My dad had his tv and video recorder into same plug. I think it would be safer than one of those cube adaptors hanging out the wall.
Afigure of 8 (meaning a bridge somewhere in the ring) means we can not be sure to which extent the current will flow in every scenario of current draw at any particular times .If each one is safe if on 2 devices, what makes them become unsafe when put on 1?
There aren't.
It isn't
But why, other than testing aggro?
By exactly the same logic we should not have any ring finals, because if the ring is broken then the circuit becomes 2 radials.
A figure-of-8 actually decreases the chances of a break leading to an overload potential.
Diagram 3 and 4 are the same, just one extra socket, what are you trying to prove? or diss-prove come to that?
Didn't Marbo (?) used to make a plug designed to take more than one flex?I've done the same in the past I must admit. In my own home. Not ideal, but as long as it is 2 small flexes and the cord grip secures them properly then not too bad.
Didn't Marbo (?) used to make a plug designed to take more than one flex?
Not really other than it's not called a ring main a ring main is a distribution circuit it's ring final circuit if you get your terms correct you may get some better responsesIt's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.
But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.
I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.
Anyone out there with circuit design software which could be used to analyse different scenarios?
youneed to get out more. don't the pubs open soon?If I start with this:
View attachment 84116
and add a loop like this:
View attachment 84117
or if I start with this:
View attachment 84118
and add a link across the middle to end up with the same figure of 8, which cable(s) become at risk of being overloaded that would not if I'd done this:
View attachment 84122
?
The more paths there are for current to flow to each point of loading the less flows in any given one, not more.
Ignoring the practical realities of actually wiring it, a "full mesh" topology of interconnections
View attachment 84124
would minimise the current flowing in every single cable (apart, obv, from the ones from the OPD to the "first" and "last" sockets, but those cables are never affected by any interconnection topology anyway).
And the more connections you have the harder it becomes to turn the circuit into radials, or to create multi-socket branches, by cutting connections.
If you are referring to me Tel, then nothing gets up my snout more than Wannbee's quoting something they know little or nothing about post ban waiting, still no one likes the truth these days do they?youneed to get out more. don't the pubs open soon?