Hi All,
I recently replaced an old rewirable fuse board for metal split load rcd board. However on testing prior to replacement I noted that one of the lighting circuits doesn’t have a cpc. I’ve put this in the EIC for the new board that no cpc for lights, advised client that needs rewiring and advise against metal fittings accessories etc,is this the right course of action to take? They do already have metal fittings on this circuit, Is rcd protection enough to cover this? Also the kitchen ring has no continuity on the neutral conductor, I’ve had all the accessories off to find it but can’t, I’m assuming the break maybe in a buried joint box as the kitchen is an old extension. What’s the best course of action to take regarding this please?
Thanks
 
This link is from the horses mouth

18th edition changes - IET Electrical - https://electrical.------.org/bs-7671/18th-edition-changes/

The only thing that jumps out to me about lighting circuits is the requirements for RCD's protecting circuits with luminaries.
I just had a look at that the only thing I could see on Chapter 54 was regarding earth electrodes and protective conductor when more than one source,so I don't know where this so-called new reg comes from
 
That just says recommended so not an absolute. Also that link is to a private company so has as much weight as helium...
IET Forums - Fuseboard Change with no cpc in lighting - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=64580
This link is from the horses mouth

18th edition changes - IET Electrical - https://electrical.------.org/bs-7671/18th-edition-changes/

The only thing that jumps out to me about lighting circuits is the requirements for RCD's protecting circuits with luminaries.
The impact of the 18th Edition (BS 7671:2018) – Chapters 41, 46, 53 and Regulation 542.2.2 - https://electrical.------.org/wiring-matters/issues/66/the-impact-of-the-18th-edition-bs-76712018-chapters-41-46-53-and-regulation-54222/
 
IET Forums - Fuseboard Change with no cpc in lighting - https://www.------.org/forums/forum/messageview.cfm?catid=205&threadid=64580

The impact of the 18th Edition (BS 7671:2018) – Chapters 41, 46, 53 and Regulation 542.2.2 - https://electrical.------.org/wiring-matters/issues/66/the-impact-of-the-18th-edition-bs-76712018-chapters-41-46-53-and-regulation-54222/

The second link is from last year and the proposed changes .

My link above is a summary of what made it into the 18th edition
 
Reading much IET literature and all the above comments, I am still convinced that as long as all the switches and luminaires are plastic there is no need for a CPC on existing old lighting circuits. After all, that effectively makes it a simple "double insulated" circuit, no different from all the hand-held(!) tools and appliances that are sold now for kitchens, gardens and DIY tools (e.g.) which only have a two-core phase and neutral lead. It would be a nonsense to allow (indeed require!) them to be used, and hand-held when in use, and not allow the same electrical situation when the wiring is hidden and out of reach of the person using it. That would be a complete contradiction in safety.
 
Reading much IET literature and all the above comments, I am still convinced that as long as all the switches and luminaires are plastic there is no need for a CPC on existing old lighting circuits. After all, that effectively makes it a simple "double insulated" circuit, no different from all the hand-held(!) tools and appliances that are sold now for kitchens, gardens and DIY tools (e.g.) which only have a two-core phase and neutral lead. It would be a nonsense to allow (indeed require!) them to be used, and hand-held when in use, and not allow the same electrical situation when the wiring is hidden and out of reach of the person using it. That would be a complete contradiction in safety.
Appreciate your hypothesis Mate but it only needs one home owner to start sticking Metal decorative switches and fittings up, on a circuit without a cpc, and that blows your thoughts out of the water.
I don't think or believe that a circuit without a cpc, with plastic switches etc, is the same as a Double insulated hand tool, nice idea, but not for me I'm afraid.
 
Last edited:
Reading much IET literature and all the above comments, I am still convinced that as long as all the switches and luminaires are plastic there is no need for a CPC on existing old lighting circuits. After all, that effectively makes it a simple "double insulated" circuit, no different from all the hand-held(!) tools and appliances that are sold now for kitchens, gardens and DIY tools (e.g.) which only have a two-core phase and neutral lead. It would be a nonsense to allow (indeed require!) them to be used, and hand-held when in use, and not allow the same electrical situation when the wiring is hidden and out of reach of the person using it. That would be a complete contradiction in safety.
the only caveat to that would be to ensure that the faceplate screws did not make contact with metal back boxes. back in the 60's this was achieved by the use of nylon lugs.where a metal back box has been replaced by one with metal lugs, then you have unearthed exposed metal parts.
 
the only caveat to that would be to ensure that the faceplate screws did not make contact with metal back boxes. back in the 60's this was achieved by the use of nylon lugs.where a metal back box has been replaced by one with metal lugs, then you have unearthed exposed metal parts.
Remember the wooden switch back boxes Tel?
 

Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
691
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top