A

amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Inspector - has responsibilityplaced upon him as to the Safety of the Installation .
Visual Inspection )- is Essential to assess the safety of anInstallation before testing takes place .

Verification . All measures by means of which compliance of the electricalinstallation with the relevant requirements of BS-7671 are checked .comprising Inspection . Testing & Certification .
 
Justa Reminder . 2392-10

612.2.2. Continuityof the Ring Final Conductors’ . :19:

A “ Test “ shall be made to “ Verify “ the Continuity of Each Conductor includingthe Protective Conductor . of every Ring Final Circuit .

 
Justa Reminder . 2392-10

( IR ) Insulation Résistance Testingrequires different test voltages for “Certain Circuits “ indentify what circuit(s) require the following voltages . 250V. 500V . 1000V

Isall in the Wording . -&-s



 
Competent. Persons responsible for Inspection & Testing . :19:

Competent person . A person who possesses sufficient technicalknowledge . relevant practical skills & experience for the nature of the electricalwork undertaken & is able at all times to prevent danger & where appropriate. injury to him / herself

Inspection& Testing . of the installation will be your responsible for decidingwhether or not an Installation complies with the Regulations in their Entirety. BS-7671:2008

2392-10:
Regulation. 134.1.1. Therefore the person carryingout the Installation . ( p/19 ) – ( p/21 ) Goodworkmanship by Competent persons or Person . Etc

Regulation . 610.5. Inspection & Testing of any Electrical Installation Work mustcomply . ( 156)
Regulation . 610.5. The Verification shall be made by a CompetentPerson . First Amendedment . ▼▼▼

Competent person . A person who possesses sufficient technicalknowledge . relevant practical skills & experience for the nature of the electricalwork undertaken & is able at all times to prevent danger & where appropriate. injury to him / herself

 
ConditionReport Inspection Schedule for Domestic & Similar Premises with up to 100ASupply .

Final Circuit(s)

Identification of conductors ( 514.3.1. )
Cables correctly supported throughout their run ( 522.8.5. )
Condition of insulation of live pars ( 416.1. )
Non-sheathed cables protected by enclosure in conduit . ducting ortrunking ( 521.10.1. )
□ To include the integrity of conduit & trunking systems ( metallic & Plastic )

Adequacy of cables for current-carrying-capacity with regard forthe type & nature of installation ( Section 523 )
Coordination between conductors & overload protectivedevices ( 433.1. : 533.2.1. )
Adequacy of protective devices . type & rated current forfault protection ( 411.3. )
Presence & adequacy of circuit protective conductors ( 411.3.1.1. : 543.1. )
Wiring system(s) appropriate for the type & nature of theinstallation & external influences (Section 522. )
Concealed cables installed in prescribed zones ( see Section D . Extent & Limitations’ ) (522.6.101. )
Concealed cables incorporating earthed armour or sheath . or runwithin earthed wiring system . or otherwise protected against mechanical damagefrom nails . screws & the like . see Section D . Extent & limitations .( 522.6..101 : 522.6.103. )
Provision of additional protection by RCD not exceeding 30mA .
□ for all sockets-outlets of rating 20A orless provided for use by ordinary persons unless an exception is permitted ( 411.3.3. )
□ For supply to mobile equipment not exceeding 32A rating for use outdoors (411.3.3. )
□ For cables concealed in walls or partitions ( 522.6.102 : 522.6.103. :
Provision of fire barriers . sealing arrangements & protectionagainst thermal effects ( Section 527 )
Band ii cables segregated / separated from band 1 cables ( 528.1. )
Cables segregated / separated from communications cabling ( 528.2. )
Termination of cables at enclosures - indicate extent of samplingin Section D of the report ( Section 526. )
□ Connections soundly made & under no undue strain 526.6.
□ No basic insulation of a conductor visible outside enclose ( 526.98 )
□ Connections of live conductors adequately enclosed 526.5
□ Adequately connected at point of entry to enclosure ( glands .bushes etc. ) 522.8.5.
Condition of accessories including socket-outlets . switches &joint boxes ( 621.2 – ( iii )
Suitability of accessories for external influences ( 512.2. )






 
Examples of items requiring Inspection for an ElectricalInstallation Condition Report .

A Visual Inspection shouldfirstly be made of the External Condition of al Electrical Equipment which isNot – Concealed . :19:

Further detailed Inspection . including partial dismantling ofequipment as required . should be carried out as agreed with the personordering the work . ( 612.2. )



 
State:- Indentify the type of circuit thatwould require the following applied voltages when conducting an Insulation Résistancetest . :19:

i) 250V .
ii) 500V .
iii) 1000V .

i) SELV / PELV .
ii) Systems up to & including 500V .
iii) Systems over 500V but under 1000V .

Short& Simple . -&-s

Locations ) containing a Bathor Shower .

Additional protection for all low voltage ( LV ) circuits by RCD not exceeding 30mA ( 701.411.3.3. )
Where used as a protective measure . requirements for SELV orPELV met . ( 701.4.4.4.5. )
Shaver sockets comply with BS-EN 61558-2-5 . formally BS 3535( 701.512.3. )
Presence of supplementary bonding conductors . unless not requiredby BS-7671:2008 . ( 701.415.2. )
Low voltage ( e.g. 230 volt ) socket-outlets sited at least 3m from zone 1 ( 701.512.3. )
Suitability of equipment for external influences for installedlocation in terms of ( IP ) rating (701.512.2. )
Suitability of equipment for installation in a particular zone . (701.512.3. )
Suitability of current-using equipment for particular positionwithin the location ( 701.55. )

 
AFundamental principle of ELECTRICAL SAFETY is that NO SINGLE FAULT CONDITION should cause ahazardous situation . Plain English .

Asthe FirstAmendment says .

Definitions . Fault Protection . p/28 .
Protection against electric shock under ( Single Fault Conditions)

Note )- for low voltageinstallations . systems & equipment . fault protection generallycorresponds to protection against indirect contact . mainly with regards tofailure of basic insulation . Indirect contact is “ contact of persons orlivestock with exposed-conductive-parts which have become live ( UNDERFAULT CONDITIONS “


 
Electrically Independent Earth Electrodes . p/27

Earth electrodes located at such a distance from one another thatthe maximum current likely to flow through one of them does not significantlyaffect the potential of the OTHER(S) .
 
E.I.C.R.

Current – Using Equipment (Permanently Connected )

• Condition of equipment in terms of ( IP ) rating etc . ( 416.2.)
• Equipment does not constitute a fire hazard ( Section 421 )
• Enclosures not damaged / deteriorated so as to impair safety (621.2. (iii))
• Suitability for the environment & external influences (512.2. )
• Security of fixing (134.1.1. )
• Cable entry holes in ceiling above luminaires . sized or sealedso as to restrict the spread of fire .List number & location of luminairesinspected ( Separate page )
• Recessed luminaires ( Down lights )

1) Correct type of lamps fitted .
2) Installed to minimise build-up of heat by use of “ fire rated “fittings . insulation displacement box or similar ( 421.1.1.1. )
3) No signs of overheatingto surrounding building fabric (559.5.1. )
4) No signs of overheatingto conductors / terminations ( 526.1. )
 
TheImpedance of the Earth connection must be low enough to ensure that sufficient currentcan flow through the protective device so that it disconnects the supply quickly( 0.4 sec ) & Voltage on the Earthconnection does not RISE more than( 50V )

RCDsoperate at much lower Fault Currents . ◄◄◄ :19:



 
701.411.3.3. Additionalprotection by RCDs

Additional protection shall be provided for all circuits of thelocation . by the use of one or more RCDs having the characteristics specified inregulation 415.1.1.
Note : see also Regulation 314.1. ( iv ) & 531.2.4. concerningth avoidance of unwanted tripping . p/166

701.411.3.3. Additionalprotection by RCDs

Additional protection shall be provided for all [ low voltagecircuits of the location ] . by the useof one or more RCDs having the characteristics specified in regulation 415.1.1.
Note : see also Regulation 314.1. ( iv ) & 531.2.4. concerningthe avoidance of unwanted tripping . p/199




 
Section705 : Additional protection : Supplementaryequipotential bonding .

Theonly wording that is changed . 705.415.2.1. ( p/183 ) – ( p/216 )

Note : Where a metal grid isnot laid in the floor a TN-C-S supply is not recommended .

Note : Where a metal gridis not laid in the floor . the use of a PME Earthing facility as the means of Earthing for the electrical installationis not recommended .



 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Section 705 : 705.1. Scope :

Theonly wording that is changed .

Rooms . locations & areas for household applications &similar are not covered by this section . p/183 .
Note : Section 705 does not cover electric fence installations .Refer to BS-EN 60335-2-76 & BS-EN 6100-1.

Rooms . locations & areas for household applications &similar are not covered by this section . p/216 .
Note : Section 705 does not cover electric fence installations .Refer to BS-EN 60335-2-76



 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top