I am quite interested to know how people would go about this installation.
Install a 3-phase supply from a house to the middle of a field and install a distribution board with main switch. approx 150 mtrs
Then from one phase run away to various outlets for caravans the furthest being 300 mtrs away. this cable would be downrated to a lowly 40 amps but would be quite sufficient for the voltage drop, probably a 35mm SWA.
Each of the caravan outlets has its own 30ma RCD and earth stake so will work on its own TT system.
The origin would have a time delay RCD so as not to trip out before any of the outlet RCD's.
My question is this.
What earth connections would you make at the 3-phase board, would you divorce the earth?
Would you divorce the single phase 40 amp outgoing way from the 3-phase but connect it with the 3-phase SWA.
The time delay is to give the SWA some protection.
Install a 3-phase supply from a house to the middle of a field and install a distribution board with main switch. approx 150 mtrs
Then from one phase run away to various outlets for caravans the furthest being 300 mtrs away. this cable would be downrated to a lowly 40 amps but would be quite sufficient for the voltage drop, probably a 35mm SWA.
Each of the caravan outlets has its own 30ma RCD and earth stake so will work on its own TT system.
The origin would have a time delay RCD so as not to trip out before any of the outlet RCD's.
My question is this.
What earth connections would you make at the 3-phase board, would you divorce the earth?
Would you divorce the single phase 40 amp outgoing way from the 3-phase but connect it with the 3-phase SWA.
The time delay is to give the SWA some protection.