This is for the people still in or has just left their electrical education or for those of us that need a refresher in domestic earthing arrangements. It's all very well looking at prity diagrams in college and in books but its different when your out in the field for the first time. Hope this thread helps you and I hope that other members will post up their pictures of main incomers/earthing so others can learn and understand this subject better. I wish I could refer to something like this when I was in college.



First of all we have 3 types of earthing arrangements, TN-S, TN-C-S and TT.

TN-C-S
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's


This is where the main earth cable from the main earth terminal (met) is connected to the neutral at the suppliers main fuse. A good way to remember the name of this arrangement is to think of the C meaning COMBINED.


TN-S
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's


This is where the main earth cable from the met is clamped or solderd to the steel of the SWA or the led outer sheath of the incoming supply cable. Again a good way to remember this is to think that the S stands for SHEATH.

TT
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's


The main earth cable from the met is connect to an earth electrode (aka earth rod). This is because not all properties are supplied with a TN system by the supplier so we have to insert a rod into the ground.


Notice how the earth cable on the TN systems go back to the main incomer, one goes to the main fuse (TN-C-S) and the other goes to the incoming cable (TN-S). If the main earth cable doesn't go back to the fuse or incoming cable it will be a TT. This is the simplest way I can put it without going into extended detail.



Now that we've seen some prity diagrams (am I starting to sound like a teacher lol) we will now look at real world photos that are not as straight forward as the diagrams.


First example, is it a TN-S or a TN-C-S or both?

[ElectriciansForums.net] Earthing Arrangements Explained + Photo's
 
Last edited:
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's



DNO drawing for ground mounted
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's
 
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's



DNO drawing for ground mounted
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's
and when you think about it Tony...its just common sense isn`t it...

differing potentials n all that lot...
 
and i`ll say this as well Tony..

one of the neighbours up until recently had issues with extranious in his house with voltage sitting on it..

then he said one day the DNO came out and were doing something...
ever since then the extranious in his house has been clear....

hmm.....
 
The DNO’s also have another crafty trick with MV OH earthing. You may have seen section switches on OH lines. If you look there will be an earth running from the switch metalwork to the ground. It isn’t a rod, there will be a mat.
The idea is that the ground the operator is standing on is at the same potential as the switch metalwork. Where it gets tricky is approaching the switch, I was taught “the shuffle”. You don’t go striding up to the switch as there could be a ground voltage gradient, you shuffle towards it not putting one foot fully in front of the other.

PS I don’t like MV OH lines.
 
Cows are more sensitive to the gradient effect because of the distance between their legs (this applies to some TV 'celebrities' as well). Luckily most cows don't need to operate MV switchgear - they normally stick the the LV stuff. Daz
 
PS I don’t like MV OH lines.[/QUOTE]

Oh boy, this is all filling me with confidence, not! So, as a poor soul who has to live with an overhead supply, is there anything I can do/have done to make it safer? Apart from avoid crawling about on all fours! The DNO is clearly not concerned until some poor sod discovers a fault!
 
Oh boy, this is all filling me with confidence, not! So, as a poor soul who has to live with an overhead supply, is there anything I can do/have done to make it safer? Apart from avoid crawling about on all fours! The DNO is clearly not concerned until some poor sod discovers a fault!

If you know there's a fault, supplies gone off etc. Don't go nosing around the MV gear, simple as. If you're that woried, talk to the DNO. If you're on a farm then it's worth a phone call.

Remember I’m talking of fault conditions, not the everyday life of country folk.
 

Reply to Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top