No cpc on lighting and no neutral continuity on kitchen ring | Page 7 | on ElectriciansForums

Discuss No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 29, 2018
Messages
30
Reaction score
20
Location
Buckinghamshire
Hi All,
I recently replaced an old rewirable fuse board for metal split load rcd board. However on testing prior to replacement I noted that one of the lighting circuits doesn’t have a cpc. I’ve put this in the EIC for the new board that no cpc for lights, advised client that needs rewiring and advise against metal fittings accessories etc,is this the right course of action to take? They do already have metal fittings on this circuit, Is rcd protection enough to cover this? Also the kitchen ring has no continuity on the neutral conductor, I’ve had all the accessories off to find it but can’t, I’m assuming the break maybe in a buried joint box as the kitchen is an old extension. What’s the best course of action to take regarding this please?
Thanks
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
So poor Mrs Jones, who can't deal with BS 3036 fuses anymore will HAVE to have her lighting rewired before you would change a fuseboard ...........................

Bad practice IMHO

What do your scheme say?
The installation has to meet requirements so mcbs will operate in the times stated in regs, whoever is responsible for changing the board has the duty to test the circuits and they have to meet requirements. Otherwise RCD will not trip.
 
What do you base that statement on?
Regs, looking at old certs dated 2013 and then phoning up and asking the person issuing the certs that he passed an periodic inspection even though there is no earth to lighting. I always believed with my old company that you had to earth no matter what. Apparently you could get away without CPC to lighting before, as long as there are no metal switches or fittings. That's all changing now.
 
If there is no R1 + R2, it's pointless to have an RCD. Earth continuity, is a must. RCDs are for earth faults. You tell Mrs Jones that you replaced her board with an up to date version but will not have the benefits of a new version, but it's fire protected because it's metal. Might as well change the 3036 fuses to wylex switches in that case, it's more practical.
 
This is irrelevant to this thread - the OP's doing a CU change , not an EICR
Exactly, there can not be any C1 or C2, otherwise he cannot issue an EIC. All has to be earthed and all mcbs and RCDs need to meet the requirements of the regs. I will never issue a EIC knowing that's the earthing to the lighting is not in place and I will tell Mrs Jones, I cannot continue with the board unless she pays me to rectify the issues that will prevent me from issuing an EIC, because I am the one responsible by law, I am the one who signs off the work and I am the one who notifies building authority.
 

Reply to No cpc on lighting and no neutral continuity on kitchen ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
281
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
691
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top