Be careful how you apply this equation! It is used to confirm the resistance between 'extraneous parts' is adequate for protection when you have doubts about the effectiveness off the 'supp' bonding. I dont take it as being an alternative mathematical solution to confirming 'supp' is physically present by use of the mark 1 eyeball.
The equation is used to determine whether supplementary bonding is required.
You cannot tell by looking at some pipes.
If all the water/gas pipework is already bonded then you will get continuity if no supplementary bonding is present as everything is tagged back to the MET? (assuming no plastic pipework!).
If those values are below 50/Ia then all is well.
If the 'supp' is physically there and you loose one of the main bonds to water/gas then the additional protection is still provided. For me this is what the regulation is about,
But it isn't.
ensuring the additional protection is there by physical bonding between all the "extraneous" parts.
You seem to be confused by the meaning of 'supplementary'.
1. Something added to complete a thing, make up for a deficiency, or extend or strengthen the whole.
So, if complete, not deficient, strong enough or whole already then not required.
Not at all, I think im quite clear in my understanding but without wanting to get into another long thread of back and forth arguements, I'll agree to disagree with you on our intepretation of the regs.
However, you may also want to check the closest definition to supplementary that counts --- in the BGB definitions -- not exactly supplementary bonding but gives a flavour. Also the ECS recommendations around what constitutes supplementary bonding and its application gives a further indication as to what supplementary bonding is about -- bearing in mind that the ECS is supported in its statements by the IET (owners of BS7671) and the large electrical bodies that speak for the industry (NICEIC/ECA etc ....)
But hey, each to their own as they say in their interpretation of the regs. The only time you really need to justify it is in a court of law ......
I like following what the ECS says so i would.
But I cant really understand the thinking behind it, as far as I can make out the exposed and extraneous parts are electrically connected. If they are not I would think C2, as they are C3.
Have you got a link to the ECS lit badged?
.... I cant really understand the thinking behind it, as far as I can make out the exposed and extraneous parts are electrically connected.
You need to convince yourself one way or the other as to whether physical conformation of supplementary equipotential bonding is required in the bathroom (in addition to the existing main protective equipotential bonding to water/gas) by having a read of section 701 on supp bonding, looking at the pretty pictures in GN8 which show the supp bonding connections (note the dead give away as to whether supp bonding is present in the bathroom by there being a connection at the light fitting!) and the ESC publications which further expands on both of the former. (Havent got a link to the ESC website publication but a quick internet search will lead you there).
Ultimately all these documents are there for "guidance" and you have to make the decision on the need to confirm supp bonding or not based on your interpretation of the regs requirements. And you can see from the thread views on YES/NO, no-one is truely in agreement so good luck!!
You don't need to convince yourself of anything other than doing it properly.
The problem in this thread leading to what is being termed 'different views' is that the ESC document is not considering the situation where supplementary bonding is NOT REQUIRED because the impedance of the parts is low enough in itself to limit any touch voltage to the safe amount.
You cannot tell by looking at the parts whether supplementary bonding is missing or not required.
There is, of course, another option where no supplementary bonding is visible; that the parts are not extraneous anyway and bonding would introduce hazards.
….. is not considering the situation where supplementary bonding is NOT REQUIRED because the impedance of the parts is low enough in itself to limit any touch voltage to the safe amount…….
I didn’t want to end up with a lengthy and boring to and fro thread but feel you are completely off course in your interpretation/understanding of the application and need for supplementary equipotential bonding. Nowhere can I find anything that states supp bonding is not required if the impedances are low enough to limit meet the touch voltage requirement.
Section 701 states additional protection in the form of supp bonding SHALL be established connecting protective conductors to accessible extraneous-conductive parts in the location. My interpretation is there has to be a physical connection to achieve this in the location and this is supported by the advice/pictures/drawings in GN8 and the ESC publications.
Change the word “insulation” for “bonding” in the definition of Supplementary in the BGB. This I believe gives a further intent as to application of supplementary. That is supp bonding is applied in addition to main bonding for fault protection. (“applied” I interpret as meaning a physical connection as with main bonding.)
If main bonding is fitted you will always get a reading in the bathroom to showing continuity and 90% of the time it will meet touch voltages (assuming continuity of metalwork). Hence a reading alone will not prove supplementary bonding is physically present. You need to see it to confirm its presence.
Once you can see supp bonding, if you have any doubt as to the “effectiveness” of that supp bonding then you can test as per 415.2 using said touch voltage equation. No where in the regulations can I see anything that suggests this test alone is a substitute for confirming sup bonding is present, just “effective”. Its application is purely as a test if not sure that the supp bonding is “effective” in providing additional protection. (i.e. you’ve seen it and now want to test to confirm compliance.)
Even to apply this equation in practice, for me you have to be able to physically disconnect an end of the sup bonding and test, because if you have any bonding elsewhere in the premises your results will be effected by parallel paths. So if sup bonding isn’t there in the first place you cant prove its effectiveness just by using the equation?
At the end of the day sup bonding is there as an additional fault protection method and if you cant confirm its presence (not effectiveness) by the good old mark one eye-ball then no testing to an equation will convince me it is, just hidden somewhere. Lack of sup bonding can have serious implications in a fault situation should for example main bonding be lost, hence why the ESC consider lack of its presence being a C2 without an RCD fitted??
If there is anything in the regulations that Ive missed or goes against anything Ive stated then please advise and correct me. I am always learning and seeking new knowledge and understanding.
There is no requirement for the terminations to be accessible or visible.
Sorry for the delay, missed this point first time round.
How will you check/ensure conform with 514.13.1 (ii) regarding warning labels if you cannot access to inspect? Just grade it code C3 as not being there regardless (safe bet!), or assume there must be one there if you are getting a reading and ignore it?
I'm sure Geoff doesn't need me to spring to his defence but I don't think he is 'off course' in his understanding of the requirements for supplementary bonding at all.
Neither of us have said this^^^, what we have said is that supplementary bonding would not be required between non-extraneous conductive parts, and just looking at pipes isn't going to tell you whether they're extraneous or not.
And you'd be completely and utterly right if we were referring to a new installation and supplementary bonding couldn't be ommitted as per 701.415.2, but we're not. We're talking about periodic inspection where depending on the installation a few assumptions are going to have to be made.
No, supplementary bonding is applied for additional protection only, not fault protection.
And how do you propose to do this on a periodic inspection? There is no requirement for supplementary bonding connections to be visible or accessible. Are you going to start ripping apart the floors, walls and ceilings just to see? If it's not visible, then the application of R≤50V/Ia is good enough to be able to assume that supplementary bonding is in place and is effective.
If you want to apply your way of thinking then the best you could do when confirming the presence of supplementary bonding is to LIM it if you can't see it.
No, but you can make an assumption that it is there by applying the appropriate test. If that test is there to confirm the effectiveness of supplementary bonding, then if the results show that it is effective, then it says to me that it is there or as good as there.
As above^. And I say again, supp bonding is not there for fault protection, it is additional protection only.
Aren't we all, but maybe seeking understanding from the ESC and thier interpretation of the regs book, which in itself is riddled with flaws, isn't best practice :)
Use your own head mate, if you can't see something but evidence suggests that it is there or at least as good as being there, then what's the issue?
By making sure that it is visible when access is gained to the extraneous conductive part in question. That regulation I believe was only meant to apply to main protective bonding conductors anyway.
Absolutely, but thats not what Im saying. If they are extraneous, which is what im being led to believe they are, then they must be supp bonded. My arguement then is that the only way to tell if they are bonded to start with is is to see if the bonding is physically there! It doesnt mean its complete, it could be broken. But if it is there then testing confirms the adequacy of said bonding, not that the bonding is there in the first place.
No, if doing an EICR you do it to the latest regulations and record your deviances as such -- no bonding is a deviation-- you dont inspect to what previous regs may have allowed or not. What you have is an caveat in the regs that because it was to a previous reg it doesnt make it unsafe, you as the inspector make that call. (I'm not that old but hasnt supp bonding always been a requirement under previous regs??). My arguement is that the "governing bodies" have deemed it unsafe not to have it without RCD top cover but whether you hold to this is entirely your choice as the inspector. Only you answer for your decisions on how you code it!
Wrong, you seriously believe additional protection is not for fault protection?. (Check 415.2 note 1). If not for fault what do you actually believe it is there for?
And how do you propose to do this on a periodic inspection? ...... If it's not visible, then the application of R≤50V/Ia is good enough to be able to assume that supplementary bonding is in place and is effective.
Thats my arguement, the equation is flawed unless you have disconnect all other bonding as you will get a reading and assume it is present even if it isnt? If you cant disconnect all other bonding (cos you dont know what other bonding may be hidden?) the only failsure method to prove supp may be there is to see it. To prove it is effective you test -- not the other way around. Your right though, I wont be ripping up floor boards. If I cant see any signs of supp bonding I assume its not there and code -- I wont rely on a test between part to prove supp bonding is present.
Valid point, you could exclude from the EICR. Personally I wont.
Not necesarily, if you have parallel paths due to other bonding elsewhere in the premises you will always get a reading. Only if you can remove every possible parallel path would this method be effective. (Have I just convinced myself of a possible method to use this for proving the presence of supp bonding?)
.....I say again, supp bonding is not there for fault protection, it is additional protection only.
And what do you believe additional protection is for if not to protect against a fault?
.... ESC and thier interpretation of the regs book, which in itself is riddled with flaws, isn't best practice
I'll leave that one with you to argue! I in no way consider myself of sufficient knowledge and experience to challenge the 'big boys' and their technical 'experts' -- plus on their interpretation and guidance I actually think they are right!
In agreement with you there if the evidence supports the probability. But my disagreement on this particualr issue with supp bonding is that not being able to see it I wont rely on a test to convince me (evidence) that it is there. I am risk adverse, numerous kickings for assumptions at work have made me that way, so always err on the side of caution. The receiver of the EICR can ignore what I state if they want, its my perogative as the inspector to make my assessment and its the perogative of the client to ignore it. I just like knowing my butt is covered should the sh8t hit the fan!
p.s. I have no personal disagreement with anyone, im just exploring the technicalities of supp bonding
But the discussion so far is that it isnt accesible ..... hence using the "equation"
Nope, "every protective bonding conductor" --- you may interpret it that way but for me it means what it says on the tin!
Edited: Forgot to add that unless the connection to the pipework is 'permanently made' it should be accessible for inspection, testing & maintenance (526.3), Again I dont think this requirement is just a 17th edition update?
Supplementary bonding is not for fault protection, that is earthing - fact, but to equalise, or reduce to an acceptable level, potential difference between two (or more) parts in the event of a fault.
That is, to reduce the impedance between these parts in order to minimise volt drop when a fault occurs causing current to flow between these parts until the opd operates.
The accepted safe voltage is 50V therefore this impedance must be below 50/Ia. See 415.2.2
If the impedance between the parts is greater than this value then supplementary bonding is required to reduce that impedance.
However, if this impedance is already below 50/Ia because the runs (from main bonding and consumer unit) are short enough or connections elsewhere then supplementary bonding is not required because the conditions are already met.
For example a small flat: the water service entry, hence main bonding, DHW cylinder and the consumer unit are all on the other side of the bathroom wall.
The maximum run, from the bathroom, of pipes to main bond and cpcs to consumer unit is three metres.
The only circuit in the bathroom is the lighting.
As it is allowed to use a pipe as a supplementary bond the conditions are satisfied by the pipes themselves.
The pipes are then effectively connected to the MET and cpcs by the main bond itself.
So, If the measurements are within the acceptable limit it does not matter (for EICR) if the reason for this is satisfactory supplementary bonding out of sight (SB does not have to be IN the location), connection between the parts elsewhere or the low impedance of the parts themselves.
Saying that supplementary bond shall be applied is true but it only if required.
Ideally you're right, but with periodic inspection we are not dealing with ideals, we're dealing with limitations.
You misunderstand me. I wasn't referring to a 'new' installation in terms of its compliance with current regs, I was referring to a new installation in general. If you were wiring from scratch and supplementary bonding was needed then you'd have to fit it and then test it to confirm its effectiveness, but when carrying out periodic inspection then you are making assumptions as to its suitability for continued use. If a test indicates that supplementary bonding is there or is as good as there then you can assume that it is.
No, it is an addition to fault protection, it is not used for fault protection. See 415.2 note 2.
I agree
I agree
I agree, with a 'but'.
But you rely on an R1+R2 test to prove that a cpc is there don't you??? No. Think about it, unless you are carrying out initial verification there is not a single continuity test you can carry out without risk of parallel paths being present. You are carrying out an EICR, you are not there to 'prove' anything, you can however use your test results to suggest that it is there.
I wouldn't exclude, I would say that although I cannot see any sign of supplementary bonding, my test results suggest that it is there.
As above, do you ensure the removal of every parallel path when conducting an R1+R2 test during an EICR?
As above, it is in addition to...
Big boys??? No mate, suits, nothing more, many of which with little experience of the practical application of the regulations. Could I challenge them on the whole regs book? No, certainly not. But I could certainly challenge them on certain sections!
Again, when carrying out an EICR you're working with what you have and what you can see and test. It is a report, not a certificate, therefore you can say whatever you want really! If you wanted to give everything a C1 regardless of its severity then that's your prerogative (although evidently you wouldn't make a very good inspector), and you still remain responsible for nowt! Every inspection you carry out and every test result you gain is nothing more than a suggestion as to the current safety of the installation. I reiterate, periodic inspection and initial verification are two completely different ball games.
Neither do I, but the vagueness of the regulations gives rise to threads such as this occuring highlighting the relevance of my comment regarding challenging the suits up at the IET! :)
If that isnt fault protection (shock) what is it? Protection against thermal effects, overcurrent, voltage or electromagnetic disturbances? Or is there some other protection for safety in the BGB that supp bonding is and I've missed? (415.2 note 1 also mentions supp bonding being an addition to fault protection)
[/QUOTE]The accepted safe voltage is 50V therefore this impedance must be below 50/Ia. See 415.2.2
No problem with that, reg 415.2.2 as you state
Is that a direct quote from the BGB? -- if so please point me to the reg as the only regs I can find are in 701 stating supp bonding must be in place and 415 where it states what must be supp bonded and how you can use the 'equation' to confirm the effectiveness of this supp bonding when in place. I cant find anything that states that if the 'equation' value is greater then only then, and then only, must supp bonding be installed?
Totally disagree, supp bonding is a requirement under 701/415 regardless of readings.
For example a small flat: the water service entry, hence main bonding, DHW cylinder and the consumer unit are all on the other side of the bathroom wall. The maximum run, from the bathroom, of pipes to main bond and cpcs to consumer unit is three metres. The only circuit in the bathroom is the lighting.
The regs allow supp bonding to be either in the bathroom or close to where the 'extraneous' parts enter the bathroom. Whether you can combine supp bonding and main bonding as the same thing just outside the bathroom sounds like another thread to discuss! Ive never thought of it like that but I can see its merits!.
New one on me! I know you can use the CPC of attached equipment as a bond (544.2.5) but didnt know a pipe was an acceptable conductor alternative. Where is this pipe as a bonding conductor defined?
Thats not the point of supp bonding -- to connect to the MET. Its to connect all the 'extraneous parts', 'protective conductors' etc ... together in the bathroom to form I guess a faraday cage? But you raised an interesting point before, can the supp bonding and main bonding be one of the same thing when just outside the bathroom
I think it does matter what is causing the reading ..... the definition is in 701 that supp bonding must be in bathroom (or close by) and 415 which defines a physical connection between all the bits, the effectiveness of this connection being proved by the 'equation'. Again if there is a reg that over rides these requirement then please quote. Or if my interpretation of what the regs state is clearly wrong please define which part supports your arguement.
No arguement from me there. Totally correct statement!
EICR and Supplementary Bonding.
rattlehead85,
D Skelton,
TrueNAS JBOD Storage Server