If someone is stupid enough to take the cover off the service head then they deserve all they get I'd say mate.
As with a fair bit of bs7671, it seems open to interpretation. Granted, NICEIC isn't Gospel but having seen many a burn mark in electrical installations, I would think it best practice to avoid and ideally replace any wooden fusebox's and sockets mounted in skirting. Fire requires a heat source, fuel and oxygen. If you can remove the fuel, the fire wont start!
A bit surprised your asking this type of question mate when your website says:Many thanks to all the helpful people out there. No where in the manual does it say to join the N and E leads together but I have and these are the results I eventually got for my house which I know is TNCS. PSC between line and earth 0.28 ohms and 0.891ka. PSC between line and neutral 0.29 ohms and 0.861ka. So, many thanks. That seems to all make sense.
However, the di-log leads are not at all easy to connect together! First result came up on screen FUSE and secondly the results did fluctuate. It was only on the third test that I got these results. Got reading's fluctuating between 0.32 ohms and 0.17 ohms so not necessarily all that easy to interpret results....
I do try to pass my skills on as much as I can and enjoy doing it but sometimes what someone needs is a bloody good rollocking. I got enough of them when serving my time to know whether something I'm thinking about doing is dangerous or not.
take a Zpn... then a Zpe....if TN-C-S the KA should be substantially the same for both tests....Blimey, why is everyone on their high horse today! My dilog 9083p takes the pscc and pefc at the same time and only when it detects line, neutral and earth. I then press the function key to find the highest kA and ze values between the two. If there's an alternative way of finding the kA value I would like to know it but don't try and belittle me! I'm sure I'm as every bit as competent as yourself if not more so!
Regards the socket outlets in skirting’s, I have never come across sockets in skirting’s that have put under undue pressure on the supply or load cables. I have however, seen them with wooden back boxes. Surely if the cables arched/overloaded then there is a fire risk with them being mounted in the flammable wooden skirting’s? Granted most are in metallic back boxes but not all.
Surely if you remove the heat source by ensuring the circuit is designed, installed, maintained and used correctly then fire shouldn't arise. Most burn marks I've ever seen have been caused by a poor standard of workmanship by the installer or incorrect design or use. Plastic burns as well doesn't it (although I'm not sure what temperature would be required)?
so you thought you`d follow suit did you?...I'm sorry but some of the criticsm is a little unjust. Yes, the di log is a very easy to use multi function tester but no where in the manual does it say to join the neutral and earth leads together to perform a seperate pfc to distinguish between tns and tncs. Additonally, the way the readings naturally fluctuate I would say it is not always easy to interpret these results.
I can distinctly remember having a high ze value of 0.9 ohms on one job. Uk power networks came out and there was some ambiguity as to whether it was tns or tncs. He removed the service head cover and showed me it was tns. He didn't isolate the supply before removing this cover. He then took his own ze readings and they were just under 0.8 ohms. When I said I was getting readings of 0.9 ohms earlier he just shruged his shoulders.
so you thought you`d follow suit did you?...
hmm.
not only do you put yourself (and possibly others) at risk....but it is an offence to interfere with DNO equipment...
I and others have explained to you (i thought quite clearly) as to how to test to verify beyond any reasonable doubt as to the earthing arrangements that cannot be verified by visual alone.