What table do I use in the on site guide to find the maximum Zs for a TT sytems? My Ze is 3.61 so they all be over anyway?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss maximum zs in the Australia area at ElectriciansForums.net
ok so shall i put 1667 on the sheet for every circuit?
Thanks
Andy
Only on those circuits protected by a 30mA RCD.ok so shall i put 1667 on the sheet for every circuit?
Thanks
Andy
To be pedantic the maximum Zs allowed on a TT system, is not necessarily 1667Ω.
That figure only relates to wher 30mA RCD protection is installed.
Where 100mA RCD protection isinstalled, 500Ω is the maximum.