Just took the time to do a couple of quick adiabatic calc's using k=154 on these tables and well passed ( 120mm/150mm)
 
Just took the time to do a couple of quick adiabatic calc's using k=154 on these tables and well passed ( 120mm/150mm)

But what level of fault current did you use for the adiabatic, im not disagreeing with the fact the cable is protected, just the tables are not correct.

As long as I2T is less than K2S2 then there's no issue, also taking into account the magnetic effect of the armouring.

It was just the case id worked out some values and cross referenced them with the tables and noticed a difference, then realized they had used K values for PVC. Reality is as you say using the adiabatic they will be ok.

Regards Chris
 
I was under the impression if it was a PME head you was not supposed to extend the earth to the out building but just use a 2 core and stake the out building with an electrode, this was told to me by my 2391 tutor when I was on my course. Is this right or wrong, either way can you point me to the reg in the BRB that states it.

Cheers

ICE
 
I was under the impression if it was a PME head you was not supposed to extend the earth to the out building but just use a 2 core and stake the out building with an electrode, this was told to me by my 2391 tutor when I was on my course. Is this right or wrong, either way can you point me to the reg in the BRB that states it.

Cheers

ICE

A 2391 tutor who believes in mythology?....the mind boggles.:uhoh2:
 
Well what ICE was saying was what I was getting at in a way, except it the install is a TT system at origin do you run a 3 core to the outbuilding carrying a CPC as one of the conductors or do you run a 2 core and put an electrode in at the out building connecting to the sub mains there?
 
Well what ICE was saying was what I was getting at in a way, except it the install is a TT system at origin do you run a 3 core to the outbuilding carrying a CPC as one of the conductors or do you run a 2 core and put an electrode in at the out building connecting to the sub mains there?

Why would you want to isolate a TT system earthing system?? If anything you would want to connect the 2 rod positions together giving you a theoretical better/lower Ra level for the installation as a whole!!
 
Agreed Engineer. If the reading on the rod at the sub building is low. In this case 18 ohms. Would I be right in saying that no regs would be broken if a 2 core cable is used to save on cost?
 
Agreed Engineer. If the reading on the rod at the sub building is low. In this case 18 ohms. Would I be right in saying that no regs would be broken if a 2 core cable is used to save on cost?

No Reg's will be broken, but will in my opinion be a false economy!! The cost of a 3 core cable is not going to be that much more than a 2 core...
 

Reply to Earths at outbuildings... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
124
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
971

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top