O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
O.S.G. - First Amendment . BS-7671:2008 – ( 2011 ) p/14

Basic Information Required .

132.16 .
For Additions & Alterations to existing installations .installers should SATISFY themselves asto the SUITABILITY of the supply . The distributor’sequipment & the earthing arrangements .

p/13 - For existing installations . Electricians should satisfythemselves as to the SUITABILITY of thesupply including the earthing arrangement .

Part P – Electrical Safety - Dwellings .
 
O.S.G. - First Amendment . BS-7671:2008 – ( 2011 ) p/17

As the First Amendment . Reminds Us .

Function of Components .

2.2.1. Distributor’s Cut-Out . :svengo:

This will be sealed to prevent the fuse being withdrawn byUnauthorised Persons .
When the meter tails & consumer unit are installed in accordancewith the requirements of the distributor’s . The cut-out may be assumed toprovide fault current protection up to the consumer’s main switch .

As the cut-out is the property of the Distributor , installersMUST NOT CUT SEALS & WITHDRAW CUT-OUT FUES without PERMISSION .

When removal of the cut-out for ISOLATION is REQUIRED . the supplier of electricity shouldbe contacted to arrange DISCONNECTION & SUBSEQUENT RECONNECTION .

NOTE : The supplier of electricitymay NOT be the same Organisation as the Distributor .


As the First Amendment . Reminds Us .

2.2.2. Electricity Meter .

The terminals will beSEALED by the METER OWNER to prevent INTERFERENCE by UNAUTHORISED PERSON.S.




 
O.S.G. - First Amendment . BS-7671:2008 – ( 2011 ) p/17

Meter Tails .

□ 521.10.1. Meter tails are part of the consumer’s installation & should be installed &sheathed or insulated & enclosed with “ CONTAINMENT “
For example (- Conduit or Trunking . meter tails are providedby the installer & are the RESPONSIBILITY of the OWNER of the electrical installation.

□ 514.3. “ POLARITY “ should be INDICATED by the COLOUR of the INSULATION & theminimum cable size should be 25mm[SUP]2[/SUP] .

The distributor may SPECIFY the MAXIMUM Length of meter tailsbetween the meter & the consumer unit in addition to the MIMIMUMCROSS-SECTIONAL AREA

( 2.2.4. ) In some cases .The distributors MAY REQUIRE an ELECRICITY ISOLATOR SWITCH .

2.2.4.
Electricity Isolator Switch .
Suppliers may provide & install an electricity isolator switchbetween the meter & the consumer unit . Labelled as Electricity Isolator Switch .
This Double-pole switch permits the supply to the installation to be interrupted withoutwithdrawing the distributor Cut-Out Fuse .

Note : An ELECRICITY ISOLATOR SWITCH may NOT always be installedby the Distributor . TT . TN-S . TN-C-S ( PME )


“Smart Electricity Meters “ is an electricity energy meter thatincorporates a communications unit .

Howlong can Meter Tails be . ??

Themeter tails should be as Short as possible .
Differentdistribution & metering companies have different policies but the length should always be lessthan ( 3 metres ) of cable from the Cut-Out through the meteringequipment to the Consumer Unit .

434.2.1 - 2011 . p/83 . p/75
(i) Not Exceed 3m inLength .

ElectricalSafety Council .

Isit permissible to install a consumer unit more than 3m from the distributorsservice head . ( Yes ) in certain circumstances
Distributorsgenerally accept a minimum of 3m from the service head .

Wherethe tails need to be longer . the distributor may require a means of Isolationto be provided within 3m of the servicehead . Any particular requirements should be ascertained in advance from thedistributor .
 
O.S.G. p/24 . First Amendment

3.4.2. Other methods of protection against electric shock .

410.3.3. in addition toautomatic disconnection of supply . BS-7671 recognises other methods ofprotection against electric shock .

2008 First Amendment 2011 . p/51

410.3.3. in each part of aninstallation one or more protective measures shall be applied . taking accountof the conditions of external influence .

The following protective measures GENERALLY are permitted .

i) Automatic disconnection of supply .
ii) Double or reinforcedinsulation .
iii) Electrical separationfor the supply to one item of current-using equipment .
iv) Extra-low voltage ( SELV& PELV ) .

Note : in electrical installations the MOST commonly used protective measure is Automatic disconnection ofsupply . ( ADS. ) :rant:
 
O.S.G. p/140 .

Voltage drop . ( Vd)

525 . To calculate the voltage drop in volts the Tabulated valueof voltage drop between ( mV/A/m ) has to be multiplied by the design current of the circuit ( Ib ) thelength of run in metres ( L ) & divided by 1000 ( To covert to Volts )

Voltage drop :- ( mV/A/m ) x Ib x L /1000 .

The requirements of BS-7671 are deemed to satisfied if the voltagedrop between the ORIGIN of theinstallation & a lighting point does NOT exceed 3 per cent of the nominal voltage ( 6.9V ) & for other current-using equipment orsocket-outlets does NOT exceed 5 per cent ( 11.5 single-phase ) Appx. 4 . 6.

525 . First Amendment . 2011 .

525 . Voltage Drop inConsumers Installation . p/130

525.1. in the absence ofany other consideration . under normal service conditions the voltage at theterminals of any fixed current-using equipment shall be GREATER than the LOWER limit corresponding to theproduct standard relevant to the equipment .

525.100 . Where fixed current-using equipment is NOT the subjectof a product standard the voltage at theterminals shall be such as NOT to impair the safe functioning of thatequipment .

525.101 . The above requirements are deemed to be satisfied if thevoltage drop between the ORIGIN of the installation ( Usually the supply terminals ) & a socket-outlet or the terminals of fixed current-using equipmentdoes NOT exceed that stated in Appendix 4 section 6.4.

525.102 . A GREATER voltage drop than stated in Appendix 4section 6.4. MAY be accepted for a motor during startingperiods & for other equipment with high inrush currents . provided that itis verified that the voltage variations are within the limits specified in therelevant product standard for the equipment or . in the absence of a product standard , in accordance with the manufacturer’s recommendation’s.


 
O.S.G. . p/107

11.7. Multipole RCDs

As each LIVE conductor of the RCD is incorporated in the magnetic sensingcircuit it is not necessary to perform the test for poles ( L2 & L3 ) however .
If there is any doubt as to the Authenticity of the device inquestion – in terms of a FAKE orCOUNTERFEIT DEVICE – the advice would be to repeat the test for poles ( L2& L3 ) it goes without saying that such important devices . designed toprotect life & property . should be obtained from trusted sources &made by reputable manufacturers .

If a decision is made to test the RCD on all three lines .
There should be little on no discernable difference in operatingtimes as each pole is incorporated in the magnetic sensing circuit . if . forexample . the test performed on one pole did not meet the required disconnectiontime . yet tests on the other two poles were satisfactory . the device shouldbe considered faulty & replaced .


 
Electrical Safety Council .

Appendix15 of BS-7671:2008 .

Givesadvice on Ring Final Circuits & sharing / spreading the load around the circuit . iii) suggests that cookers . oven & hobs over( 2 kW ) should be on their own dedicatedcircuit .

Whycan’t ovens of less than ( 3kW ) be connected to a Ring Final Circuit via a suitable connection point such as a socket-outlet or fused connectionunit .

Reminder :- Appendix 15 . isintended to guidance only . ( Informative )
Suchconnection is NOT prohibited . provided that NO part of the Ring Final Circuit will be OVERLOADEDas a result . 433.1.5.



 
( T ) 514.1.2. Identification& Notices . p/114 .

So far as is reasonably practicable . wiring shall be so arrangedor marked that it can be indentified for Inspection . Testing . Repair or Alterationof the installation .

( Main protective bondingconductor )


 
Current – Carrying – Capacity.

Currentrating are dependent on the method of installation . The insulation material affecting the maximumconductor temperature . Internal thermalrésistance & external

ambient conditions .

Current – Carrying – Capacity. Example .
Currentrating are based on continuous operation at an ambient temperature of 30°C - Maximum permissible ambient temperature 70°C

VoltageDrop .

Voltdrop ( Vd ) is dependent on theimpedance of the conductor . The load current . power factor & route length . in accordance BS-7671: 2011

MinimumBending Radii .
The minimum bending radii should be observed to ENSURE operatingreliability .

Avoid problems by taking appropriate care during Installation .

522.8.3. p/125
The radius of every bend in a wiring system shall be such thatconductors or cables do not suffer damage & terminations are not stressed .

Current – Carrying – Capacity. p/25 First Amendment

The maximum current which can be carried by a conductor underspecified conditions without its steady-state temperature exceeding a specifiedvalue .

□ The Guidance given in the O.S.G. is a Suggestion. NOT a regulation .


 
UsefulJunk . ( Facts )

Bending Radius 2392-10 .

Installing T&E & Three-core cable(s)

Itis Important to be aware of certain Constraints .
When a cable is BENT . The Conductor Insulation on the inside of the BEND will COMPRESSED &that on the Outside STRECHED :gettree: .

 
Table A2 . Allowance for Diversity . 17[SUP]th[/SUP] 1B

Water – heater ( Instantaneous type )

In this context an (Instantaneous water heater ) is considered to be a water heater of any loadingwhich heats water ONLY while the TAP isturned ON & therefore uses Electricity Intermittently .

 
Continued - Table A2 First Amendment . 17[SUP]th[/SUP] . 1B

Allowance for diversity .

Current demand to be assumed for points of utilisation current-usingequipment .

Reminder.

Purpose of the final circuit fed from the “Conductors “ or “Switchgear “ to which the diversity APPLIES .

Notes to table A2 : 2392-10 . :13:

) It is important to ensure that distribution boards or CONSUMER UNITS are of sufficient rating to take the totalload connected to them without the APPLICATION of any DIVERSITY .

 
Declaration .

Regulation 631.4 .

The Certificate must be made out & signed by a competentperson in respect of the design . construction . inspection & testing ofthe work .

631.4.

Electrical Installation Certificates . Electrical Installation ConditionReport & Minor Electrical Installation Works Certificates shall be compiled& signed or otherwise authenticated by a competent person or persons .

 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top