Hi all, I have done a few EICR's before however could do with a bit of advice on what codes you more experienced guys would give these observations;
1 Old 3036 DB made up of wooden base/back. (C3?)
2 Underszed main bond. (C3?)
3 Cooker switch mounted 18" above cooker (C3?)
4 Mutiple cct's in MCB (C3?)
Thanks for any input.
 
Then you need to re-calibrate your brain.

Multiple radials from one OCPD are classed as one circuit which is spurred at the OCPD.
Dividing these branches into separate OCPDs would make them individual circuits.
This is by definition, and cannot be anything else.
he is a lost cause andy, he wouldnt understand parallel supplies either.

a parallel supply is exactly the same so no code.

besides smokes would be looped off perm L from a light not back to board
 
Nope. We are gonna have to agree to disagree on this one.

Does the definition for final circuit mention an OCPD ? No
Does the definition of either final circuit or circuit mention standard arrangements or your preconceived ideas of what a circuit should be ? No
If a radial was spurred off into three branches along it's length would you say it was separate final circuits ? No
So when it is spurred at the OCPD is suddenly becomes more circuits ? No
Is the definition of circuit an arrangement in any form, not just standard final circuit arrangements, supplied by the same OCPD ? Yes

It's not agreeing to disagree, it's just your failure to read and understand definitions.
 
I fail to see how hard this is to comprehend?!

Let me make this simple for you UKES; that regulation is there to prevent people from connecting one circuit to two OCPDs.

No matter how many conductors there are in one OCPD, it is still one circuit. Take a branch from that one circuit and connect it into a second OCPD and you would then be in breach of this regulation.
 
So in your opinion when would 314.1 come into force?


At the design stage.
You wouldn't put everything onto one ocpd so the installation is divided into circuits. Lighting,power heating etc.
Similarly, an installation with say several rooms or floors or high loads wouldn't have all the power on one circuit. That's where reg 314.1 comes in.
How these circuits are arranged or divided up is down to the person designing the installation.
Now, if for example he puts several rooms onto one way of a db then that is one circuit.
 
Does the definition for final circuit mention an OCPD ? No
Does the definition of either final circuit or circuit mention standard arrangements or your preconceived ideas of what a circuit should be ? No
If a radial was spurred off into three branches along it's length would you say it was separate final circuits ? No
So when it is spurred at the OCPD is suddenly becomes more circuits ? No
Is the definition of circuit an arrangement in any form, not just standard final circuit arrangements, supplied by the same OCPD ? Yes

It's not agreeing to disagree, it's just your failure to read and understand definitions.

So when does a final circuit start / finish?
 
I am starting to come around to what you are saying gents. It must be the eliquent way in which you put it. Do I agree? Probably not. No big thing. If carry on doing things how I have been taught it still is not wrong is it?
 

Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
437
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top