Just put a new cu in started testing .so here it goes start doing rfc line 0.33 nn 0.32 cpc 0.55
Ins all good now this a split load
Dis the cpc what i was working on and now showing earths in and are out so theor is no parallall paths has far that i can see the main earth is out but showing earths all water and gas have been disconnected
 
I'm with Sparkdog here
I wouldn't rely on a plug tester for anything.
Perhaps there is supplementary bonding somewhere, it used to be taken off the nearest cpc.
My guess supp bonding under the bathroom floor between earthed copper pipe and your RFC earth.
 
I still don't see what you are hoping to find or achieve here. It could be supplementary bonding, it could be metal dual boxes. It's a parallel path somewhere. If I was the customer I wouldn't like to be paying for all this unneeded work.
 
sorry if I repeat anything said/done.....but forget the plug in tester. Use your multimeter on all RFC's dead test end to end & also test for any cross over of RFC's r2 on cct1 to r2 cct2 (neutrals as well)etc and RFC r2 to the met with other ccts attached...anything ?
If you want to work live test at sockets removing neutral from cct ?
 
If I understand correctly, you have one specific RFC that has a connection to earth somewhere, despite the installation earth & bonding connections all being disconnected?

As others have mentioned, I'm not totally understanding why this is a problem? I'm assuming nothing is tripping, and you just want to know why, rather than needing to disconnect this other earth? Normally I'd just move on.

Assuming you really do need or want to know, then can you not just split the RFC into two, and find which half is still earthed. Then repeat with the earthed bit, until you narrow it down? Just like looking for any other fault on an RFC?

And when you say earthed, are you measuring a resistance to the suppliers' earth? If so, what value (from each end of the RFC)? Or did I recall seeing you are measuring Zs values on this RFC (with main earth and bonding disconnected)?
 
Usually it's me trying to find out why something does not compute - go Buzz go !
Perhaps confirm IR on that circuit and then isolate any backbox connections. With 23.6 Ohms it sounds like there's "an earthrod" attached :) .
 

Reply to Now i am pulling my hair out in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
748
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
975

Similar threads

  • Question
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Replies
6
Views
420
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
484

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top