Before everything, a safe isolation procedure must be carried out. Periodic-inspecting . :aureola:
What is Insulation-résistance-testing ??
The insulation resistancetest is an electrical-test which uses a certain type and level of voltage ( 500V d.c. for Low-Voltage-installations )

Required-test-voltage& the minimum-required-résistance in accordance with BS-7671:2008:2011:

BS-7671:2011: Sates . The ( Minimum-résistance ) to comply with the Regulation(s)

Circuit-Nominal-voltage : Between 0V & 50V a.c.
Test Voltage: 250Vd.c.
Minimum-résistance : 0.5MΩ

P/191 . Note : ( IR ) values are usually muchhigher than those of , Table – 61 .

Circuit-Nominal-voltage : Between 50vand 500V a.c.
Test Voltage: 500V d.c.
Minimum-résistance : 1MΩ

Circuit-Nominal-voltage : 500V above , 1000V a.c.
Test Voltage: 1000 V d.c.
Minimum-résistance : 1 MΩ

P/31 . Nominal-voltage : ( see-Voltage, nominal )


 
2392-10 . Overlooked :- The, Why’s ? Megger – 1552

Connect - leads tometer and test , short & open-circuitfor lead-continuity. :35:
 
[h=3]Useful-junk :[/h][h=3]P/25 , Consumer-unit: [/h][h=3]Were did thatname come from . ( CCU ) Consumer-Control-Unit , BS-7671:2001:2004:2008:2011. :icon_bs:[/h]
 
[h=3] BS-7671:1991 : Extracts. Wiring-systems : ( When is a Regulation past it’s Best ) :46:
[/h][h=3]604-10-01. Every-wiring-system shall be so arranged that no-strain is placed on the , terminations of conductors unless such-terminations are designed for this purpose .
[/h][h=3]604-10-02. Cables shall not be run-across a site-road or awalkway unless , adequate-protection ofthe cables-against , mechanical-damage is provided . [/h]

 
BS-7671:
All Appendices are informativeother than , Appendix 1 which is normative. Appendix1 is a requirement and all others are provided for guidance

 
Re-cap :

For installation(s) with a 230V –single-phase-supply , rated up to 100A ,that are under the control of Ordinary-persons . ( Switchgear & Controlgear )
Comply with , BS-EN-60439-3 & Regulation - 432.1. P/80 .

Be a , Consumer-unit incorporating-components-complying with , BS-EN-60439-3 .

Switch-disconnections, BS- EN-60947-3.

432.1 . Protection against overload-current ( Only) Etc
For a , Circuit-breaker making, anyovercurrent up to & including the ( Maximum-Prospective-Fault-Current ) at the point where the device is Installed.

P/284 : BS-EN-60439-3:1991 . defined as .
Particular-requirementsfor , ( LV ) Switchgear &Controlgear assemblies intended to beinstalled in places where ( Unskilled-persons ) have access totheir use , Distribution-boards .

BS-EN-60439-3:1991+A2:2001

Low-voltage switchgear and controlgear assemblies. Particular requirementsfor low-voltage switchgear and controlgear assemblies intended to be installedin places where unskilled persons have access to their use. Distribution boards

P/150 . 537.1.4. General-requirements.
A main-switch intended for operation by ordinary-persons , of a household orsimilar-installation , should interrupt, both live-conductors of a ,Single-phase-supply .

537.1.4. A main-linked-switch or linked-circuit-breaker shall be provided as near as practicable tothe origin of every-installation as ameans of switching the supply on load & a means of Isolationswitch

P/29 . Isolation :- is the function that Allows operatives to work-safety onelectrical-equipment. BS-7671:2008:2011: as defined as :

A “ function-intended to cut off for reasons of safety the supply from all ,or a discrete-section , of the installation by separating the installation orsection from , every-source of electrical-energy

RCCBs , are devicesdesigned to protect against , fault-currents flowing to earth,
 
Testing . 2392-10 .
Test-method 1 : use the Line-conductor as a return-lead , Otherwise known as the ( R[SUP]1[/SUP]+ R[SUP]2[/SUP] ) method .
Résistance of the ( CPC )
Q . Why do I need to bother with the, Résistanceof the Line-conductor ?
Reason being : can use Line-conductor as part of the circuit . ( Willyou use a Wander-lead , NO )
Reason : Your ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) reading can be used for working out your ,Earth-fault-loop-impedance-value . (Circuit-loop-impedance )
Have you , Obtained Polarity . at the same-time . ( L / CPC )
Most used methodused for ring-final-circuit(s) Line-conductor runs alongside a ( CPC ) conductor , factor is utilised in this Test . :yes:
 
2392-10 . better-understanding.

Test-method 2 : uses the , Wander-lead , it’s title ( R[SUP]2[/SUP] - method)

Your Reason . Wander-lead is a simply a long-length of conductor that can be moved to different-points . in anInstallation .

( R[SUP]2[/SUP] - method) confirm the continuity of , Equipotential-bonding-conductor(s) 612.2.1. :svengo:

2392-10, you do not have a, Line-conductor as a return-path. “ Simple “

 
For , safety-reasons ... (You may have Implication(s)

( R[SUP]2[/SUP] - method)
Ensure that you have the permission beforehand ( Disconnectany parallel-paths) main-protective-bonding-conductor . Etc
 
Design-Procedures : of Any- BS-7671: 2392-10 : As , Installers / Designers.

Safety of , Life & Property, are the first-two-important-factors to be considered in the ( Design ) of low-voltage-systems.( LV )
 
2392-10:- How significant is Insulation-résistance-testing !!

Insulation starts to age as soon as it's made. And, agingdeteriorates its performance.

Installation-résistance-test : Integrityof Conductor(s).

Insulation-résistance, confirmthe reliability of the circuit , in question .

( shorted-connectionwould be obvious from the test-results)

Initial-verification: 2008:2011:
Every-installationshall , during-erection & on-completionbefore being put into service , be . ( Inspected & Tested to verify )

Regulation - 612.3 ( Under-the-section for Initial-verification) :icon_bs:

GN-3 : States :
Insulation-résistance-testedduring various-stages of installation to ( Prove ) the integrity of installed-cables .
 
( 1MΩ / 2MΩ ) Extracts.

2008: GN-3 , States :

Whole-installation, Periodic-testing... ( Existing )
Single-circuit(s), Initial-Verification... ( New-installation )

Insulation-résistance to Earth.
Single-phase .
Test between the line &neutral-conductor(s) connected together& Earth at the appropriate , distribution-board, of for circuits /equipment not vulnerable to ,insulation-résistance-testing , line & neutral-separately to Earth .
For circuits containing two-way-switching ortwo-way & intermediate-switching ,the switches must be operated one at a time & the circuits subjected to additional-insulation-résistance-test(s)

Where a low-reading is obtained ( Less than 2MΩ ) it may be necessary to test each-conductor-separately to earth , after ensuring that all equipmentis disconnected .

Résistance-readings obtained should be not less than the ,minimum-values , refer , Table – 61

If a sufficient-high-reading cannot be obtained on the , ( Whole-installation) GN-3 - requires us to . Test ( On any individual circuit(s) discover where any fault is occurring .

Sixth-edition : Inspection& Testing (GN3) provides us with an opportunity comment onthe critical-importance of the Verification-process.
GN3 is, primarily concerned with Part 6 of BS-7671 – Inspection and Testing.
2392-10 , You are only testing , Single-circuits (T&E ) on Initial-Verification. ( You will not Test , Whole-installation)
 
fifth-edition- 2008 GN-3 : P/38 , Extracts .
Although an , insulation-résistance-value of not less than ( 1.0MΩ ) complies with the Regulations , where aninsulation-résistance of less than ( 2MΩ ) is recorded the possibility of alatent-defect-exists , in these-circumstances ,
Each-circuit should be tested-separately .
GN-3 , re-cap .
This will help identify (i) whether one-particular-circuit in theinstallation has a lower-insulation-résistance-value , possibly-indicating alatent-defect that should be ( Rectified) Or
(ii) whether the low-insulation-résistance-represents, for example , the summation of individual-circuit-insulation-résistance &as such may not be a cause for concern .
 
From , 1991 / 2011 . BS-7671 : :icon_bs:

P/29 . Insulation : Suitable non-conductive-material enclosing, surrounding or supporting a conductor .
 

Reply to Re-take - Useful Information for 2394 : in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

thanks for the confirmation this is what i thought. i cant think of what use this device is . i have seen David Saverys Arc Fault Detection Device...
Replies
4
Views
396
  • Question
those old mk rcds are very fast the figure you have quoted is the maximum allowed not the typical times,I have seen mk ones trip at 9 ms , the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top