Functional-Testing- 612.13.1.
Whichstates that for an RCD ( Theeffectiveness of any test-facility incorporated in the device shall be Verified)
Re-cap :Built-in-test-button . RCDs
test-button- can be used to place a load between the output - Line-conductor and theinput-neutral-conductor . creating animbalance in the windings . this imbalance causes the RCD to trip .
point to note : thetest-button only demonstrates that the trip-mechanism-works . confirming-nothing-else .about it’s specific-operational- characteristics .
Re-cap -2394: with 2008: & 2011:
17[SUP]th[/SUP]Edition increases the need for circuit(s) to be provided with RCD-protection -The circuit(s) that require RCD are as follows .
i) . Where the - Earth-fault-loop-impedance . isto high to provide the required-disconnection-times . where thedistributor - ( DNO ) or does notprovide an Earth - TT - system(s) 411.5.
ii) . Socket-outlet - circuit(s) in domestic andsimilar-installation(s) - 411.3.3.
iii) . For circuit(s) of locations-containing-a bathor shower - 701.411.3.3.
iv) . For circuit(s) supplying mobile-equipment .not exceeding - 32A for use outdoors - 411.3.3.
v) . For cables without earthed-metallic-coveringinstalled in walls or partitions at a depth of less than 50mm and not protectedby earthed-steel-conduit or similar - 522.6.7.
vi) . Forcables without earthed-metallic-covering installed in walls or partitions withmetal-parts - excluding screws or nails . and not protected byearthed-steel-conduct or the like - 522.6.8.
for items( ii and vi ) above the RCDs used shouldbe rated at 30mA .
(Additional-Protection Only ) 5 x 30 =150mA
RCDs are rated at . 30mA and 40mS . andmust disconnect the supply within ( 40mS ) for a leakage-current of ( 5 x times) the rated-operating-current - 150mA . refer to BS-7671:2008:2011: - 415.1.1.
Useful- junk ( 5x and x5 ) are the same thing . RCDs
Re-cap . What the Regulations arereminding us . p.29 / p.36 .
□ Inspection :-Examination of an electrical-installation using all the ( Senses as appropriate )
□ Testing :- Implementation of ( measures to assess ) an electrical-installation by means of which its . ( effectiveness is proved ) this includesascertaining-values by means of ( appropriate-measuring-instrument(s) ◄ it has been -Defined . Part - 4 . 2 . 3 . 5 . 6 . refer to . GN-3 .
□ Verification :- All ( measures by means ) ofwhich compliance of the electrical-installation with the relevant-requirementsof - BS-7671 : are checked . comprising . Inspection . Testing and Certification .
BS-7671:2011: BS-EN-61557 : P.288 .
BS-EN-61557: Electrical-safety in low voltage distribution systems up to 1000V a.c and 1500V d.c. - Equipment for testing . measuring ormonitoring of protective-measures . ( General-requirements ) 612.1. - 621.3.
P.190 - BS-7671:2011: 612.1.
Testing :
The tests of . Regulations - 612.2. to 13 . where relevant . shall becarried out and the results compared with relevant-criteria .
P.194 - 621.3.
Periodic-inspectionand Testing :
Precautionsshall be taken to ( Ensure ) that the periodic-inspection and testing shall not cause ( Danger ) to persons or livestock . and shall not cause damage to property and equipment even if the circuit is defective . Measuring-instrumentsand monitoring-equipment and methods shall be chosen in accordance withrelevant-parts of ( BS-EN-61557 ) ifother measuring-equipmentis used . it shall provide no less degree ofperformance and safety .
BS-EN-61557-2 :Insulation-résistance .
p.288 . BS-EN-61557-6 : 1998 .Residual-current-devices - ( RCD ) in TT . TN - 612.8.1 . a) 2)
p.193 : General .
The - Verification . ofthe effectiveness of the measures for . fault-protection byautomatic-disconnection of supply is effected as follows . a) 2)
a) TN - system . Compliance with .Regulation - 411.4. shall be verified by . (2)
verification of the -characteristics and / or effectiveness of the associated-protective-device .This verification shall be made :
- for -Overcurrent-protective-devices . by ( Visual-inspection ) i.e. short-time or instantaneous-trippingsettings for circuit-breakers . current-rated and type for fuses .
- for - RCDs . by ( Visual-inspection & Test ◄ ) The effectiveness of disconnection ofsupply by RCDs . shall be verified using ( Suitable-test-equipment according to BS-EN-61557-6 . ( Part - 6 ) Regulation - 612.1. to confirm that therelevant-requirements in . Chapter - 41 are met .
Testing :
The tests of . Regulations - 612.1. where relevant . shall be carried outand the results compared with relevant-criteria .
The disconnection-timesrequired by . Chapter - 41 shall be verified . → Chapter - 41 . Protection againstelectric-shock .
Safety -LVD .
BS-EN-61557: Electrical-safety in low voltage distribution systems up to 1000V a.c and 1500V d.c. - Equipment for testing . measuring ormonitoring of protective-measures . ( General-requirements )
Part - 1 :General-requirements .
Part - 2 : Insulation-résistance-testers .
Part - 3 : Loop-résistance .
Part - 4 : Low-résistance-ohmmeters .
Part - 6 : Residual-current-devices - RCDs . in TT and TN- system(s)
Part - 7Phase-sequence .
Other reference standards for testing - RCDs .
RCD -Standards : BS-EN-61008-1 . BS-EN-61009-1
BS-EN-61008-1 : ( Part - 1 )
Residual-current-operated-circuit-breaker - ( Without ) integral-overcurrent-protection . for household andsimilar uses. ( General-rules )
BS-EN-61009-1 : ( Part - 1 )
Residual-current-operated-circuit-breaker - ( With ) integral-overcurrent-protection . for household andsimilar uses. ( General-rules )
Current-multiplier ( x ) x 1 / 100%.
Current-multiplier ( x ) x 5 / 500%.
Megger -1552 . Do we get lazy withMultifunctional instrument(s) .
Two-settings.
Automatic: - Nulling-out . “ Leads “
Manual : By calculation . Subtracting . “ Leads “
RCD - ( G ) ~ 30mA . ( BS-EN ) ◄
For thesake off . -&-s . Select the -RCD-function using thefunction-selector-switch . Am using theword - Manual - Setting(s) : back to basics
( 1/2 . 0.5 ) Half of 30mA / 15mA .
- Start ofTest : with ( IΔn ) 0° .step 1 . RCD should not Trip .
- Start ofTest : with ( IΔn ) 180° .step 2 . RCD should not Trip .
(500% . x5 )
- Start ofTest : with ( 5 x IΔn ) 0° .step 3 . RCD should Trip-out . ( Example - 0° / 7.7mS … 180° / 11.1mS ) Manual .
Re-activateRCD . - Start of Test : with ( 5 x IΔn ) 180° .step 4 . RCD should Trip-out .
(100% . x1 )
- Start ofTest : with ( 1 x IΔn ) 0° .step 5 . RCD should Trip-out . ( Example - 0° / 46.0mS … 180° / 35.7mS ) Manual .
Re-activateRCD . - Start of Test : with ( 1 x IΔn ) 180° .step 6 . RCD should Trip-out .
Highest → of the two-readingsshould be recorded - Certificate
Re-cap. Table- 3A / p.295 . BS-EN-61008-1 : & BS-EN-61009-1 :
Delay ( S ) Trip-time (mS ) Minimum & Maximum . tΔ .. 130mS < tΔ < 500mS .
Table -41.5 gives maximum-values of ( Zs ) for non-time-delayed - RCDs .
Value ofthe two-current-tests ??? ( Example - 0° ~ / 46.0mS … 180° ~ / 35.7mS )
Re-cap :2394 . ( Additional-protection - 30mA only ) 5x .
2394: Guessworkdoes not pay .
Point to Note : it appears thatmany candidates believe the . Minimum-acceptable-value forinsulation-résistance is ( 2MΩ and not1MΩ ) stated in BS-7671:2008:2011:
Re-cap. Table - 61 . MINIMUM-value of insulation-résistance . Wording is MINIMUM . ( 1MΩ ) BS-7671:2008:2011:
Note - 2: Insulation-résistance-value(s) are usually-higher than those of Table-61 . ◄◄◄◄◄
Point toNote : - Exams 2394 : There is no excuse for studying for any exams. Q/As are taken from . BS-7671:2008:2011: - GN-3 .
Point to Note : “ a Must “ GN-3 . P.58 . :mad2:
Operationof residual-current-devices . ← ← ← ← ← ← .
411.4.5. - For each of the tests . readings should betaken on ( Both-positive and negative-half-cycles ) ↔ ( 0° & 180° ) andthe longer-operating-time-recorded .
Technical-Knowledge; Examiners - 2012 .
Many-candidateswere unable to correctly -indentify the requirements for the application ofRCDs . the Maximum-test-currents appliedand the Maximum-operating-times . many candidates failed to score as well asthey may as they failed to indentify the test-currents . in mA . to be appliedat each step of the test . failed to indentify the correct-operating-times ateach step and not indentifying that the ( Highest of the values at 0° and 180° ) should be recorded . Many candidatesfailed to confirm the operation of the ( Test-button ) on completion of the electrical-tests. Somecandidates stated incorrectly that an RCD to - BS-EN-61008-1 should disconnectin ( 200mS ) whentested at 5 x IΔn .
Regulationshave to state the facts : p.167
Facts : Minimum-cross-sectional-area of the . main-protective-bonding-conductor .in relation to the ( Neutral of the supply )
Electrical-installation-condition-reports. & “ Testing “
Gas &Water-installation-pipe(s) The size of main-protective-bonding-conductor is always selectedfor the appropriate tables in the regulations . 54.8.
( 10.0mm[SUP]2[/SUP] ) is fine for most installations of a C.S.A.of the supply-neutral-conductor ( table- 54.8. - 35mm[SUP]2[/SUP] or less 10.0mm[SUP]2[/SUP] )
The conductorsare connected in a appropriate-place forboth the Gas - Water-installation-pipe(s) using BS-951 - clamps . and also suitable indentifiedwith the correct-label . - Provision of earthing and bonding-labels at all appropriate-locations
Older-installation(s) where the installation has - supplementary-bonding they will also have to bechecked . - Provision of earthing and bonding-labels at allappropriate-locations
Verifying( Zs ) readings . ( Lighting-circuit )
Determine ( Zs ) adding ( Ze ) which you determined during the prospective-earth-fault-current-test. to your value of ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) looking attable - 41.3. Maximum - ( Zs is 6A - 7.67Ω ) for a 6A circuit-breaker to operate . your ( Zs ) is well below this . it is important to remember that theregulations do require a adjustment to the figure to allow for the increase ofrésistance of conductors of increase oftemperature when a circuit is under-load .
You canfind guidance on this - Appendix - 14 . p.424. 80% method . so the tabulated - (Zs ) needs to be reduced to 80% - per-cent of its value you can just do this multiplying . ( 7.67 x 0.8 = 6.14Ω )
Used as a Leaning-curve .
High-current-loop-testing :
For Supplies that are ( Not RCD - protected ) thehigh-current-test . can be used . as there is no-risk of tripping and RCD .
Megger - LTW-325 : Loop-impedance-tester .
Two-wires -loop-impedance-measurement
Line to earth - testing.
Line toneutral - testing .
Prospective-short-circuit-current-test. ( PSCC )
The ideaof this test is to measure the maximum-current that can flow betweenlive-conductor(s) in the event of a fault .
The reasonthat we have to know this to make sure that we select the right type ofprotective-device . where it is installed in the circuit .it needs to carry thehighest amount of current without damage . Megger - LTW-325 . Loop / No-trip . Loop / Max-Z
Firstly :we must have Safe-Isolation . locking - OFF . Padlock
Danger -400 Volts .
Warning -This is a Live-test .
Green-lead- onto the neutral .
Loop / Max - Z. Loop - high-current .
Testbetween the neutral which is a live-conductor - then test between the incoming- line-conductor . PFC - ( 2241A ) which is 2.24kA .
Need to dothe same test between all three-line-conductors . ( L1 . L2 . L3 )
Brown - L1 - 2241kA . 2.24kA .
Black- L2 - 2256kA . 2.25kA
Gray - L3 - 2257kA . 2.25kA
We can seethat the reads 2.25kA .
becausethis is a Three-phase supply . you need to double the valve I’ve got . 2.25 x2 is 4.5 . ( 4.5kA is what you write onyour test - certificate )
Megger - LTW-325 : Loop-impedance-tester .
External-earth-loop-impedance-test- ( Ze ) Earth-fault-loop-impedance-test-instrument .
Firstly :We must have Safe-Isolation . locking - OFF . Padlock
Danger -400 Volts .
Warning -This is a Live-test .
Disconnectedthe - Earthing-conductor . ( Which is aProtective-conductor )
Reason forthis . We do not want ( Parallel - paths ) we need to know the résistance between hereand the supply-transformer .
With leadsto GS-38 .
Green-lead with a crocodile-clip .
Red - lead. with plastic-cover with maximum cover . 2mm . ( Live-parts )
Loop /High-current .
Loop / Max - Z.
Connectthe Green-lead with a crocodile-clip . To the disconnected - Earthing-conductor .
With theRed-lead . with plastic-cover with maximum cover . 2mm . ( Live-parts )
Brown - L1 - incoming Line to earth . value of 0.17Ω. you’ll need to know the highest-value . you’ll testbetween all three-lines .
Black- L2 - 0.17Ω
Gray - L3 - 0.17Ω . thereall consistent . so your value is - 0.17Ω .
Ring-final-circuit-test.
Firstly :We must have Safe-Isolation . locking - OFF .
3 - thingsneeded . Lock-off that is appropriate forthe type off isolation . Padlock for locking-off . Sign - danger-do-not-switch-on.
Danger -400 Volts .
Warning -This is a Live-test .
Wheninsolating any-mains . ask permission . is it safe to do so .
Lock -off . placing the lock-off . padlock . cable-tie the Sign onto the padlock - danger-do-not-switch-on . You are the key-holder .
Is it Dead - With a approved-voltage-indicator
Test between. Earth to Line .
Testbetween . Earth and Neutral .
Testbetween . Neutral and Line .
With aknown device - proving-unit . With aapproved-voltage-indicator - all lightsare working .
Back to. With a approved-voltage-indicator . Test between . Earth and Line .
Ring-final-circuit-test- with all the cables disconnected .
Instrument-use. Low-résistance-ohm-meter . turn it on. and Null the leads . Re-cap . you leads have résistance 0.04Ω in them . which you do not want toinclude in your test . Zero the Leads .
Test each-conductor. End-to-end . ( Single-cables arethe same-size 2.5mm[SUP]2 [/SUP] ) not T&E .
Line-conductor(s) - 0.56Ω .
Neutral-conductor(s) - 0.55Ω
Circuit-protective-conductor(s) - 0.57Ω
Next :- Cross-connect the . Line and neutral-conductor - Connector-block .
Next :- Cross-connect the . Neutral and Line-conductor - Connector-block .
Dead /Testing . - your probes are 4mm . Not a Live-test . test between the two-ends off theconnector / blocks . ( Loop ) 0.27Ω you should be getting half the reading of one of these conductors . go toeach-socket-outlet . & test between each Line and Neutral at each socket .
You are .checking that it is a Ring. And no interconnections . from a socket-out-let - Line/ Neutral - 0.31Ω . ( Plus - Polarity) by continuity - method
You havecheck the . Line and Neutral at each-socket=outlet .
You doingthe same test . between the Line and Earth . & at each-socket-outlet .
Next :- Cross-connect the . Line(s) and Earth(s) - Connector-block . 0.27Ω . all you socket-outlets have beentested . your at the last-one - reading between .05Ω & the originalreading of 0.27Ω . - your reading is 0.29Ω
Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
thanks for the confirmation this is what i thought.
i cant think of what use this device is .
i have seen David Saverys Arc Fault Detection Device...
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...