I just re-read your post reply, maybe this was an addition written after your initial post?? But this statement is totally Wrong! I'm not sure where your information is coming from, but the armouring of either 70C PVC or 90C XLPE 2 core SWA cables DO COMPLY for use as the CPC. 3 core 10mm SWA cables and above will comply with both equipotential bonding and CPC provision for the cable (Please check the sticky section on this subject (above) particually the tables in the link within post #37 by spinlondon)

I notice that you and some others, often use the term ''CPC'' when referring to equipotential bonding conductors. They are substantially different animals in fact, and perform totally different roles within an electrical installation and should never be confused with each other.

umm.....
I have looked at this 'sticky' post and it confirms what I have said. and is substantiated by the DNOs recommendations regarding the use of SWA's supplying external installations ( albeit back in the 80's).
10, 16, 25 mm2 2-core XLPE SWAs are insufficient to be be used as both a cpc and a MPB
I don't ever remember referring to a MPB as a cpc although they may have a duel function in regard to exportation of a PME supply.
 
umm.....
I have looked at this 'sticky' post and it confirms what I have said. and is substantiated by the DNOs recommendations regarding the use of SWA's supplying external installations ( albeit back in the 80's).
10, 16, 25 mm2 2-core XLPE SWAs are insufficient to be be used as both a cpc and a MPB
I don't ever remember referring to a MPB as a cpc although they may have a duel function in regard to exportation of a PME supply.


We must be looking at different tables then, as 2 core SWA cables will comply with CPC provision upto 95mm and possibly by calculation above!
3 core SWA armour cables from 10mm will comply with bonding and CPC requirements, ...bonding via the 3rd core, and CPC via the SWA. I have certainly not inferred that the Steel wire armour was of sufficient size to be used as a means of a combined bonding and CPC conductor!!!
 
We must be looking at different tables then, as 2 core SWA cables will comply with CPC provision upto 95mm and possibly by calculation above!
3 core SWA armour cables from 10mm will comply with bonding and CPC requirements, ...bonding via the 3rd core, and CPC via the SWA. I have certainly not inferred that the Steel wire armour was of sufficient size to be used as a means of a combined bonding and CPC conductor!!!

The RHS XLPE 2-core .... marked in pink
[h=3]Can we use the armour of an SWA as the CPC???[/h]It would help if I made a reference so that we can be clear about things
 
Last edited:
The RHS XLPE 2-core .... marked in pink
Can we use the armour of an SWA as the CPC???

It would help if I made a reference so that we can be clear about things

OK, Now i understand, the table you have been looking at can be a little confusing and often requires adiabatic calculation to confirm compliance. If you check this link out, as posted in ''Post 37 on this thread, ( steel wire armour as the earth conductor ) These tables are far more convienient to use, and are what i have been using for some years now, for a quick reference point to check SWA for CPC compliance...

It is well worth reading the whole of this article, as it can explain many things relating to the subject matter. The author of this article John Peckham, is a well respected Chartered Engineer.
 
OK, Now i understand, the table you have been looking at can be a little confusing and often requires adiabatic calculation to confirm compliance. If you check this link out, as posted in ''Post 37 on this thread, ( steel wire armour as the earth conductor ) These tables are far more convienient to use, and are what i have been using for some years now, for a quick reference point to check SWA for CPC compliance...

It is well worth reading the whole of this article, as it can explain many things relating to the subject matter. The author of this article John Peckham, is a well respected Chartered Engineer.

Thank you for this information. I can see there would be an element of confusion between the two tables.
However, I still find it interesting that the MEB would not allow the armour of certain sizes of 2-core SWA,s above 6mm2 to be used as cpcs.
 
The tables are a little misleading, all swa is now xple 90 C, so adjustments need to made to the tables. The restraints are more prevalent where conductor tempretures are upto the 90C.

Just work out the size of the protective conductor, bonding conductor using the tables or adiabatic, then apply the equation with the correct k values and cross reference with the manufacturers details.

Regards Chris
 
The tables are a little misleading, all swa is now xple 90 C, so adjustments need to made to the tables. The restraints are more prevalent where conductor tempretures are upto the 90C.

Just work out the size of the protective conductor, bonding conductor using the tables or adiabatic, then apply the equation with the correct k values and cross reference with the manufacturers details.

Regards Chris


Spin did send me an updated version by John Peckham, but couldn't find it. However what i remember of the tables, there was very little difference in them...
 
I always run a supply earth to out buildings un less we are specifically advised not to by the regs , i must admit i also never rely on the SWA as an earth i always use a cable incorperating a core that can be used as an earth and soley use the SWA as a meants of protection for the cable you cant beat a proper earth , when you do a caravan install using TT earthing the readings vary so much and i have had them going way over the 200 ohm limit in dry weather when it was wet it was less than 40 ohms so the earthing on a TT can be unstable and we all know how RCD can play up even the expensive ones ,an as i have said if TNS TNCS are permitted then that what ill install
 
This should be the updated version.
As far as I'm aware, it is only the Reg. Nos. that have changed.
View attachment 8067
This is the old one for comparison.
View attachment 8066

The issue with this table along with the ones in GN1 and GN8 is the incorrect K value seem to of been used.

The k value for the line conductors is given as 115(PVC) the problem is the standard now require XLPE for the line conductors. The K value being 154(XLPE)

So an example 2 core 120mm 115/51 x 60 = 135.29 but the insulation isn't PVC, its XLPE

It should be 154/51 x 60 = 181.2 mm, so you can see many sizes would not be adequate using the tables, the adiabatic may well prove otherwise.

The issue seems to of come about as the XLPE is rated to 90C, the problem is most of the time we work to 70C, they haven't included a K value for this scenario, so they used the PVC values, and they don't air on the side of caution.

Ill let you know the outcome, though i don't see how it can be incorrect, several cable manufacturers agree.

Regards Chris
 
I don't know why we keep harping on this 90C aspect for cables, it's highly unlikely that you'll ever see a 70C cable working at anywhere near that tempreture, let alone a 90C cable.
 
Last edited by a moderator:
Yes but no but.
Unless the equipment the SWA is connected to is rated at 90ºC, then the 70ºC tables would suffice.

The tables are using a k value for PVC, initial temp 70C and final 160C.

SWA no longer since 2008 utilises PVC for conductor insulation, so when calculating for short circuit we should be using the specific K value for that material.

XLPE, initial temp 70 and final temp 250 would give a K value of 154, so quite a difference. So as it stands i disagree with the tables.

Regards Chris
 

Reply to Earths at outbuildings... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
124
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
971

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top