Some of the Basic’s .we take for Granted . So what’s my point here . !!!!!! :banghead:
When asked to explainhow a ( PFC -test ) result may be used to determine if a circuit--breaker was suitable
Wrong .)- many candidates incorrectly referredto disconnection times of 0.4s or 5s.
Many descriptions did not make it clear thatthe circuit breaker's maximum breaking capacity must be at least equal to the ( PFC – test-result )
Prospectiveshort circuit current ... ( PSCC ) :30:
Is the highest electric-current which can existin a particular electrical system under short-circuit-conditions . It isdetermined by the voltage & impedanceof the supply-system.
When designing an electrical installation circuit-breakers must bechosen so that they can safely break the current of a short circuit .
Isolation: Circuit-breakers conforming toBS-EN-60898 are suitable for Isolation .
16[SUP]th[/SUP]Edition , Miniature-circuit-breakers (MCBs ) manufactured to earlier-standards ( such as BS-3871 ) are unlikely to besuitable .
Note :There is no ( Type A instantaneous-tripping-characteristic ) to avoid confusion with the ( A abbreviation for amperes )
Overcurrent-protective-device ( OCPD )
Rated-short-circuit-capacity ( Icn) of the circuit-breaker .
GN-3. P/56 .
Thedifference between the two-short-circuit-ratings described is the condition ofthe ( Circuit-breaker ) after manufactures-testing .
Two-short-circuit-capacity-ratingsare ( Defined ) in BS-EN-60898 & BS-EN-61009-1
( Icn ) of the circuit-breaker .
( Icn ) The rated-short-circuit-capacity, ( marked on the device ) The ( Icn) → [ 6000 ] & for the majority of applications the ( PFCurrent ) atthe terminals of the circuit-breaker shouldnot exceed value
( Icn ) The service-short-circuit-capacity
( Icn ) is the maximum-fault-current the device caninterrupt safely , although it may no longer be usable .
Note: GN-3 . P/56 . FOR-DOMSTIC-INSTALLATIONS . 2392 / 2394 .
The ( PFCurrent ) isunlikely to exceed ( 6kA ) up to which-value ( Icn) willequal ( Ics)
RCD's work by means of the , current balance principle
RCDs :- Residual - dual / Line & Neutral-conductor(s) Two in Balance
Operation of RCD
411.4.5. ◄◄◄ ( Very-important RCDs ) Question why do we loss-points in Exams.
for each of the ( Tests ) readingsshould be taken on ( Both positive & negative half-cycles ) and the longer operating-time recorded . ( mS) ( half-cycles 0° & 180° ) ◄
When asked to explainhow a ( PFC -test ) result may be used to determine if a circuit--breaker was suitable
Wrong .)- many candidates incorrectly referredto disconnection times of 0.4s or 5s.
Many descriptions did not make it clear thatthe circuit breaker's maximum breaking capacity must be at least equal to the ( PFC – test-result )
Prospectiveshort circuit current ... ( PSCC ) :30:
Is the highest electric-current which can existin a particular electrical system under short-circuit-conditions . It isdetermined by the voltage & impedanceof the supply-system.
When designing an electrical installation circuit-breakers must bechosen so that they can safely break the current of a short circuit .
Isolation: Circuit-breakers conforming toBS-EN-60898 are suitable for Isolation .
16[SUP]th[/SUP]Edition , Miniature-circuit-breakers (MCBs ) manufactured to earlier-standards ( such as BS-3871 ) are unlikely to besuitable .
Note :There is no ( Type A instantaneous-tripping-characteristic ) to avoid confusion with the ( A abbreviation for amperes )
Overcurrent-protective-device ( OCPD )
Rated-short-circuit-capacity ( Icn) of the circuit-breaker .
GN-3. P/56 .
Thedifference between the two-short-circuit-ratings described is the condition ofthe ( Circuit-breaker ) after manufactures-testing .
Two-short-circuit-capacity-ratingsare ( Defined ) in BS-EN-60898 & BS-EN-61009-1
( Icn ) of the circuit-breaker .
( Icn ) The rated-short-circuit-capacity, ( marked on the device ) The ( Icn) → [ 6000 ] & for the majority of applications the ( PFCurrent ) atthe terminals of the circuit-breaker shouldnot exceed value
( Icn ) The service-short-circuit-capacity
( Icn ) is the maximum-fault-current the device caninterrupt safely , although it may no longer be usable .
Note: GN-3 . P/56 . FOR-DOMSTIC-INSTALLATIONS . 2392 / 2394 .
The ( PFCurrent ) isunlikely to exceed ( 6kA ) up to which-value ( Icn) willequal ( Ics)
RCD's work by means of the , current balance principle
RCDs :- Residual - dual / Line & Neutral-conductor(s) Two in Balance
Operation of RCD
411.4.5. ◄◄◄ ( Very-important RCDs ) Question why do we loss-points in Exams.
for each of the ( Tests ) readingsshould be taken on ( Both positive & negative half-cycles ) and the longer operating-time recorded . ( mS) ( half-cycles 0° & 180° ) ◄