O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Copperhas & continues to be the most widely used material for Earthing .

BS-7430. Code of Practice for Earthing .
Whichstates “ Copper is one of the better & commonly used materials for EarthElectrodes & Underground Conductor’s .

Earthingarrangements’ within buildings in the UK . should conform to BritishStandard – 7671: & 2011.

Forthe sake off . 2391-10 . -&-s Exams . The requirements for “ Erection & Initial Verification of Electrical Installations .

(2 sets of Testing here ) Verification &Periodic Inspection & Testing
i) InitialVerification . 134.2.
ii) Periodic Inspection . 135 . – tofollow 134.2.2.

Appendix 6 . for Certification & Reporting Electrical Installation ConditionReport . that replaces the ( Periodic Inspection Report ) New condition reportincludes a New Inspection Schedule

p/36. Verification : All measures by means of which compliance ofthe Electrical Installation with therelevant requirements of BS-7671 are checked . Comprising
Inspection. Testing & Certification .

134.1.7. Testing – Where necessary for safety purpose. suitable warning signs & / or notices shall be provided .

BS-7671:2011 & GN-3 . go Hand & hand . intesting . & Exams 2391-10 .

313.1. Reminds us . (v) The suitability for the requirements of theinstallation . including the Maximum Demand . 2392-10 .
MaximumDemand . Ring Final Circuit – maximumpermitted sustained load to be drawn by this circuit would . be 32A – 100%

Doesthe device that has to be provided for switching off a bathroom ( Extract Fan ) for mechanical maintenance need to be locatedadjacent to the Fan . ( No )
p/152. Regulation – 537.3.2.4.
Butthe device does need to be placed & marked as to be readily identifiable& convenient for the Intended Use .

2392-10: Installation Circuit Arrangements .

p/46. The Four Regulations under Section 314 of BS-7671:2011 .
Setout the requirements for the circuit arrangements . Essentially . circuits mustbe provided in sufficient number so that danger is prevented . &inconvenience minimised . both under normal & fault conditions &arranged so that operation . Inspection . Maintenance & testing may becarried out in a safe manner .

Itis Important . that a sufficient number of circuits are provided so thatequipment unaffected by a fault condition remains safe & functioning whenanother circuit develops a fault . The designer would need to consider theeffects . in terms of consequential events . of the operation of a singleprotective device .

Regulation314.1.4. calls for each circuit to beelectrical separate & connected individually & detached from all othercircuits where they terminate in a distribution board .
Implicitly: the connection of each circuit Line .Neutral & CPC conductors must follow a logical sequence at theirtermination in the distribution board

Summaryof ( Low
ExistingBS-7671:
 
Summaryof ( Low – voltage ) fuse standardchanges for first amendment . p/295 .

ExistingBS-7671:2008 fuse. BS-88.2.2. : BS-7671:2011 fuse . BS-88-2 . ( Bolted ) type fuse is recognised ( Fusesystem E )
ExistingBS-7671:2008 fuse. BS-88-6 : BS-7671:2011 fuse . BS-88-2 . “ ( Clip in ) type fuse is recognised ( Fusesystem G )
ExistingBS-7671:2008 fuse. BS-1361 : BS-7671:2011 fuse . BS-88-3 . “ ( Cartridge ) type fuse is recognised ( Fusesystem C )

 
Ambient Temperature Correction Factor .

The measured Loop Impedance given . O.S.G. p/120 . Table B8
Thevalues assume that the maximum operating temperature of the insulation is ( 70°C ) & the Ambient Temperature whencarrying out the test is at ( 10°C ) AtAmbient Temperatures other than this . Correction Factors . should be applied .

Table B8 p/120 . The correction factor is given by :
(1 + 0.004 – ambient temp – 10 )
Where( 0.004 ) is the temperature coefficient per ( °C ) at 20°C for copper &aluminium .

If the ambient temp is ( 25°C - 1.06 ) the measured impedance of the circuit protected by a ( 32A type MCB ) should not exceed ( 1.16 x 1.06 = 1.23Ω )

 
SomethingKnock-up . 2392-10 .

□ Measurementof Prospective Fault Current - Ipf - ( PFC ) & ( PSCC )

For the sake of -&-s )- This test is made with an Earth Fault Loop Impedance Tester set to Amps . -&-s– BS-EN-611557-3.

The ( PFC ) which is how much current will flow in the event of a fault .
isdivided into two parts .

Prospective Earth Fault Current )- Line to Earth .
Prospective Short Circuit Current )- Fault between Liveconductors ! L/N

The ( PFC ) test is made at the Origin of theInstallation . & its value ( Obtained in kA )
(PFC ) & ( PSCC ) tests ( Higher ofthe Two Values is Recoded )

□ How do we Do this Test . for -&-s sake .
BS-EN-611557-3. – GN-3 ◄

AnEarth Fault Loop Impedance Tester .the valueof Earth Fault Loop Impedance ( Zs ) maybe determined by . !!

i) Direct measurement of ( Zs ) at thefurthest point in the circuit .
ii)Direct measurement of ( Ze ) at the Origin of the circuit &adding to the “ Value “ of ( R[SUP]1[/SUP]+ R[SUP]2[/SUP] ) point to NOTE : measured during Continuity Tests .
iii) Obtained the “ Value “ of ( Ze ) from theElectricity Supplier & adding to this “ Value “ of ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) as above .

(Ze ) is the Loop Impedance “ Value “ External to the Source of the Circuit(s) Supply .
 
□ DirectMeasurement of ( Zs )

Directmeasurement of Earth Fault LoopImpedance . is achieved by use of an . Earth Fault Loop Impedance Tester .
TheInstrument operates from the main supply & therefore can only be used ona ( LiveInstallation ) connected directlyto the ( Furthest Point ) of the circuit .

Note : ( Parallel Paths) will be present which will ( affect ) the true circuit(s) Earth Loop ImpedanceReading(s)

□ Measurementof ( Ze )
(Ze ) can be measured using an . Earth Fault Loop ImpedanceTester . at the ( Origin )
Connectedusing approved leads between the ( Live Terminals ) ofthe supply & means of Earthing with the main switch closed .

Note : to Remove the possibility of ( Parallel Paths) the means of Earthing must bedisconnected from the Main Protective Bonding . conductors for the duration of the Test.

“ Verification “ of Earth Loop Impedance Test Results .
Valuesof Earth Loop Impedance obtained ( Zs ) should be compared with one of thefollowing . 41.3.: 41.4. : 41.5. :

EarthFault Loop Impedance ( Zs )
This is a Live Test .
Canbe obtained direct measurement using an “ Earth Loop ImpedanceTester “ Or by adding ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) obtained earlier to ( Ze )

Obtaining( Ze ) External Loop Impedance .
This is a Live Test .
ByEnquiry ( Must test to ensure Earth ispresent )

Direct measurement of ( Zs ) can only be made on a . Live Installation. No earthing conductors aredisconnected for this purposes of the test & this may result in readingsobtained which are lower than the value of . Ze + ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) This is due to the parallelearth paths presented within the installation .

□ Whattype of Earthing System are there .

Thereare Three types listed in BS-7671:2011 . p/45

TN-S. system
TN-C-S. ( PME ) system .
TT. System .

2392-10: Testing point of View .
Continuity of protective conductors is clearly important as are the Tests for ( Insulation Résistance : Loop Impedance : Operation of RCDs )







 
(1 ) -

InstantaneousTrip Currents . x In .

MCBs : Icu - ( rated ultimate / breaking capacity )
MCBs : Ics - ( rated service / breaking capacity )

Thedifference between . BS-EN-60898 MAY be used insteadof CALCULATION “ / BS-3871 formula. To beUsed :
BS-3871– are still out there .

MiniatureCircuit Breakers “ conforming to BS-EN-60898 are suitable for Isolation ◄
Miniaturecircuit breakers ( MCBs ) manufacturedto earlier standards . such as . BS-3871 : are unlikely to be suitable for Isolation. ◄

Note: There is NO type ( A) instantaneous tripping characteristic to ( Avoidconfusion ) with the ( A ) abbreviation for Amperes . B : C : D : - MCBS

Determinationof Maximum Earth – Loop Impedance ( Zs )
Themaximum value of Earth Fault Loop Impedance maybe found in the . Wiring Regulations . BS-7671:2011 . details’ published bythe Manufactures . ◄◄
 
B: C : D : - Table 41.3 . BS-EN-60898 . ( For instantaneous operation givingcompliance with the ( 0.4s ) Disconnection time )

B) 3 ( In) to 5 ( In )
C) 5 ( In) to 10 ( In )
D) 10 ( In) to 20 ( In )

B / Curve.
Themain characteristic of the ( B ) curve is Instantaneous trigger for currentsbetween ( 3 to 5 times) the rated current . Therefore .
Theyare mainly applied for the protection of circuits with ( resistive characteristics ) or involvingsignificant cable distance . Incandescent lamps . showers. . etc .

{ B means the fast magnetic trip will operatebetween ( 3 to 5 times ) nominal setting }
p/25 . Circuit Breaker. Abnormal currents such as Short Circuit Currents}

Note : THE valuesspecified in Table 41.3. for the types& ratings of Overcurrent devices listed “ MAY be used insteadof CALCULATIONp/55 . ◄◄◄◄

Circuitbreakers are going to be used for protection . disconnection times willautomatic conform to the requirements provided that the circuit(s) meet the ( Zs ) …. 41.3.
MCBs. BS-EN -60898 .

TypeB – 3 & 5 times . its rating passed through it .
TypeC – 5 & 10 times .
TypeD – 10 & 20 times .

Tablesfor ( Zs ) specific value of current is required . ( Worst case is Used )

OhmsLaw : to the supply voltage ( 230V ) & ( Ia ) to obtain a ( Zs) value for the device . Regulation411.4.5. – ( Zs x Ia ≤ Uo )

TypeB . – Zs for a 20A can be calculated . 5x 20 = 100 . 230 ÷ 100 = 2.3Ω …… ( Worst case is Used ) ◄◄◄
TypeC . – Zs for a 20A can be calculated . 10 x 20 = 200 . 230 ÷ 200 =1.15Ω
TypeD . – Zs for a 20A can be calculated . 20 x 20 = 400 . 230 ÷ 400 =0.57Ω

Switch disconnectors. it function is Only to disconnect electrical circuits with currents of up to 100A . Singlepole . “ Doublepole “ . Triple pole . Four pole .
MainLoad Disconnector Switch – Isolator .
 
(2 )

TypeB . – Zs for a 20A can be calculated . 5x 20 = 100 . 230 ÷ 100 = 2.3Ω …… ( Worst case is Used ) ◄◄◄

Regulations’. table 41.3 . ( Look it UP )◄◄

Rating20A – Zs . is 2.30Ω .

TypeC . – Zs for a 20A can be calculated . 10 x 20 = 200 . 230 ÷ 200 = 1.15Ω
TypeD . – Zs for a 20A can be calculated . 20 x 20 = 400 . 230 ÷ 400 = 0.57Ω


 
(3 )

For. BS-3871 )- Types 1 , 2 , 3 , & 4 ,

Themaximum value of . Earth Fault LoopImpedance ( May be Calculated ) &using the Manufactures Tripping Characteristic .

formula.O.S.G. p/72 . Table 7.2.7. (ii) - ( b ) . Now withdrawn )

Thesetypes of circuit breakers are identified by the use of numbers . 16[SUP]th[/SUP] Edition . still in Use .

BS-3871 - formula. To be Used :

1 . 2.7 / 4 – ( In ) …. BS-3871
2 . 4 / 7 – ( In ) ….
3 . 7 / 10 – ( In ) ….
4 . 10 / 50 – ( In ) ….

TypeB )- 3 to 5 ( In ) …. BS-EN-60898 .
TypeC )- 5 to 10 – ( In ) ….
TypeD )- 10 to 20 – ( In ) ….

Circuitbreakers . …. BS-3871

Type( 1 ) … Multiplier ( 4 ) .. In
Type( 2 ) … Multiplier ( 7 ) .. In
Type( 3 ) … Multiplier ( 10 ) .. In
Type( 4 ) … Multiplier ( 50 ) .. In

Zs) value for a 20A type ( 1 ) – BS-3871. ( 4 x20 = 80 ) ( 230÷ 80 = 2.87Ω )
 
-&-s. Any circuit or equipment vulnerable to a particular test should beindentified by . ?
p/117- 514.9.1. The provision of a Legible diagram . chart ortable prior to testing .
2392-10: The purpose of the Inspection conducted prior to Testing an installation isto verify that . ?
p/189- 611.2. (iii) “ equipment ” is not damaged or defective so as to impairsafety .
2392-10: No alteration shall be made to an existing installation unless the ?
p/20- 132.16 . it is established that the alteration will notimpair the safety of the existing installation .

2392-10: The Inspecting & Testing required duringa Periodic Inspection should be recorded on a Electrical Installation Condition Report . & be carried out by .
p/195- 621.5. Competent Person .

2391-10: Q) prior to an Inspection in accordance with BS-7671:2011 , The competentperson carrying out the work shall normally . ?
p/189- 611.1.
A) Inspection shall ( Precede Testing ) & shall normally bedone with that part of the installation under Inspection disconnected from thesupply .

2391-10: Q) Installations should be arranged so as to avoid hazards in the event ofa fault . & to facilitate safe operation inspection . testing & maintenance . .? Onemethod of complying with this is to .
p/46- 314.1.
A) divide the installation into circuits .
 
Reasons) ( IR ) Testing . 2392-10 .

InsulationRésistance . Details of such equipmentshould be recorded on the Schedule of Test Results . “ Inspector “ TestResults . so that the Inspector carrying out ( Routine ) Periodic Testing in thefuture is aware of the presence of such equipment .

□ “ Generic Scheduleof Test Results . “ p/402 . Apprentices .

Aswith the 17[SUP]th[/SUP] Edition 2008 - “ Schedule of TestResults . “ ( Test Results – ► Functional Testing ) RCD time 13 / Other 14 .

Withthe 2011 : the Wording has gone . ( RCD ) – ( mS ) 1 x / 5x / Testbutton operation . ( Same thing -Functional Testing )

Apprentices.
612.13. – p/194 .

The Effectiveness of ANY Test Facility





 
2392-10: for -&-s . they will work into 2011 .

Keychange is to the “ Schedule of Inspections “ That is to be used when carrying out a ( PeriodicInspection )

“ Now “ a Condition Report. will need to have a “ Schedule of Inspectionsrelevant to thePeriodic Inspection . workcarried Out .

BS-7671:2008

Previously . Schedule of Inspections was ( Generic ) ◄ & used for both the (Periodic Inspection Report ) & ( Electrical Installation Certificate )

Thisis were -&-s will trip you Up .2392-10 ▲

134.2.2. : The designer of the Installation shall make arecommendation for the interval to the ( First ) Periodic Inspection & Test. as detailed in Part 6 . 2011
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top