RCD's wont TRIP! | Page 3 | on ElectriciansForums

Discuss RCD's wont TRIP! in the Australia area at ElectriciansForums.net

M

Marie-Claire

I changed a distribution board on a TT system to a new one but both RCD's won't trip when i have pressed test. Is it possible both RCD's are faulty? Everything is installed correctly
 
Im sure some ones mentioned this have you done a Ze , what you possibley have is no earth or a very high Ra reading ,if this is the case then the RCD's may not trip due to the high readings when you carry out the Ze the reading on a TT system should be less than 200 ohms , if you look at your RCD's as a set of scales the center being the Earth and the two arms being the L and N , how the RCD works is that it monitors the balance between the earth and live and neutral and any fault situation to earth , the balance is offset then the RCD trips , now if there is no earth then this could be the reason the RCD's are not tripping so do a Ze at the supply see what readings you get and take it from there be nice to let us know what you find
 
Last edited by a moderator:
A silly question, but have you done any tests at all on these 2 RCDs with an RCD test kit/multi function tester?? I ask because you have made no mention of undertaking any testing apart from measuring the voltage
 
Not such a silly question, Engineer54.

It went very quiet here the minute you mentioned proper testing!!!

Does it not strike anyone else as strange that she's checking the installation is energised with the 'kettle test' - didn't see that in GN3, and she's putting a fault on the RFC to test the RCD!!

So what happened to 'Supply Polarity', Ze, Zs and RCD tests..........and she didn't know what a ramp test was??

Competent to swap a CU - me thinks not!

This work is notifiable, by the way, Marie-Claire
 
Makes you wonder if theres owt in em? I have heard of cheapie "breakers" being sold with nowt but a link wire inside.........


Serious millwall, i think i saw an article on it a while back someware

Glenn I'm sure I saw it posted on here too and if my memory serves me correctly the person who mentioned it was a very well respected member.

May have been MCB's not RCD's though??? Anything is possible though :(
 
It always amuses me when a female electrician asks a question there is a very quick respones and I suspect 99.9999% of those are males.:29:


Yes - and they're awfully quick with their advice, with very little criticism........if this had been a bloke asking, he'd have been questioned to death on his quals/competence to do this work! ha ha

What you have to bare in mind, lads, is that this is the internet..........so it could be a bloke, anyway!! ha ha
 

Reply to RCD's wont TRIP! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
199
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

M
  • Question
I believe you're in Australia? Could you clarify the distribution arrangements - is this RCD for one particular circuit, or is it protecting a...
Replies
1
Views
329
It was >999 on all, tested cables connected and individually, he ce the reason i came on here to ask for ideas
2
Replies
19
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top