N

Nicebloke

If running power to an outbuilding (usually a garage at the bottom of someones garden), I normally run it from the non RCD side of the C/U in the house and then put a 2 way RCD protected C/U in the garage. I was however, told that I can no longer do this as it must be connected to an RCD in the house C/U. I was also told that any outbuilding more than 20 metres away from a house must have it's own TT system?
 
If running power to an outbuilding (usually a garage at the bottom of someones garden), I normally run it from the non RCD side of the C/U in the house and then put a 2 way RCD protected C/U in the garage. I was however, told that I can no longer do this as it must be connected to an RCD in the house C/U. I was also told that any outbuilding more than 20 metres away from a house must have it's own TT system?
where did you hear this?
 
Surely yours is the best method, as long as the cable has physical protection (i.e. not triggering the cables in walls reg). Having RCD in series is difficult to discriminate and the longer the run the more impact it has. A lamp blows in building2 at night and trips a board in building1 a 100m away creating an unnecessary hazard, imho.
Edit : and the reverse, a problem in building1 takes out RCD covering building2
 
I am with Stroma. With regards an outbuilding requiring its own TT system if it's more than 20 metres from the house, I can't see where he got this from?
out of a chinese christmas cracker, i'd assume. what a load of bollox.
 
While there are arguments to support that thinking, it is only one way of doing it, there is guidance to download called Exporting PME. If I put an RCD at the house I personally would only use that for the cable protection supplying the garage and do a TT at the garage. I understand the DNO do not like exporting PME too far from the origin as it may defeat their PME. But the above is not set in stone, there are other approaches.
Exporting Pme - http://www.electriciansforums.co.uk/resources/exporting-pme.101/
 

Reply to Outbuilding on non RCD side of C/U? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top