Hi all
Working on a site with a general builder who planned on doing all the electrical work - total rewire - on the job, and is miffed because the home owner decided to call in a qualified electrician and get his certificates - builder has run some lighting cables, any old cable he had lying about (4 core/immersion heater cable/etc), which I'm replacing - and told us that he was going to run the ring circuit to start in 6mm T&E from the Consumer Unit, then (after an unspecified distance) to a junction box to split into 2 x 2.5mm T&E. Obviously he wasn't going to test, or notify, or certificate the work. Like to see the comments
Working on a site with a general builder who planned on doing all the electrical work - total rewire - on the job, and is miffed because the home owner decided to call in a qualified electrician and get his certificates - builder has run some lighting cables, any old cable he had lying about (4 core/immersion heater cable/etc), which I'm replacing - and told us that he was going to run the ring circuit to start in 6mm T&E from the Consumer Unit, then (after an unspecified distance) to a junction box to split into 2 x 2.5mm T&E. Obviously he wasn't going to test, or notify, or certificate the work. Like to see the comments