Where's a lot of things murdoch?
That certificate is a disgrace.
No Certificate number
He's saying it's a new installation
No date to say what amendment he worked to
He's put he used old colours as a departure
No next inspection date
He says the main protective device is a 60898, now I can't tell clearly from the photos, but I doubt it.
He's also saying the main switch is a 60898, I can see that's not the case. He also says the 60898 main switch is a 30ma rcd
He used 10mm as the main earthing conductor, if he used 25mm tails then I would expect to see his calculations for this.
That was a quick look over, I'm sure there are other issue
And as Murdoch says, wheres the part p notification?