDING arrangements . if necessary forthe protective measure applied for the SAFETY of the ADDITION or ALTERATION .shall be adequate .
 
Definitions – Part 2 : p/31 / p/28 :christmaswreath:

From a Inspectors point of View.

Reporting : Communicatingthe results of ( Periodic Inspection& Testing ) of an electricalinstallation to person Ordering the Work .

 
Standard ( PVC )Insulated Cable(s) are designed to operate at Temperature’s up to ( 70°C ) beyond this there is a risk of Damage . :gettree:

p/340 . Table 4D5 - ( 70°C ) Thermoplastic Insulated & Sheathed flatcable with Protective Conductor - ( Copper Conductors ) T&E .

Cableis guided by two main principles’ .

i)Cable should be able to carry the current load ( Imposed ) on it without ( Overheating )
(( Extreme conditions of temperature it willencounter during its Working Life . ))

ii) You should have sufficient sound Earthing - Limit the voltage to which people areExposed . Safe Level . ( Fault Current to trip MCB inshort time . )

OverCurrents can be Classed into two types

Overload )- An overload occurs when a current flows thatis somewhat to High .
□ Overloadsdon’t normally cause immediate damage . ( The likelihoodof Damage gradually as the duration of the Overload Increases )
□Cables will Overheat & Melt . (Exposing bare conductor(s)

□ DomesticInstallations Overloads usually results from using to many Appliances at the same time . 2392-10

ShortCircuit )-
□ isa connection between Line & Neutral . OR Line & Earth .
Youare looking for a ( Low Résistance ) & thecurrent that can flow may be hundreds or thousands of times to High for thesystem .

Thiscurrent is called the ( FaultCurrent or Short Circuit Current )

Short Circuit Current . An overcurrent resulting from a fault ofnegligible impedance between ( Live Conductors L/N ) having a difference in potential under normaloperating conditions . p/34

Fault Current : A currentresulting from a Fault . p/28

InPractice )- DomesticInstallation(s) Overload protection& Short circuit protection are both provided by the same Device . ( MCB ) or ( RCBO )
Additional Protection . may beprovided by an ( RCD )

Residual Current Operated circuit breaker withIntegral Overcurrent Protection ( RCBO ) designed to perform the functions of protection against Overload & Short Circuit.
“ Resi/ dual dual - two - L/N
 
Circuit Breaker : ( MCB ) Definitions . p/25 - p/21 :17:

A device capable of making . carrying & breaking normal loadcurrents & also making & automatically breaking . under pre-determinedconditions . ( Abnormal Currents )
Such as ( Short Circuit Currents ) . it is usually required to operateinfrequently although some types are suitable for frequent operation .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top