immersion heater and a shower pump

Hi im new to this site, you are correct the Imm Heater should not be on a plug top nor should it be on a 13 amp double pole fused spur, it should be on a 20 amp doulbe pole unfused spure

So should I remove the plug top from my 3kw kettle and put the kettle on a 20 amp pole switch ? OMG
 
the immersion heater is wired with a plug top for a good reason. it's so he can shove the cable to the pump in with the plug pins, saves using matches.
 
i'll raise your code 3 to a code 2
 
So should I remove the plug top from my 3kw kettle and put the kettle on a 20 amp pole switch ? OMG

Are you sure your kettle does not say 2800 to 3000 watt, as your kettle reaches that point of say 3000 watts, for a short spell, yes it is over the raiting of the fuse, but for a short spell, also if you was to calculate the real Voltage of the supply you would find it is over the stated amount of 230 volt in the regs, you may find it at say 242 volts and yes this would lower the current that would be drawn through the fuse and thus protecting the appliance and house from fire, but as i said before if you want to comply with the regs you must apply the regs, and yes if your kettle was to be on for an Hour constant, yes i would recomend you cut the plug off. and yes i would saythat it would e a code 2. But come on we are only on this site to make things better, and Clarification, not who has the biggest Regs book.
Crazy thinking always comes clear in the end.
 
Last edited by a moderator:
Are you sure your kettle does not say 2800 to 3000 watt, as your kettle reaches that point of say 3000 watts, for a short spell, yes it is over the raiting of the fuse, but for a short spell, also if you was to calculate the real Voltage of the supply you would find it is over the stated amount of 230 volt in the regs, you may find it at say 242 volts and yes this would lower the current that would be drawn through the fuse and thus protecting the appliance and house from fire, but as i said before if you want to comply with the regs you must apply the regs, and yes if your kettle was to be on for an Hour constant, yes i would recomend you cut the plug off. and yes i would saythat it would e a code 2. But come on we are only on this site to make things better, and Clarification, not who has the biggest Regs book.
Crazy thinking always comes clear in the end.


As I missed regulation 554.3.3 already, would you mind posting the reg number about the non compatibility of a 13amp FCU please
 
Last edited by a moderator:
As I missed regulation 554.3.3 already, would you mind posting the reg number about the non compatibility of a 13amp FCU please

Malc

A 13amp plug top or a 13amp switched fused spur is sufficient to protect and operate the domestic type 3kw immersion heater.

Regulation 554.3 applies to uninsulated elements, not the insulated ones found in domestic type water cylinders and kettles.

People who are not sure of the Current IEE Regulations should seriously consider joining a scheme provider and use the Technical Help Phone Lines they provide.
 
Hi im new to this site, you are correct the Imm Heater should not be on a plug top nor should it be on a 13 amp double pole fused spur, it should be on a 20 amp doulbe pole unfused spure, the reason being is that under current regs the 13 amp double pole fused spure falls below the required protection, this is due to the current regs using the voltage range of 230V and not 240V calc this and you will come up with 2990 watts, and as you have stated the IMM heater is 3KW no diversity allowed 100%, and as for the shower pump is the plug top located out side the zones, if so then this would be ok acording to current regs, under a bath with a fixed panel screwd would also meet current regs, as this is clased as having to use a tool to gain access to under the bath, but must be fused acording to raiting of pump.
If not no cert can be issued for work, pump does not require one if out side zone on plug top. but IMM heater will.

I think you are confusing your manufacturers stated ratings.
The stated rating for an immersion is usually 3kW at 240v. this gives a current of 12.5A.
The manufacturer may state an equivalent rating at 230v, which would be 2875W.
This is for the simple reason that the resistance of the element is the same no mater what voltage you apply to it (at a given working temperature and ignoring minor variances). Reduce the voltage and you reduce the power.

It's the same with showers. Manufacturers still quote the rating at 240v, because the wattage figure is higher than at 230v and so makes the shower 'look' more powerful. And in any case we pretty much still have a 240v supply anyway - the figures are something of a fudge.

What you seem to be doing is dividing the 240v rating by 230v, which is not correct.
 
As I missed regulation 554.3.3 already, would you mind posting the reg number about the non compatibility of a 13amp FCU please


Guidance note 1, page 131, says "Immersion heaters should not be connected by a plug and socket-outlet, but by a switched connection unit complying with BS 1364-4." and i am sure you know already BS 1363-4 is the specification for 13A fused connection units, switched and unswitched.
 
People who are not sure of the Current IEE Regulations should seriously consider joining a scheme provider and use the Technical Help Phone Lines they provide.[/QUOTE]


or retrain as a 6 week wonder plumber
 
People who are not sure of the Current IEE Regulations should seriously consider joining a scheme provider and use the Technical Help Phone Lines they provide.


or retrain as a 6 week wonder plumber[/QUOTE]

Don't care where they go or what they do as long as they get well away from this industry, its giving the industry a bad name.
 
So when are you going to start your painters course,
All you have to do is calculate it chap. Also BS EN 60669-1 spur out let 20 amp, protected by a 16 amp circuit breaker, at db, why would you put a fused spure in line on a dedicated supply for a IMM Heater. Isolating at the db then allows for maintenance, so what you are saying im wrong in my practice, or just over protecting, if you can say 100% yes to that then, prove im wrong. or explain yourself better.
 
why would you put a fused spure in line on a dedicated supply for a IMM Heater. Isolating at the db then allows for maintenance, .

A double pole, switched fcu beside the immersion allows for local isolation that is in view of the person carrying out the maintenance and allows a point to change to heat proof flex.
 
I under stand this, what im saying is that you would use a 20 amp db pole switch and the protective devices at the ccu would be 16 amp.
this would also give local isolation, but you would still need to isolate the circuit as you may have a loose wire in the spur.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
pushrod,
Last reply from
richelec,
Replies
140
Views
40,763

Advert

TrueNAS JBOD Storage Server

Back
Top