Useful-junk .
P/29 , Leakage-current : Electric-current in anunwanted-conductive-path , under normal-operating-conditions .
Touchcurrent :- also known, as earth-leakage-current must be withinspecified limits for its Class. :aureola:
Class I equipment, the earth-leakage-current is thecurrent that flows in the earth supply conductor during normal operation of theequipment.
Class II equipment, leakage is measured to earth fromaccessible conductive-parts of the enclosure

 
2008: GN-3 ,States : if test an installation as a whole
Insulation-résistance to earth.
" Although aninsulation-résistance-value of not lessthan 1.0 MΩ complies with the Regulations, where an insulation resistance ofless than 2MΩ is recorded the possibility of a latent defect exists. ( In these circumstances, each circuit should be tested separately ) "

2392-10
" Although an insulation-résistance-value of not less than (1MΩ complies with the Regulations ), New-installations should not yield test results this low "

( 299MΩ ) . reason(s) , New-installation .
 
Circuits must be designed that are fit for purpose andsuitable for the load they are intended to supply. They should be correctlydesigned in accordance with BS-7671.

Useful-junk .

New numberingsystem introduced for UK-only national regulations . :icon_bs:

In Amendment - 1 , UK national regulations willend in 100, 101,102, etc.

Regulation , 522.6.7 now 522.6.102

Regulation , 433.1.5 now 433.1.103

This will show-regulations that are specificto the ( UK only and not used in theEU )

 
Useful-junk

1988 an agreement was reached that , voltage-levels across Europe should be unified at 230V , Single-phase & 400V , Three-phase with effectfrom , January 1[SUP]st[/SUP] 1995 .

Tables in the 17[SUP]th[/SUP] Editionhave been , recalculated to take account of the unified-voltage-levels . 230V & 400V

BS-7671: Made a Stand . :icon_bs:

Introduction of the ( Free-European-Marker in 1993 ) caused serious-problems for , UK electrical-contractors . IEE / IET wiring-regulations were held in high-esteem .they had , no-legal-status thatwould require Europeans who werecarrying out , installation-work in the UK to abide by them .

1992 , when the , IEE / IET wiring-regulation(s) became a (British-Standard ) BS-7671: giving them therequired-international-standing , from 2010 , BS-7671:

 
Useful-junk: 2011:
Definition :- JPEL/64 . Regulation – GP / 10 . as at June 2011.
The , UK National-Committee-responsible for , BS-7671: is ( JPEL/64 ) :icon_bs:
J ... joint IET / BSI – committee .
P ... Power .
EL ... Electrical .
64 ... IEC– designation for Committees dealingwith , low-voltage-electrical-installations .

 
BS-7671:2011: have stated the facts for us . :icon_bs:

2394 : RCCBs are still out-there ,
BS-EN-61009-1 ( RCBO ) BS-EN-61008-1 – ( RCCBs )

p/286 . BS-EN-61008-1:2004 + 12:2009
Residual-current-operated-circuit-breaker(s) without, integral-overcurrent-protection for household & similar uses ( RCCBs ) – Part 1 : General-rules
Introduction , Chapter -41 , 411.4.9.
411.4.9. . P/57
Where an , RCD is usedto satisfy the requirements ofRegulation , 411.3.2.2. the maximum-values of , earth-fault-loop-impedance in ,table- 41.5 may be applied for non-delayed RCDs to BS-EN-61008-1. & BS-EN-61009-1 . for anominal-voltage , ( Uo of 230V ) in such-cases , anovercurrent-protective-device shallprovide protection against , overload-current & fault-current in accordancewith Chapter – 43 .

411.3.2.2. Automatic-disconnection in case of a fault .
The maximum-disconnection-time stated in , Table -41.1 shall be applied to final-circuitsnot exceeding 32A .
Table 41.5.
Maximum , earth-fault-loop-impedance( Zs ) for non-delayed RCDs . to BS-EN-61008-1. & BS-EN-61009-1 for ( Uo of 230V ) Regulation – 411.5.3.

Table 53.4. Guidance on the selection of protective , isolation & switching-devices .

710.411.3.2.1. Medical-Locations .
Care shall be taken to ensure that ,simultaneous-use of many-items ofequipment-connected to the same-circuit , cannot-cause unwanted-tripping of the residual-current-protective-device ( RCD )

710.410.3.4. Exhibitions , Shows & Stands .
A cable-intended tosupply-temporary-structures shall beprotected at its origin by an RCD whose-rated-residual-operating-current , dosenot exceed 300mA , This device shallprovide a delay by using a device in accordancewith BS-EN-60947-2 , or be the ( S – type in accordance with BS-EN-61008-1 ) or BS-EN-61009-1for discrimination with RCDs protecting-final-circuits .

Note : The requirement for ,additional-protection relates to theincreased-risk of damage to cables in temporary-locations.

721.411.1 Electrical-Installations in Caravans & Motor-caravans .
Where-protection byautomatic-disconnection of supply is used ( Section – 411 ) an RCD – complying with , BS-EN-61008-1 . & BS-EN-61009-1, interrupting all-live-conductors’ shall be provided having the characteristics specified in Regulation –415.1.1. & the wiring-system shall include a circuit-protective-conductor which shall be connected to . Etc . refer . 721.411.1 (i) (ii) (iii)

740.410.3. Section – 740 .
Automatic-disconnectionof supply to the temporary-electrical-installation shall be provided at theorigin of the installation by one or more RCDs with a rated-residual-operating-current not exceeding 300mA , the RCD shall incorporate, time-delay in accordance with BS-EN-60947-2 , or be the ( S – type inaccordance with BS-EN-61008-1 ) or BS-EN-61009-1 , where necessary to provide discrimination with RCDs protecting-final-circuits .

740.411 , Note .
p/295 . Appx 3, Table – 3A . Time / current , characteristics of overcurrent-protective-devices & RCDs

am justbring it to your Attention . BS-EN-61008-1




 
What’s in a Book.

Re-cap : GN-3 ,P/11 , offers Us Guidance. 2394 . What will help me in my ,Exams . ( Better-understanding )

Safety:
Electrical-testing inherently-involves some degree of Hazard .

It is the Inspector’s-duty to ensure his ( or her ) ownsafety , & that of others , in the performance of the test-procedures .

The safety-procedures detailed in , Health &Safety-Executive-Guidance , Note GS-38 .( revised )

Electrical-test-equipment for use by , electrician’s should be observed . When testing does not require the equipment orpart of an installation to be ( Live )

It should be made ( Dead) & ( Safety-isolated)

Guidance on ( Live & Dead-working ) Safety-Executive-publication , Memorandum of guidanceon the , Electricity-at-work-Regulations – 1989 ( HSR.25 )

Guidance on, Safe-isolation-procedures can be found in a ,best-practice-guide-published by the , ESC .

 
What are the Objectives of the IET– Wiring-regulation(s) BS-7671:2008: 2011.

To ensure the ( Protection) of people & livestock from , fire , shock or burns from any installation thatcomplies with their-requirement’s.

 
What in the Eyes of , The IET-Wiring-Regulations ( Cover) Main-cover , The Words , Wiring-Regulations.

Re-cap , TheRegulations cover both : ( What ?? ) :icon_bs:

Electrical-installation(s).
Electrical-equipment .

 
It assumes that behind every Electrician thereis a Designer. :icon_bs:

Ohm’s-law , the current-flowing will depend on thevoltage-applied & the résistance of the current-path.

In the Eyes of ,BS-7671:2008:2011:
Limit the severity of , Electric-shock is the limitation of ,Earth-fault-loop-impedance .

As Electrician’s, we know this all too well . Electric-shock results from contact with a conductor that form-part of a circuit . ( Live )

Circuit-breaker(s) :- Overcurrent-protective-system will offer , no-protection
RCDs . RCBOs /MCB . RCD with an opening-current of 30mA . ( BS-7671: do not claim great expectations , Additional-protection ) May-do-so . 2392-10 . Can a RCD become faulty or is faulty . that’s why Testing is very-important .

GN-5 : The effects of an , Electric-shock ... ( Dependent on the current )
Depends on two-factor(s)

• Value of shock-current-flowing .
• Time for whichit flows . ... ( Additional-protection )

Human-body is composed largely of water, & has very-low-résistance ( Theskin has very-high-résistance )

 
Just making you aware : ( Fixed-electrical-equipment )

Protection from Burns . 423 . P/77 :icon_bs:

Regulations provide a Table showing the , Maximum-allowable-temperatures-surfaces, that could be touched & thus-cause-burns .
From you point of view , Very-Young , Old , Infirm . Etc

Accessible-part of equipment within-arms-reach , refer
 
Working my way around the Regulations .

Overcurrent-Protection. against Overcurrent . 43 . P/79 :icon_bs:

The term can bedivided into two-types of excess-current .

Overload-current(s) ... ( higherthan those intended to be present in the system )
Short-Circuit-Current(s)... ( These currents will only occurunder , fault-conditions )

-&-s. The type of fault which occurs when a Line-conductor comes in contact with aneutral-conductor is called : ( short-circuit-fault)

430.1. This chapter provides-requirements for theprotection of ( Live-conductors fromthe effects of Overcurrent )

Etc . describes how ( Live-conductors are protected by one-or-more-devices for the automatic-disconnection of the supplyin the event of Overload-current )

Note - 1, Live-conductors-protected against-overload in accordance with Section – 433 are also considered to be protection-against-faults, likely to cause overcurrents of a magnitude similar to overload-currents . Etc .refer

 
2011- Note : P/55. 411.4.7. Table – 41.3. for the types & ratings of overcurrent-devices , listedmay be Used-instead of calculation . :icon_bs:


► Taken from , Old-notes . 16[SUP]th[/SUP] Edition . :oops:

Overload-provisions are met , if the setting of the protective-device: ( In )

Exceeds the circuit-design-current . ( Ib )
Does Not-exceed the rating of the smallest-cable-protected .

The current for operation must not be greater than ( 1.45 times the rating ) of the smallest-cable-protected .

BS-EN-60898 . ( B –type ) requires a 32A Circuit-breakerto operate within one-hour when carryinga current of 40A .
Fig – 3.4. P/301 ... ( 5 x 32A = 160A) High-current-operation

Maximum-loop-impedance. ( Ia, Ief )

Amp ÷ current = sec .
32A ÷ 230v = 0.1
Zs ≤ Uo / Ia .
Zs ≤ 230 / 160 .
Zs ≤ 1.4375Ω ... 41.3 , Zs - 1.44Ω

Instantaneous“ which is actually within ( 0.01 s ) 10mS . ( Current for time. 0.1s to 5s. ) Fig – 3.4. P/301

Fig . 3A4 . 3A6 .

B . 3 x 6A = 18A or 5 x 6A = 30A
C . 5 x 6A = 30A or 10 x 6A = 60A
D . 10 x 6A = 60A or 20 x 6A = 120A

When does a Circuit-breaker trip . B , 3 - 5 .

The Circuit-breaker-side of the RCBO. BS-EN-61009-1 , Fig . 3A4 . 3A6 . Overcurrent-characteristics

433: P/81 . Protection against ,Overload-current .

Reason : Overload-protection is to safeguard-Conductors & Cables .
Overload-protection is related to the ,Current-carrying-capacity of the cables. Etc
 
Extracts . taken

Health and Safety at Work Act 1974

The Health and Safetyat Work Act 1974 and the Electricity at Work Regulations 1989 are statutorydocuments and non-compliance constitutes a criminal offence.

Electricity at Work Regulations 1989

Because of the widerange of work covered by the regulations, the requirements are framed ingeneral terms , the Memorandum of Guidance on the above regulations, a clearcase is made for using RCDs as an additional safeguard forearthing ( Reg - 8 ). Also under clause 12 ( Isolation ), it advises that the use of , RCDs will meet the provision of ( Isolation) check – Table 53.4.
 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
449
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top