Hi Pete999, here is a partial screenshot of a page of the doc.
Clipboard01.jpg
 
The only one i can see on the report just above the testing schedule info I sent, Measured Ze: 0.65. The other parameters you describe are not included on the report that i can see, other than on the testing schedule info I already uploaded. What I mean is there isn't any box into which any of these test values could be written, unless I'm just overlooking them. Are you sure that this particular form requires a test result rather than just confirmation that a test was or was not done? I can't see any boxes for these values, it's not that the electrician has left them empty.
 
Other values I can see:
Nominal frequency: 50Hz
External earth fault loop impedence Ze (2/3): 0.57
Prospective fault current (2/3): 0.5

the report also states that he used for testing equipment, a Kewtech KT64 (might be 84, hard to read)
 
When changing a consumer unit I would expect to test and record R1+R2 values for radial circuits, r1, rn, r2 and R1+R2 values for ring final circuits. Insulation resistance for each circuit. Zs for each circuit and RCD trip times for each RCD/RCBO on the board.

These prove continuity of the protective conductors on the circuit (R1+R2) and go a long way to proving the correct polarity of the circuits, end to end continuity of ring final circuits (r1, rn and r2), give an indication of the condition of the cables and demonstrate there is nothing on the fixed install that might trip the RCDs (IR), demonstrate that the circuit can meet the requirements to achieve the maximum disconnection times required by BS7671 (Zs) and that the RCDs will operate in a manner that should save your life (RCD trip times).

Without these tests you can't say the installation is safe and in my opinion, he should not really have signed it off.
 
Other values I can see:
Nominal frequency: 50Hz
External earth fault loop impedence Ze (2/3): 0.57
Prospective fault current (2/3): 0.5

the report also states that he used for testing equipment, a Kewtech KT64 (might be 84, hard to read)
file:///C:/Users/Pete/Downloads/BS_7671_2008_AMD3-2015_Model_Forms(3).pdf
Nothing akin to this see download
 
Vol, do you have a snap shot of the 'Circuit Details' and the 'Test Instrument Used'?

PS good that the dangerous fault has now been rectified. Its a shame your electrician didn't do all the form filling in and testing in the first place.
 
Last edited:
Just been looking at a forum on the ------.org website. Some bright spark says that the average pass rate is 60%? Not sure about the significance of that except I guess that not all electricians are right all of the time and then they forget! This has been a case in point! My electrician needs a refresher course!
Thanks for all the help I did get. Many of the early answers were right on the button and were as I thought: not overly dangerous except in specific conditions and probably the meter tails had been swapped over. I actually emailed over the weekend to British General, the manufacturer of the CU, and this morning they answered saying much the same.
I've tried to show willing in response to the help I did get by showing as much info from today's resolution as I could. I'm done now. Obviously not perfect, but then again, who is?
As for those that jumped on this bandwagon started by Midwest "Are you thinking what I'm thinking and probably what everyone else is thinking, or am I being just too cynical suspicious", please adopt a more constructive, more friendly approach next time and please change your motto from Guilty Until Proven Innocent! :) Cheers!
 

Reply to New Consumer Unit Installation - L&N Reverse at the sockets in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
The 0.05 ohms comes from the OSG, I have not seen it in the regs book. Certainly if the readings obtained were for intial verification tests as...
Replies
2
Views
722
OLDBOY
O

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top