Q). 2394 : ( T ) could you get this on Exams.
Documentationfor every electrical-installation . should include that required by . Regulation . ??

p.20. 132.13 .
Everyelectrical-installation . shall be provided with appropriate- documentation .including that required by . Regulation - 514.9. Part - 6 . & where applicable Part - 7 .

 
Q). 2394 : ( T ) could you get this on Exams.
Documentationfor every electrical-installation . should include that required by . Regulation . ?? Sorry .All the Above - 132.13 .
 
2394: Q ) . When automatic-disconnection of supply . is used as a measure of protection. additional-protection by RCD . shall be provided for . ??
Socket-outlets. with a rated-current not exceeding . 20A. that are for the use by . Ordinary-persons & are intended for .general-use. - 411.3.3.
 
2394: Q ) . All circuits in a location .containing a bath or shower shall have . ??
Additional-protectionby . a 30mA - RCD - 701.411.3.3.

Q) . in Exams . this is to warm you up. -&-s
Maximum-disconnection-time. for a lighting-circuit in acommercial-premises . protected by a . TT- system . A) . 0.2s - table - 41.1

Q) . The maximum - ( Zs ) to ensure .30mA RCD operation is . A) . Table - 41.5. 30mA - 1667Ω

Q) . BS-EN-60898 - circuit-breaker can . be used for . Table - 53.2.
Isolation.
Emergency-switching.
Functional-switching.
All of the above

2394: As BS-7671:2011: makes a song & dance about it . “ Line-conductor “ please referto definition
Q) . A Line-conductor includes ?? .
Aconductor of an . a.c. system for the transmission of electrical-energy other than a .neutral . protective-conductors & PEN-conductor . definition

 
Thiswas Posted to me . two-days ago . some reading required .

411.4.5. - Where an RCD is used for . Fault-protectionin a circuit TN-system . the condition ( Zs/ Ia ≤ Uo ) has to be met . just as it does when an. overcurrent-protective-device is used to provide . Fault-Protection . to meetthis condition where an RCD . is used . the earth-fault-loop-impedance ( Zs )in the circuit must not exceed the nominal-voltage of the supply ( Uo ) divided by the current ( Ia )causing-automatic-operation of the RCD within thespecified-maximum-disconnection-time .
Time not exceeding ( 0.4s ) has to beachieved using an RCD to BS-EN-61008-1 & BS-EN-61009-1 . of Non-delay-type. with a rated-operating-current ( IΔn) of 100mA

( a ) in a . circuit of nominal-voltage - 230V . it can be seen from table - 3A . in appendix -3 . BS7671:2011:
That a current of . 100mA is required to cause the RCD to operatewithin - 0.4s . Operation will actually-occur within . 300mS at 100mA .
Accordingly. the maximum-earth-fault-loop-impedance ( Zs ) thatcan be tolerated in the circuit is . 2300Ω - ( 230V ÷ 0.1A = 2300Ω ) …. 100mA ÷ 1000 = 0.1A

RCDs- IΔn - mA

Maximum-valuesof earth-loop-impedance ( Zs - Ω ) for RCDs for fault-protection - TN- systems . operating on 230V .
Earth-loop-impedance ( Zs - Ω ) Circuit-loop-impedance .

Note- ( G - RCDs ) (a)
BS-EN-61008-1:
BS-EN-61009-1: ( 0.4s )
30mA- 7667Ω
100mA - 2300Ω
300mA- 767Ω
500mA- 460Ω

a) . Measured-values of ( Zs) should be lower than those in the above table . as the earth-loop-path in a TN- system is entirelymetallic . The ( Zs - value ) in this table apply to TN- system only .

b) . RCD - time-delay ( S ) Maximum-permitted( Zs ) depends on the rated [ declared-time-delay ] of the RCD .
Todetermine . Maximum - ( Zs ) consultRCD-time-current-characteristics . & obtain ( Ia ) the current inamperes-causing-operation . within the required-disconnection-time-delay ( Zs ) must not exceed ( Uo / Ia )

RCD- time-delayed ( S )
100mA- (b) 0.4s . 1150 Ω .
300mA- (b) 0.4s . 383 Ω .
500mA- (b) 0.4s . 230 Ω .

RCD- time-delayed ( S )
100mA- (b) 5s. 2300Ω .
300mA- (b) 5s. 767Ω .
500mA- (b) 5s. 460Ω .

Forconvenience . it has been listed . the maximum-earth-fault-loop-impedance values( Zs ) for RCDs used for .fault-protection in TN-systems . it is important that the ( Zs) values achieved in the installationshould be much lower . than those given in the table . as the . earth-fault-loop-path. in a TN-system . it should also be noted thatthe . maximum-values of ( Zs ) in theabove relate only to a nominal-voltage of 230V .& should be multiplied by a factor-equal to . Uo / 230V . if othernominal-voltages are to be used .

RCD. is employed for . fault-protection . consideration must also be given to protection against Overcurrent .






 
Backto the past . BS-7671:2001 / 2004 . O.S.G.

1.1.Scope .
Thisguide is for electricians ( Skilled-persons) it covers the following-installations. (in these days you could ask the boss for a pay-rise )

1.1.Scope . 2011 :
Thisguide is for . installers ( forsimplicity , the term installer has been used for electricians& electrical-installers) it covers the following-installations.



 
Usefuljunk

- Ampere or Amps - represents the amount of current in a circuit .
- Voltage- is defined scientifically as . the circuit-potential-difference . & can be seen as the amount of “ Pressure“ that drives electricity in a circuit .
- One-Watt- is equal to one volt . multiplied by one-amp .

Garden-hose.
Thewater-pressure in the hose . is like-voltage
Ampis like the . volume of water-flowing through the hose .
Wattagethen . is the total amount of water that comes out the hose . per unit of time .

Term- that helps tie . together the other three . is the ( Ohm ) which is a unit of ( Electrical-résistance ) going back to the garden-hose . has alarger-diameter . more water will be able to flow through .
- Circuitwith a high-résistance-value . expressed in ( Ωs ) isable to carry fewer-amps . than with lower-résistance . regardless of the voltage.
-High-voltage-encounters-high-résistance . the amount of possible-amps in thecircuit . will be very-low . not muchwater will get through a narrow-hose . no matter how high the pressure is .
 
TT- Installations . “Protective-devices “

Disconnection-timeof ( 0.2s ) for TT- installation has beenintroduced in the . 17[SUP]th[/SUP] Edition . This makes the use of an . RCD or. Circuit-breaker with a . residual-element . virtually-essential .


RCDs- again
TT- installation . the earth-fault-loop-impedance is not usually-sufficiently lowto facilitate the operation of an (Overcurrent-protective-device ) within the required-disconnection-time .BS-7671:2011: as the disconnection-timefor . TT - systems is 0.2s .

TT - systems compared with the ( 0.4s ) required in the Previous-Edition . “how thing have Changed “

TT- installations require attention becausethey normally have a higher-impedance to earth via-an electrode buried in theground . high-earth-fault-impedancewould reduce an . earth-fault-current & slow down the tripping of acircuit-breaker . 2395 : “ RCDs “

Some-Facts: TN- systems have avery-low-earth-impedance . which in most-cases . circuit-breakers would meetrequirements should an earth-fault-occur .
BS-EN-60898 & BS-EN-61099-1- circuit-breakers . designed to trip - 0.1s . reason ( Instantaneously) . requirements for . fault of Low-impedance . between Live-conductors
TT- systems . which have ahigher earth-impedance . they do notreliably meet the requirements for disconnection-time . Backto RCDs again . so . 0.04s / 0.2s

2394: don’t get mixed up on TN- . TT- . Systems . 0.4s - 0.04s / 0.2s - 0.04s . ( If )
TN- low-earth-impedance . ( Zs ) circuit-loop-impedance .
TT- systems . which have ahigher earth-impedance . ( Zs ) circuit-loop-impedance .
 
2394: Where an RCD is used . we have two-methods .
Addition-protection )
Fault-protection )

Wherean RCD is used for ( Fault-protection ) product of the rated-residual-current andthe sum of the resistances of theinstallation - Earth-Electrode . & Protective-conductor (s) connecting it to . exposed-conductive-parts ( R [SUP]A [/SUP]) is required to benot . greater than . 50V - regulation - 411.5.3.

(R [SUP]A [/SUP]) It isrecommended that an . Earth-Electrode-résistance. where possible not-exceed - 200Ω -411.5.3. Note -2

2394: TT - system . do comeinto the Equation . in Exams . ( R [SUP]A [/SUP]) I got this on Exams . 411.5.3. so that there’s no confusion .
P.38 . The sum of the résistance of the . earth-electrode& the protective-conductor .connecting . Etc

Fault-protection: ( ADS ) - TT - system .
TT- system there is no . direct-connection between the installation . MET &the earthed-supply-source - earthed-neutral or star-point . other than throughthe general-mass of the Earth . therefore . particular requirements are necessary- Regulation - 411.5.1.

 
2394:
Dear Customer . RCD / RCBO . Have you tested by . Operation of thepushbutton at . frequent-intervals . Then I can stop using (Grecian-2000 )

Iwas taught to do the ( x5 - test ) first . &if the device didn’t trip . take that as evidence that the ( User )probably wasn’t exercising the device .at the recommended-periods . in thelast six-months I’ve use this method . it can free sticky RCDs . not always , Howdo you get through to your customer . “ RCD is important “
“Seize up “ Lubricant used on the .Latching-mechanism - would emulsify overa period of Time . Yeah . as we wouldsay . “ Push theButton

N****. training-DVD - Inspection & Testing . does say that . Initial-pushbutton testto ( Pre-lubricate the mechanism ) No am not working for the other side .

 
2394 : Known yourregulations .

Earth fault loop impedance (Z[SUB]s[/SUB]) ……. inour case - Circuit-loop-impedance

Regulation612.9 requiresthat, where protective measures are used which require a knowledge of the earthfault loop impedance (Z[SUB]s[/SUB]), the relevantimpedances are to be measured, or determined by an alternative method.
 
Useful junk BS-951

Installing a clamp in an inaccessible position

Likeall types of electrical connection that are not excused by Regulation - 526.3of BS 7671, the electrical connections between a BS 951 clamp, the pipe (or other tube) to which it isattached, and the protective conductor connected to its terminal must beaccessible for inspection, testing and maintenance (Regulation 543.3.3 refers).
Failing to fit a warning label

It is adeparture from Regulation 514.13.1 of BS 7671 to fail toinstall a suitable ‘SAFETY ELECTRICAL CONNECTION - DO NOT REMOVE’ label in avisible position at the connection of an earthing-conductor to an earthelectrode or of a bonding conductor to an extraneous-conductive-part. Such alabel is normally supplied with each BS 951 clamp. Misuse of BS-951 clamps Casesof misuse of BS 951 clamps are occasionally found Fitting a BS-951 clamp to the armour or metallic sheath of a cable BS-951 states that clamps to this standard are notintended for connection to the armour or sheath of a cable and requires thepackaging of the clamp to include the warning “ Notintended for use on the sheath or armour of a cable ”. This is becausethe action of tightening the clamp is liable to damage the cable, for exampleby crushing the bedding or insulation or by causing the metal in a lead sheathto cold-flow. Such damage may result in high resistance and unreliability in theelectrical connection between the clamp and the armouring or metallic sheath,and may even result in an electrical fault within the cable, with thepossibility of serious injury to persons. Fitting a BS951 clamp to the armour or metallic sheath of a cable is thereforeunacceptable. Fitting a BS 951 clamp whichis unsuitable for the pipe diameter and/or cable size.

A BS 951 clamp must be correctly selected for both thesize of pipe or tube to which it is to be fitted and the size of cable. Fittinga clamp which is unsuitable in either of these respects is liable to be adeparture from the requirements of Regulations 526.1 and/or 526.2 of BS 7671 relating to durable electrical continuity,adequate mechanical strength, and appropriate selection of a means ofconnection.
 
2394: As the RCBO . is here to stray . Somefacts . ( i )
Conventional-tripping-current. RCBO-61009-1.

Anovercurrent-protected-pole . is defined by BS-EN-61009-1 . as a pole provided with an overcurrent-release .

Rated-current ( In ) is the maximum-current which an RCBO . isdesigned to carry for long-periods . ata specified-reference air temperature . normallyof 30°C
Theterm ( Rated-current ) generallymeans the same as ( Current-setting ) asused in BS-7671 . in relation to protection against . Overcurrent .

Thepreferred-values of rated-current givenin BS-EN-61009-1 . 6A - In . up to 125A- In . BS -

Rated-residual-operating-current- ( IΔn ) of an RCBO . is the value of . residual-current . assigned to the RCBO by themanufacture . at which an RCBO-operatesunder specified-conditions .

The. Standard-value . of ( rated-residual-operating-current ) BS-EN-61009-1- 0.01A . 0.03A .0.1A . 0.3A . 0.5A .
Re-cap.
10mA ÷ 1000 = 0.01A . . Etc .
500mA ÷ 1000 = 0.5A .

Wherethe function of an . RCBO as a RCD . rather than as anOvercurrent-device . is used for . fault-protection as part of the . protective-measure . ( ADS ) fault-protection depends upon the .RCBOs - sensitivity . as a residual-current-device .

The - Lower the rated- residual-operating-current . the Greater the sensitivity . should the fault be of .non-negligible-impedance . There’s a However .
Ifan RCBO is selected with to . low arated-residual-operating-current . this may result in . unwanted-tripping .

 
2394: As the RCBO . is here to stray . Somefacts . ( ii )

Conventional-tripping-current. RCBO-61009-1.

The conventional-tripping-current . of acircuit-breaker . is the characteristic relating to . protection of the circuitagainst overload . it is a . specified-value of the circuit-current . which causes the device to trip within a specified-time - known as the conventional-time . at the specified-reference-temperature .
Conventional-tripping-current. is usually expressed as a . multiple of the rated - ( nominal ) current - ( In) of the circuit-breaker .

RCBO- residual-current-breakers . conforming to BS-EN-61009-1 . all have a conventional-tripping-current of. ( 1.45 - In ) the related- conventional-time . is
(1 - Hour ) for circuit-breaker(s) of rated-currents ( In ) up to and including ( 63A )
(2 - Hours ) for circuit-breaker(s) of rated-currents . Greater than( 63A )

Symbolgenerally used for . conventional-tripping-current ( I[SUP]2 [/SUP] ) rather than ( I[SUP] t [/SUP] ) as is used in . circuit-breaker standard such as RCBO-61009-1.
This is because . conventional-tripping-current. means the same as the . term .current-causing-effective-operation ofthe . Overload-protective-device . used in - BS-7671 - in which the symbol ( I[SUP]2[/SUP] ) is used .

 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
929
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
355
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top