A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
This is a Live Test “ .
415.1.1. –. Additional protection : RCDs
It only works if the RCD is Energised
Regulation RCD effectiveness of any testfacility incorporated in the device
To Ensure . The test buttonshould operated at intervals of not greater than 3 months . BS- 514.12.2. p/118..
H&S . Legislation .
The Electricity at Work Regulations 1989 . specificallydeal with Electrical “ Systems “ Regulation 4 .
i) All “ Systems“ shall at all times be of suchconstruction as to prevent . so far is reasonablypracticable . Danger .
ii) As may benecessary to prevent “ Danger “ all systems shallbe maintained . sofar prevent . so far as is reasonablypracticable . Danger .
iii) Every work activity . including ( Operation ) use & maintenance of a sytem &work near a system . shall be carried out in such a manner as not to give rise. so far is reasonablypracticable . Danger .
iv) Any equipment providedunder these Regulations for the purpose of ( ProtectingPerson(s) at work on or near Electrical Equipment shall be suitable for the use for which
it is provided . etc .
415.1.2. An RCD is not used as the solemeans of protection & does not obviate the need to apply one of theprotective measures specified in section 411 to 414 .
- AnRCD is not used as the sole means of protection against Exposed live conductors.
Wiring regulation 17[SUP]th[/SUP] Edition – 2011
Which . amongst other requirements .specifies therequired methods for safe Fusing & Earthing . 415.1.2. The single most important precautionagainst Electric Shock is a properly constituted Earthing System supported by ( Fuses or MCBs ). To correctlydisconnect the supply in case of Overcurrent or Fault to Earth .
For “Portable Units “ the Test Button shouldbe operated before every use at a new site to ensure that it isFunctioning .
You know the outcome . Any device failing to Trip must be removed from service .
612.13.: Functional testing . 2392-10 . last test .
i) Where ( ► Faultprotection ) & / or ( ►Additional protection) is to be provided by an RCD .
ii) The effectiveness of any test facility incorporatedin the device shall be verified .
Determining the Protective DeviceCharacteristics’ . “ MCB “ p/38
Main formula .
( Iz > In > = Ib )
433.1.1.:
Ib ) –Design current of circuit ( A ) Load to be connected tothe circuit . :
Table 41.3.
In ) – Ratedcurrent or current setting of protective device ( A ) .
433.1.1.
Iz ) –Current-carrying capacity of a cable for continuous service under theparticular installation conditions concerned ( A )
This means that in every circuit at all times thecurrent carrying capacity of the cables must be ( Higher ) than the ( Highest ) possible load current .
The ( Protective Device ) rating must be ( Higher ) thanthe ( Load Current ) but ( Lower ) than the maximum current carrying capacity ofthe ( Cable ) installed
-&-s 2392-10: RCDs “ MUST “be used in conjunction with an “ Overload ProtectionDevice “ such as MCB .
-&-s 2392-10: RCD . Double-poleswitching types are preferred to ensure full isolation should a fault occur .
RCD: Hazards .
RCDs– don’t offer protection against current Overloads .
RCDs– will NOT protect against a socket outlet being wired with its Line &Neutral terminals the wrong way round .
RCDs– will NOT protect against the overheating that results when conductors are NOTproperly screwed into their terminals
RCDs– will NOT protect against Line & Neutral shocks . because the current inthe Line & Neutral is balanced . so if you touch Line & Neutralconductors at the same time . ( bothterminals of a light fitting ) you maystill get a shock .
2392-10 : Visual Inspection . 611.1. to 611.3.
“ Inspection “ shall precede testing & shall normally be donewith that part of the Installation under Inspection ( Disconnectedfrom the Supply )
Continuity of Conductors in Ring Final Circuit . 612.2.2.
Purpose of this test is to verify that the Ring FinalCircuit . are
Correctly wired & connected .
Continuous .
-&-s. Not interconnected / Bridged
Earth Electrode Résistance .612.7.
Where the Earthing System incorporates an EarthElectrode as part of the Installation , The Electrode résistance to Earth shallbe ( Measured )
The Earth Electrode . where used . is the means ofmaking contact with ( General Mass of Earth ) Thus it must be ( Tested) to ensure that good contact is made .
Your main consideration here 2392-10 : To ensure thatthe Electrode résistance . is ( NOT HIGH ) thatthe voltage from Earthed Metalwork to Earth ( Exceed50V ) ◄
Where an RCD . is used This means that the result ofmultiplying the RCD operating current ( in Amperes ) by the Electrode résistance( in Ohms ) does NOT Exceed 50V
If a ( 30mA /RCD ) is used . This allows a maximum Electrode résistance of ( 16667*Ω ) althoughit is recommended ( Table 41.5. – Max Earth Fault LoopImpedance ( Zs )
Earth Electrode résistance should NEVER be GREATER than (200Ω )
2392-10:
Whena New Installation has been Completed , it must be Inspected and Tested toEnsure that it is” SAFE “ to use ,
ThisProcess is known as the Initial Verification ,Regs 610.1 for Safety reasons , the Inspection process must precede Testing ,
Please take the TIME to READ this MATTER . 2391-10 / 2392-10 ◄◄ :13:
This Forum can ONLY give YOU GUIDANCE . ◄◄
What is ( Time ) Money .
Firstly. We are ( All) guilty of NOT reading theQuestions / Rightly. 2391-10 . C&G ?? . :blush5:
C&G ?? Identifythe most suitable test instrument for a set of circumstances C&G ?? . GN-3 . ( Incorrect Instrument Names being Used in Exams ) 17[SUP]th[/SUP] Edition& 2011 .
p/83 . GN-3 . Insulation RésistanceOhmmeters’ .
the instrument used should be capable of developing the( Test ) voltage requires across the ( Load )
[ Instrument conformingto BS-EN-61557-2 ] ◄◄◄
p/83 . GN-3 . Earth Fault Loop Impedance Testers
These instruments operate by ( Circulating ) a currentfrom the Line conductor into the Protective Earth . This will raise thepotential of the Protective Earth System .
For circuits rated to ( 50A ) a Line-Earth loop testerwith a resolution of ( 0.01Ω ) should be adequate . in general . suchinstruments can be relied upon to be accurate down to values of around ( 0.2Ω )
Instruments conforming to BS-EN-61557-3 . will fulfilthe above requirements . ◄◄◄
p/84 . GN-3 . Earth Electrode RésistanceTesters .
this may be a ( Four terminalinstrument ) OR ( Three terminal One ) where a combined lead to the ( Earth Electrode ) would not have a significant résistancecompared with the ( Electrode Résistance ) sothat the résistance of the test leads & temporary spike résistance ( Can be eliminated from the Test Result )
-&-s ?? .Please NOTE (- “ Wording Used “ . ◄◄
It may be HELPFUL to NOTE thatInstrument complying with ( BS-EN-61557-5 ) . incorporatethis facility . ◄◄
p/84 . GN-3 . -&-s ?? . PleaseNOTE (- “ Wording Used “ . ◄◄
Phase Rotation Instrument . BS-EN-61557-7. ◄◄ . gives the requirements for measuring equipmentfor testing the ( Phase Sequence in Three-phase distribution systems .
[ Whetherindication is given by . Mechanical . Visual . & /or AudibleMeans . ]
RCD Testers .
The test instrument should be capable of applying thefull range of test current to an ( In-service ) accuracy as given in (BS-EN-61557-6 ) ◄◄
Now -&-s (- Wording Only . 2392-10 Exams . To CHECK - RCD operation & to minimise ( Danger ) during the test . The test current should beApplied ( For No Longer Than2 Seconds ) 2392-10 . This only Appliesto RCD Only . ◄◄◄◄◄◄
2392-10 . The instrument used for ( Low Résistance Tests) 612.2.1. No-load voltage between 4V &24V . & a shortcircuit current NOT less than 200mA .
Instrument to ( BS-EN-61557- 4 ) will meet the above requirements . ◄◄◄◄◄◄
p/81 –GN-3 : Instrument Standard .
The ( Basic ) instrumentstandard is ( BS-EN-61557 ) Electrical Safety in Low-Voltage Distribution Systems. Up to 1000V . a.c. & 1500V . d.c. Equipment for Testing .Measuring or Monitoringof Protective Measures . ◄◄◄◄◄◄
NOTE (-. This Standard includes performance requirements & requires ( Compliance with BS-EN-61010 )
ISBN-978-086341-857-0 . GN-3
Amendment 2011 .
□ Electrical Installation Condition Report .
Electrical Installation Condition Report . ( EICR ) from Appendix 6 of BS-7671 . is for use when carrying out ( Routine ►► PeriodicInspection & Testing ) of an Existing domestic& similar installation . with up to ( 100A ) ( Single – phase ) or ( Three-phase) supply .
►► It isNOT use when ( Alterations or Additions are Made)
A Generic Scheduleof Test Results ( 4 ) & aCondition Report Inspection Schedule ( 7 ) shouldaccompany the Electrical Installation Condition Report ( 6 )
( 6 ) The ElectricalInstallation Condition Report . ( EICR ) to be used for Domestic & SimilarInstallations with ( 100A ) Single – phase ) or ( Three-phase ) supply
( 4 ) Generic Schedule of Test Results .
( 7 ) Condition Report Inspection Schedule . ( forDomestic & Similar Premises with up to ( 100A ) supply .
The ( Forms ) are Numbered .
1 ) . Electrical Installation Certificate . Please Note : (Single – Signature )
2 ) . Electrical Installation Certificate .
3 ) . Scheduleof Inspections . Please Note : ( for NEW Installation Work Only )
4 ) . GenericSchedule of Test Results .
5 ) . Minor ElectricalInstallation Work Certificate .
6 ) . ElectricalInstallation Condition Report .
7 ) . ConditionReport Inspection Schedule . Please Note : ( forDomestic & Similar Premises with up to ( 100A) supply .
( 1 & 4 ) are designed for use when ( Inspecting & Testing ) a New Installation . or an Alteration orAddition to an ( Exceeding Installation ) forms comprise the following .
1 ) . Short –form of . Electrical Installation Certificate . PleaseNote : ( to be used when oneperson is responsible for the Design . Construction . Inspection & Testing. of an Installation ) OR .
2 ) . Electrical Installation Certificate . ( Standard from Appendix 6 of BS-7671 )
3 ) . Scheduleof Inspections . Please Note : ( foe NewInstallation Work ONLY )
4 ) . Generic Schedule of Test Results . .
-&-s . State the ( TWO ) different types of Inspection & Testing . may require
“ InitialVerification “ … ( Initial Verification & Inspection )
“ Periodic Inspection & Testing “ … ( ElectricalInstallation Condition Report )
***Cont../ Useful Information for Electricians & Apprentices***
Australia
amberleaf,
Dan,
TrueNAS JBOD Storage Server
