I recently replaced an old rewirable fuse board for metal split load rcd board. However on testing prior to replacement I noted that one of the lighting circuits doesn’t have a cpc. I’ve put this in the EIC for the new board that no cpc for lights, advised client that needs rewiring and advise against metal fittings accessories etc,is this the right course of action to take? They do already have metal fittings on this circuit, Is rcd protection enough to cover this? Also the kitchen ring has no continuity on the neutral conductor, I’ve had all the accessories off to find it but can’t, I’m assuming the break maybe in a buried joint box as the kitchen is an old extension. What’s the best course of action to take regarding this please?
Thanks
 
And unless you take a bit of a scientific approach with additional testing it'll always be the very last socket that you open up with the dodgy connection. :)

It's always the last socket. Why would you open more when you've found the fault ? :grin:
 
Do you know which sockets/outlets the break is between? as if you intend to change the protective device to 20A the NICEIC will take a dim view of the live being left as a ring you will need to test as two radials below earth loop limit. The loading, diversity and distribution of
the sockets would be a factor especially as it is feeding the kitchen.

As above, a faulty ring energised with a lower value ocpd is still an energised circuit with known faults.
The fault was already energised before being discovered, the addition of a 20a OCPD would in my opinion be an acceptable temporary measure as long as the inspector can see that a plan is in place to rectify.
 
I have noted on the EIC that these need rectifying. And the client is a family friend who will listen to my advice. I was also going to use this job to show NICEIC inspector for domestic installer, as is the only one close enough that fits the criteria Would you advise that I do these remedials before the inspection, will he out right tell me to do one or accredit me once I prove the remedials are done? Thanks
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.
 
Yes, inspector will make you fix these issues and will lecture you, the installation has to be fit enough for the consumer board so fault trips meet regulation requirements. Also the regs have set in place that all lighting be earthed, I think it will be introduced in the 18th edition. Plus you have to notify building authority, so if anything does go wrong, your name is on the papers.

I believe the requirement for protective conductors in lighting circuits was introduced in 1966.
 
In your situation I would advise the customer that the installation has to be checked as the consumer board is different to the previous one. It has to meet a particular standard before it can be changed over, otherwise the board will not work as it should, then a new board just defeats the object even if it is metal.
 
I believe the requirement for protective conductors in lighting circuits was introduced in 1966.
Oh, I mean that if there was no CPC before it was advised that no metal fittings were fitted, but now they have to be earthed no matter what. Even if there is no earth point, all cables in and out should be earthed with connector. For R1 +R2 reasons cables in zones and walls be RCD protected.
 

Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
691
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top