***Cont../ Useful Information for Electricians & Apprentices***
A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
Overcurrent ” a current flow in a circuit which is ( Greater ) than the ( Rated )current carrying capacity of the cables . :89:
Thiswould normally be due to a Fault on the Circuitor Incorrect Cable .
Ifa ( 20A ) cable protected by a ( 32A ) MCB was loaded by ( 25A) the cable would Overheat & the Device would continue to allow current to flow – This couldDamage the cable . ( Iz)
A Fault Current is a current which is flowing in acircuit due to a Fault ??
A Nail is driven through a cable causing an Earth Fault or a Short-Circuit Fault .
Thiswould cause a ( Very High Current to Flow ) through the circuit . Which must be( Interrupted ) before the Conductor reach a Temperature that could Damagethe Insulation or even the Conductor(s) .
TTSystems .
FinalCircuits that are rated UP to & ( 32A ) require a maximum disconnection time of ( 0.2sec) 41.1.
Distributioncircuit require a maximum disconnection time of ( 1 second ) 411.3.2.4
Ihave not done any TT Systems yet . Am working onit . Amber . ( Youwill get this on 2392-10 ) thisis a start . Yeah :coolgleamA:
Apprentices. → 411.3.2. 1. Final Circuits that are rated UPto & ( 32A ) Look First is it ?? TN- or TT ◄◄ :6:
Apprentices. Look in 41.1→ The Regulations are telling you . - requirea maximum disconnection time of ( 0.2sec ) TT :6:
ElectricShock : ( Earthing comes into Exams a Lot )
Two– Ways in which we can be a risk .
i)Touching Live parts of equipment or system that are intended to be Live .
ii)Touching ( Conductive-parts) which are not meant to be Live . but havebecome Live due to a Fault . ( Basic Insulation Fails )
( Conductive-parts ) associatedwith the second of these can either be ( Metalwork )of Electrical Equipment & Accessories ( Class 1) & that of electrical wiring systems such as ( MetallicConduit ) & ( Trunking ) etc called (Exposed-Conductive-Parts )
orother ( Metalwork ) such as ( Pipes ) ( Radiators) ( Girders ) called ( Extraneous-Conductive-Parts )
17[SUP]TH[/SUP]Edition - P/24
( Extraneous-Conductive-Parts ) A ( Conductive-part) liable to introduce a potential . generally Earth Potential. & not Forming part of the ElectricalInstallation
( Extraneous-Conductive-Parts ) NOT ( Forming part of the Electrical Installation )
17[SUP]TH[/SUP]Edition – p/21
( Class 1 ) Equipment in which protection againstElectric Shock does NOT rely on Basic Insulation Only .
Butwhich includes means for the ( Connection of Exposed-Conductive-Parts ) to a ( ProtectiveConductor ) in the Fixed Wiring of the Installation . BS-EN 61140) :28:
BS-EN 61140 ) Protection against Electric Shock . :28:
Commonaspects for Installation & Equipment requires That :-
• (Hazardous-Live-Parts ) . Shall not beAccessible .
• (Accessible-Conductive-Parts) Shall not be Hazardous-Live when there is ( No Fault or UnderSingle FaultConditions )
BS-EN 61140 ) States that those ( ProtectiveMeasures ) providing protection under normal conditions ( That is . When no Faults Exits) provide Basic Protection & those ( Protective Measures ) giving protection Under Single Fault Conditions provide Fault protection– Sec 410 . refers
Themeasures of protection by ( Automatic Disconnection of Supply)
Regulations/ 410.3.3.
- DoubleInsulation .
- ReinforcedInsulation .
-Electrical Separation to Supply to Supply a Single Item of Equipment .
-Extra-Low-Voltage :- SELV . or . PELV . are generally applicable
2392-10. ( Automatic Disconnectionof Supply ) is the MostCommonly Employed method for Electrical Installation(s) .
TheWhys .
- Double & ReinforcedInsulation are more frequently encountered in ( Items)
- Electrical Separation . SELV/ PELV . are only Applied to ( Specific Parts of an Installation)
- Basic/ Protection . ( Protective Earthing )
- Barriers. ( Main Protective Bonding Conductor )
- Enclosures. ( Automatic Disconnectionof Supply ) in the Eventof a Fault .
- Obstacles. ( Automatic Disconnectionof Supply ) for the PrimaryCircuit & connection of ( Exposed-Conductive-Parts ) ofthe Secondary Circuit connected to the ( Protective Conductor ) of the Primary-Circuit ofthe Source .
Point to NOTE : Fictional Extra Low Voltage ( FELV ) ◄◄◄ Equipment so supplied to ( TheProtective Conductor ) -&-s
WhereFictional Extra Low Voltage ( is Employed ) itis necessary to connect the ( Exposed-Conductive-Parts ) ofthe Equipment so supplied to ( The Protective Conductor ) of the Primary Circuit of the Sourcein addition to these Protective Measures required for ( ADS ) Regulation 411.7.3.
Whena Designer ( 2391-10) is considering the Use of ( Obstacles or Placing Out of Reach ) to provide Basic / Protection. it is strongly recommended that careful consideration be given to the ( Statutory Requirements ) relating to :-
• System. work activities & work equipment ( Regulation / 4. of the Electricity at Work Regulation 1989 )
•Insulation . Protection & Placing of Conductors ( Regulation / 7 . of the Electricity at Work Regulation 1989 )
•Work On or Near Live Conductors. ( Regulation / 14 . of the Electricity at WorkRegulation 1989 )
Earthing . or other suitable precautions . (Regulation / 8 . of the Electricity at Work Regulation1989 )
•Working Space . Access & Lighting . ( Regulation / 15. of the Electricity at Work Regulation 1989 )
•Person to be “ Competent “ to prevent Danger& Injury . ( Regulation / 16 . of the Electricity at Work Regulation 1989 )
►►► Wording /NOT Act . ◄► But . Law . Exams ( Electricity at Work Regulation 1989 )
( Electricityat Work Regulation 1989 ) is ( law ) in the United Kingdom. ◄◄◄ in Exams / Wording is ( LAW )
ConsumerProtection is an ACT ◄◄◄ :75:
( Electricityat Work Regulation 1989 ) Applies to all ElectricalSystems at ( All Voltages )
2391-10- Inspection & Testing: ( Remember two different Words ) Yeah. 2392-10
Inthe case of most Types Electrical Installation there is ( No Statutory Requirement ) to carry out ( Inspection & TestingPeriodically )
Itis . However . A Commonly adopted practice seen as a Means of Meeting the Maintenance“ Obligations
The. Electricity at Work Regulations 1998. Regulation ( 4 ) & the Housing Act 1985 –Section 11 . BS-7671 is in the Most Part concerned with the Design .Installation . & Initial Inspection & Testing of New Installations
Chapter62 .
Containsa number of Requirements relating to ( Periodic Inspection & Testing ) . Regulation. 622.2. States that ( PeriodicInspection & Testing ) is not required an Effective Management SystemOperated by ( Skilled Persons ) covering itsMaintenance .
However. & as has been Mentioned Previously .
( The Person Responsibly may be Held Accountable in the Event ofan Incident Occurring )
(2391-10 ) Appropriate Records must be Keep of the Maintenance ActivitiesUndertaken . ( Cover ones But . Yeah ) :75:
UsefulJunk .
Ambersof on One .
ImportTerms . that -&-s . will bring up in Exams .
Statutory& Non- Statutory Regulations .
Electrical Systems .
TheBuilding Regulations ( Part P )
Instruments .
2392-10. Firstly .
Foryour Assessor ?? are you aware of the Statutory& Non- Statutory Regulations that are relevant to InstallationWork
Tester. Example . Insulation Résistance.
i)The Range of Instrumentrequired . ≥ 0.5MΩ / 0.1MΩ .
ii)The Requirements regarding the Use & Performance of Test Equipment .
The more you put in the Easier it Becomes . :icon6:
Asan Inspector . You have to consider the Implicationswhen carrying out an Inspection & Testing . ( Of an Installation ) :13:
Inspection& Testing . Certification Required .
InitialVerification .
PeriodicInspection & Testing .
( 2392-10 ) Initial Verification (- New Work & Alterations & Additions . ( TheCertification ( EIC ) Electrical InstallationCertification .
(2391-10 ) Periodic Inspection & Testing . for ExistingInstallations . ( TheCertification ( PIR ) Using Wording – Condition Report . ( PeriodicInspection Report)
►► Both must be accompanied by a ( Schedule of Test Results & Schedule ofInspections ) (EIC ) / ( PIR )
2392-10 – Exams . STATUTORY & NON- STATUTORY REGULATIONS .
Thestatutory regulations the apply to ( Electrical Work) 2392-10 / Initial Verification / NEW INSTALLATIONS . only
Let’skeep the Assessor . Happy . Yeah
TheHeath & Safety at Work . ( ACT ) ◄
TheElectricity at Work Regulation 1989 . ( Law )
2392-10.
The Building Regulation Part / P . ( Domestic Installation ) Yeah (This will guide you back to BS-7671 ) onMatters
BS-7671:2008/ British Standards . Non- Statutory Regulations. ( By using BS-7671 . You are complying with :- ( 2)
TheHeath & Safety at Work . 1974 ( ACT )
2392-10. ( As an Inspector ) -&-swill use the wording ( Inspector / You ) → → → → Not ( Tester ) Fail :grouphug:
Amberof on One again .
ThisForum is here to HELP& Guide you on Matters .
Froman Exam point of View . 2391-10 . ( NotMeggers here )
( Electricityat Work Regulation 1989 ) Wording / Your Test Instrument / Sourceof Energy . Mains- Power / Battery ???
YourTest Instrument ?? Continuity Tester. is a Test on the System in itself . -&-s want to here . “ Continuity Tester “ Etc
2392-10/ Loop Impedance Tester . ( Live Test )
( Electricityat Work Regulation 1989 ) Which requiresan ( External Supply Source ) ≈ ≈ A.C. – becomes part of the System into whichit is Connected .
Point to Note . Here . Amber . :rockon:
Withoutany Thank You . I don’t know if am in the Right Direction . :43:
Pleasehit the ( Like Button ) it does help me OUT. PS. What’s a click on the Button. ( A Lot To Me )
UsefulJunk .
Apprentices(- Earth Fault Current . ??
AnOvercurrent resulting from a ( Fault ) of ( Negligible Impedance ) between a Line Conductor & an ( Exposed-Conductive-Part ) or a ( ProtectiveConductor )
2392-10(- Protective Conductor Current ) “ Meaning “ ( Earth Leakage Current) Deleted / BS-7671:2008 ◄◄ :33:
Acurrent which flows to Earth . or ( Extraneous-Conductive-Parts ) in a circuit which is ( Electrically Sound )
Thiscurrent may have a ( Capacitive Component )including that resulting from the ( Deliberateuse of Capacitors )
17[SUP]th[/SUP]Edition . p/27 .
( Protective Conductor Current ) Electric current appearingin a ( ProtectiveConductor ) . Such as ( Leakage Current )or Electric current resulting from an ( InsulationFault . ) :19:
UsefulJunk .
Tocomply with the Electricity at Work 1989 . & BS-7671:2008.
It is necessary . in appropriate circumstances . Toprovide means to “ Provide “ means to “ Prevent “ any equipment from being Inadvertently or unintentionallyEnergized .
Safe Isolation . ( Padlocking in the Isolated Position )
BS-7671:2008. No VoltageLimitations are Specified . Yeah :19:
Electricityat Work 1989 / Reinforces this ( Regulations apply to all System )
BS-7671:2008. 2392-10 – These are Designed toEncourage Good Practice . Yeah .
Ihave Knocked something Up . in wording .to help you along the Way . Amber . :thinking2:
Thefollowing Test results . States what tests have been performed & which meter has been used .
( Ω) • Low-résistance ohmmeter / Continuitytester .
(MΩ ) • An Insulation résistance tester .
( Ω) • A Loop impedance tester .
(mA ) • A residual current device ( RCD ) tester …….. -&s / GN-3. ( Test instrument should not beoperated for longer than ( 2 seconds )
(kA ) • A prospective fault current ( PFC ) tester .
( Ω) • An earth electrode résistance tester .
An approved test Lamp orvoltage indicator ……. GS-38
A Proving Unit …….. ( Thisis an Optional item of Test equipment )
Insulation Résistance test isthe correct term for this form of testing .
Loop Impedance tester .
Thisinstrument functions by creating . in effect . an “ EarthFault “ for a brief moment . & is connected to the circuit via a Plug or by “ Flying Leads“ connected separately to Line . Neutral . & Earth.
( The instrument should only allow an Earth Fault to exist for a maximum of ( 40mS ) &resolution of ( 0.01Ω ) is adequate for circuitsup to ( 50A )
PFC tester .
Normallyone half of a dual loop Impedance ( PFC ) tester . This instrument measures the prospective ( Line Neutral FaultCurrent )
atthe point of measurement using the same leads as for ( LoopImpedance )
Shouldbe Banned (- “ NeonScrewdriver “ which encourages the passage of Current . at Low-voltage .Through the body .
Proving Unit :
Thisis an Optional item of Test equipment . in thatTest Lamps should be proved on a known Live Supplywhich could . of course be an “ Socket Outlet/ Lighting Point )
TestLamp on such A Known Live Supply may involve entry into “ Encloses “ with the AssociatedHazards
-&-s. Point to Note . TestLamps must be Proved against a ( Voltage Similar ) to that to be Tested . ( 230V.. Lamp ) ??????
BS-7671:2008. requirements .
AnElectrical InstallationCertificate can be issued only by the Installerresponsible for the Installation Work . :oops: BS-7671:2008
UsefulJunk .
Asyou Know . Maximum Touch Voltage ( 50V )
TT/ Electrode of 100Ω & RCD of 300mA. What would the Touch Voltage Be???? :oops: 100 x 0.3 = 30V - Touch Voltage .
amberleaf,