Just took the time to do a couple of quick adiabatic calc's using k=154 on these tables and well passed ( 120mm/150mm)
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Earths at outbuildings... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I don't know why we keep harping on this 90C aspect for cables, it's highly unlikely that you'll ever see a 70C cable working at anywhere near that tempreture, let alone a 90C cable.
Just took the time to do a couple of quick adiabatic calc's using k=154 on these tables and well passed ( 120mm/150mm)
I was under the impression if it was a PME head you was not supposed to extend the earth to the out building but just use a 2 core and stake the out building with an electrode, this was told to me by my 2391 tutor when I was on my course. Is this right or wrong, either way can you point me to the reg in the BRB that states it.
Cheers
ICE
Well what ICE was saying was what I was getting at in a way, except it the install is a TT system at origin do you run a 3 core to the outbuilding carrying a CPC as one of the conductors or do you run a 2 core and put an electrode in at the out building connecting to the sub mains there?
Agreed Engineer. If the reading on the rod at the sub building is low. In this case 18 ohms. Would I be right in saying that no regs would be broken if a 2 core cable is used to save on cost?