RCD's wont TRIP! | Page 5 | on ElectriciansForums

Discuss RCD's wont TRIP! in the Australia area at ElectriciansForums.net

M

Marie-Claire

I changed a distribution board on a TT system to a new one but both RCD's won't trip when i have pressed test. Is it possible both RCD's are faulty? Everything is installed correctly
 
the rcd's were not tripping, they were not going to trip out on the X.5 or the x1 as it was totally obvious they were not tripping under any circumstance. it was a dodgy batch for sure. putting the new ones in that tested immediately told me they were faulty
 
So you pressed the test buttons on the 2 new RCDs and it's a good-un!!

So absolutely no need to conduct the stipulated RCD tests at X.5, X1, and X5 then right?? Maybe none of the others tests either, as you have never mentioned any kind of tests, apart from voltage, and the Kettle test!!!

the rcd's were not tripping, they were not going to trip out on the X.5 or the x1 as it was totally obvious they were not tripping under any circumstance. it was a dodgy batch for sure. putting the new ones in that tested immediately told me they were faulty​
 
2 faulty RCDs in 1 board would make me suspicious of the MCBs as well. while you can test the RCDs with your MFT, there is no way you can test the MCBs for disconnection within the specified time, so i'd not be happy with that board at all.
 
2 faulty RCDs in 1 board would make me suspicious of the MCBs as well. while you can test the RCDs with your MFT, there is no way you can test the MCBs for disconnection within the specified time, so i'd not be happy with that board at all.

Fair comment, i will install a whole new board i think, i was concentrating on the problem being the rcd's, it never crossed my mind that the mcb's may be faulty too. thanks
 
If she tried the test button first as many electricians may very well do

If it didn't function,then whether the x1 and x5 tests were carried out or not would make no difference to the conclusion that they were faulty,the operation of the test button is also recomended test

Maybe she had made that decision and further meter tests were not required for that decision to be final
 
If she tried the test button first as many electricians may very well do

If it didn't function,then whether the x1 and x5 tests were carried out or not would make no difference to the conclusion that they were faulty,the operation of the test button is also recomended test

Maybe she had made that decision and further meter tests were not required for that decision to be final

totally babe :)
 
If she tried the test button first as many electricians may very well do

If it didn't function,then whether the x1 and x5 tests were carried out or not would make no difference to the conclusion that they were faulty,the operation of the test button is also recomended test

Maybe she had made that decision and further meter tests were not required for that decision to be final
Looking at her pic.....errrrr....i mean reading her diagnosis of the fault,,,,,,,,,,,and being thoroughly professional of course, i need to get there and check it out myself asap lol
 
the rcd's were not tripping, they were not going to trip out on the X.5 or the x1 as it was totally obvious they were not tripping under any circumstance. it was a dodgy batch for sure. putting the new ones in that tested immediately told me they were faulty​



RCDs come with many faults and symptoms of faults. A very common fault, is that an RCD device can perform well and pass all such RCD testing, but will not trip on pushing the test button on the device itself!! So not so totally obvious at all!!!

Another very common fault, is RCD devices will trip by pressing the test button, but won't trip under testing, or that the trip times a well outside acceptable limits!! ...That's why we ''Test''​
 
Warning, smug mode ON!



It always amuses me when a female electrician asks a question there is a very quick respones and I suspect 99.9999% of those are males.:29:


my one and only post..

Have you got a spare RCD of your own you could temporarily swap and try? If you don't know the background of the equipment it could be counterfeit.

and Tony..

This really is looking like counterfeit equipment. Two failed “brand new” RCD’s doesn’t bode well for the reliability of the gear in the rest of the board.
As someone said you leave yourself wide open if something goes wrong further down the road.


problem turned out to be..

Hi guys, thanks for all your advice. The RCD's were faulty, both of them!! I put some new ones on the board, pressed test and they tripped out instantly (thank god). I would of thought it strange that perhaps one could be faulty but two? whats the odd's? I am so glad it's sorted now and i have all the circuits connected. This forum is fab!! :)


I THANK YOU VERY MUCH

:rockon:



Smug mode off..

 

Reply to RCD's wont TRIP! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
199
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

M
  • Question
I believe you're in Australia? Could you clarify the distribution arrangements - is this RCD for one particular circuit, or is it protecting a...
Replies
1
Views
329
It was >999 on all, tested cables connected and individually, he ce the reason i came on here to ask for ideas
2
Replies
19
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top